<div dir="ltr"><div>Hey folks,</div>I went to investigate 3 Radian 8048A&#39;s that had the master inverter slowly die from salty air. The newest slave that was added to the existing system of 2 radians was programmed to be the master and the AGS was set to the new master as well. The corroded ex-master was replaced with a new radian (now a slave) and the system runs fine. <br><div><div><br></div><div>Except when the generator runs for about 20 minutes. After 20 minutes the main AC breaker trips and the power goes out on the system. It&#39;s clear that the AC output must be seeing more than or equal to 50A and that&#39;s causing the trip but I cannot figure out why this only happens with the generator running. <br></div><div><br></div><div>Also when the generator is running an error of overcurrent will occur and show an imbalance of 34A to 108A from phase A to B. Eventually the current will come closer together and the error will disappear. However during the imbalance I will check the actual generator output conductors with my amprobe and see around 43A to 48A phase A to B.  <br></div><div><br></div><div>Has anyone experienced this or know what the best solution would be to resolve this issue? <br></div><div><br></div><div><br></div><div><br></div></div></div>