<div dir="ltr">Bob, <div>This is a very interesting idea to have two separate battery banks in series. I find it odd though that this particular motor&#39;s datasheet calls for 9 12V batteries. I suppose that I could have one charge controller set for 48V and the other set for 60V. Although this will also pose the problem of trying to run the house loads - if I have two 48V inverters that still leaves one battery that will get loaded less than all the others.</div><div><br></div><div>And it seems that everyone else is pointing to the fact that it seems important to keep the neutral and ground internally separated in the inverter in a boat, so I&#39;ll stick to marine inverters for this one.</div><div>Cheers,</div><div>Dave</div><div><br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Jun 30, 2021 at 5:30 PM <a href="mailto:bob@midnitesolar.com">bob@midnitesolar.com</a> &lt;<a href="mailto:bob@midnitesolar.com">bob@midnitesolar.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div>
    <br>
    If you can&#39;t find a single compatible charger, what also works it to
    use 2 (two) separate<br>
    <br>
    MPPT charge controllers each with a separate PV array inputs and
    connect each CC&#39;s<br>
    battery to half of the battery bank.  This has worked fine for both
    OB and MNS controllers<br>
    in past years and should with others as well I would imagine.  Set
    each for slightly higher<br>
    voltage than 48V of course.<br>
    <br>
    One thing you may not be able to do might be connecting the chassis
    grounds together<br>
    depending on how those grounds are tied to the battery negative and
    positive lines internally.<br>
    <br>
    Sometimes the internal SPD MOVs can get in the way if their voltage
    isn&#39;t high enough to handle<br>
    the two PV voltages that are seen as in series from the MOV&#39;s
    standpoint.  But those MOVs are<br>
    usually sized voltage wise to handle much higher voltage than, say,
    300V which would he the maximum<br>
    voltage both CC&#39;s would see for 150V max input controllers.<br>
    <br>
    You also cannot use the same remote controllers if they are not
    isolated from battery minus except for<br>
    the controller that is on the bottom side of the battery bank.<br>
    <br>
    I have seen this method used many times now for 120V battery banks
    and also for higher voltage<br>
    electric boats.   There is quite a bit of this kind of wiring out
    there as I remember.<br>
    <br>
    There are some other standards for marine inverters like,  UL 458
    marine supplement and ABYC ratings.<br>
    <br>
    This includes neutral ground switching like in mobile apps too IIRC.<br>
    <br>
    Of course, just adding the word &quot;marine&quot; has to increase the price
    not matter what the product is.<br>
    \U0001f601<br>
    <br>
    boB<br>
    <br>
    <br>
    <br>
    <div>On 6/30/2021 12:50 PM, Dave Tedeyan
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">Hi All, 
        <div><br>
        </div>
        <div>I am going to be working with someone who plans to
          completely electrify a boat. The electric motor is meant to
          run on nine 12V batteries, or 108V. The motor manufacturer
          recommends a charger that can run on 120V or 240V. But has
          anyone seen a charger that can take solar power and directly
          charge a battery bank of 108V? The alternative that I see here
          is to have two separate battery banks, one for the motor, and
          one for house loads. Then we would have the solar charge a 48V
          battery bank, and then use an inverter to charge the 108V
          battery bank. It seems inefficient, although that may be the
          only choice.</div>
        <div><br>
        </div>
        <div>A separate but related question: what is special about a
          marine inverter? If there is a 5kw charger for the battery
          bank, we will need a large inverter to handle this plus
          other AC loads, and I am not sure if there are &quot;marine&quot;
          inverters this large. And so other than concerns about getting
          wet, is there harm to putting a Radian, or a Sol-Ark on a
          boat?</div>
        <div><br>
        </div>
        <div>Cheers,</div>
        <div>Dave</div>
        <div><br>
        </div>
        <div>-- <br>
          <div dir="ltr">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <table style="border-spacing:0px;border-collapse:collapse;color:rgb(68,68,68);width:525px;font-size:11pt;font-family:Arial,sans-serif" cellspacing="0" cellpadding="0">
                    <tbody>
                      <tr>
                        <td rowspan="6" style="font-family:Arial,sans-serif;padding:0px 10px 0px 0px;font-size:10pt;border-right:1px solid rgb(236,189,0);width:125px;vertical-align:top" width="125" valign="top"><a href="https://www.sungineersolar.com/" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><img alt="Logo" src="https://sungineersolar.com/wp-content/uploads/2019/08/Logo-Image-Only-1.png" style="border: 0px; vertical-align: middle; width: 105px; height: auto;" width="105" border="0"></a></td>
                        <td style="padding:0px 0px 0px 10px">
                          <table style="border-spacing:0px;border-collapse:collapse;background-color:transparent" cellspacing="0" cellpadding="0">
                            <tbody>
                              <tr>
                                <td style="font-family:Arial,sans-serif;padding:0px 0px 5px 10px;width:400px;vertical-align:top" valign="top"><span style="color:rgb(236,189,0);font-size:11pt;font-weight:700">Dave
                                    Tedeyan, P.E.<br>
                                  </span><span style="font-size:11pt;font-weight:700"><font color="#ecbd00">Owner | Sungineer
                                      Solar</font><br>
                                  </span></td>
                              </tr>
                              <tr>
                                <td style="font-family:Arial,sans-serif;padding:5px 0px 5px 10px;font-size:10pt;vertical-align:top;line-height:17px" valign="top"><span style="color:rgb(236,189,0)"><span style="font-weight:700">p: </span></span><span style="font-size:13.3333px"><span style="font-size:10pt;color:rgb(0,0,0)">he
                                      | him | his</span></span><span style="color:rgb(236,189,0)"><span style="font-weight:700"><br>
                                      a: </span></span><span style="font-size:10pt;color:rgb(0,0,0)">1653
                                    Slaterville Rd.</span> <span style="font-size:10pt;color:rgb(0,0,0)">| Ithaca,
                                    NY 14850</span><br>
                                  <span style="color:rgb(236,189,0)"><span style="font-weight:700">w:</span></span><a href="http://www.sungineersolar.com/" rel="noopener" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><span style="font-size:10pt;color:rgb(0,0,0)"> www.sungineersolar.com</span></a><br>
                                  <span style="color:rgb(236,189,0)"><span style="font-weight:700">c:</span></span><span style="font-size:10pt;color:rgb(0,0,0)"> (607) 288-2898</span></td>
                              </tr>
                            </tbody>
                          </table>
                        </td>
                      </tr>
                    </tbody>
                  </table>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank">http://re-wrenches.org</a>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn&#39;t work, try the other:
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </div>

</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div><div dir="ltr"><div dir="ltr"></div></div></div></div><div dir="ltr"><table cellpadding="0" cellspacing="0" style="border-spacing:0px;border-collapse:collapse;color:rgb(68,68,68);width:525px;font-size:11pt;font-family:Arial,sans-serif"><tbody><tr><td width="125" valign="top" rowspan="6" style="font-family:Arial,sans-serif;padding:0px 10px 0px 0px;font-size:10pt;border-right:1px solid rgb(236,189,0);width:125px;vertical-align:top"><a href="https://www.sungineersolar.com/" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><img border="0" alt="Logo" width="105" src="https://sungineersolar.com/wp-content/uploads/2019/08/Logo-Image-Only-1.png" style="border: 0px; vertical-align: middle; width: 105px; height: auto;"></a></td><td style="padding:0px 0px 0px 10px"><table cellpadding="0" cellspacing="0" style="border-spacing:0px;border-collapse:collapse;background-color:transparent"><tbody><tr><td valign="top" style="font-family:Arial,sans-serif;padding:0px 0px 5px 10px;width:400px;vertical-align:top"><span style="color:rgb(236,189,0);font-size:11pt;font-weight:700">Dave Tedeyan, P.E.<br></span><span style="font-size:11pt;font-weight:700"><font color="#ecbd00">Owner | Sungineer Solar</font><br></span></td></tr><tr><td valign="top" style="font-family:Arial,sans-serif;padding:5px 0px 5px 10px;font-size:10pt;vertical-align:top;line-height:17px"><span style="color:rgb(236,189,0)"><span style="font-weight:700">p: </span></span><span style="font-size:13.3333px"><span style="font-size:10pt;color:rgb(0,0,0)">he | him | his</span></span><span style="color:rgb(236,189,0)"><span style="font-weight:700"><br>a: </span></span><span style="font-size:10pt;color:rgb(0,0,0)">1653 Slaterville Rd.</span> <span style="font-size:10pt;color:rgb(0,0,0)">| Ithaca, NY 14850</span><br><span style="color:rgb(236,189,0)"><span style="font-weight:700">w:</span></span><a href="http://www.sungineersolar.com/" rel="noopener" style="color:rgb(51,122,183);background-color:transparent" target="_blank"><span style="font-size:10pt;color:rgb(0,0,0)"> www.sungineersolar.com</span></a><br><span style="color:rgb(236,189,0)"><span style="font-weight:700">c:</span></span><span style="font-size:10pt;color:rgb(0,0,0)"> (607) 288-2898</span></td></tr></tbody></table></td></tr></tbody></table></div></div></div></div>