<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto">I would double check the new inverter\u2019s wiring. Those extra neutral wiring points can be a trickster. <div><br></div><div>From the Mate3 main status, press the Inverter Status soft key (3rd button from the left). The upper left status will indicate Selling, charging, etc. Press the Port button to cycle around the inverters. Make sure none of the inverters have Errors. Especially ones that don\u2019t necessarily report as an Event. I had a similar issue and it turned out I also needed a née Hub. </div><div><br></div><div><br><br><div dir="ltr"><div class="" style="caret-color: rgb(0, 0, 0); color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; -webkit-text-size-adjust: auto;"><div class="ApplePlainTextBody">Maverick Brown<br>Off-Grid Solar Commander since 2006<br><b>Maverick Solar Enterprises, Inc.</b></div><div class="ApplePlainTextBody"><b> \u2022 Solar Commander Remote Power</b></div><div class="ApplePlainTextBody"><b> \u2022 SunFlow Systems Cathodic Protection <br></b>maverick@mavericksolar.com<br>512-460-9825</div><div class="ApplePlainTextBody"><br></div></div></div><div dir="ltr"><br><blockquote type="cite">On Jul 18, 2021, at 10:34 PM, Jon Siegenthaler <jon.siegenthaler@gmail.com> wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<div dir="ltr"><div>Hey folks,</div>I went to investigate 3 Radian 8048A's that had the master inverter slowly die from salty air. The newest slave that was added to the existing system of 2 radians was programmed to be the master and the AGS was set to the new master as well. The corroded ex-master was replaced with a new radian (now a slave) and the system runs fine. <br><div><div><br></div><div>Except when the generator runs for about 20 minutes. After 20 minutes the main AC breaker trips and the power goes out on the system. It's clear that the AC output must be seeing more than or equal to 50A and that's causing the trip but I cannot figure out why this only happens with the generator running. <br></div><div><br></div><div>Also when the generator is running an error of overcurrent will occur and show an imbalance of 34A to 108A from phase A to B. Eventually the current will come closer together and the error will disappear. However during the imbalance I will check the actual generator output conductors with my amprobe and see around 43A to 48A phase A to B. <br></div><div><br></div><div>Has anyone experienced this or know what the best solution would be to resolve this issue? <br></div><div><br></div><div><br></div><div><br></div></div></div>
<span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address & settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules & etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></div></body></html>