    <p>Copper can get a pretty good oxide layer on it as well, but I'm
      not versed in the science enough to know how any of that effects
      the conductivity. Instead, I assume that the NEC has investigated
      corrosion, and so we just follow the code. For plate electrodes
      (250.52(A)(7)), it just specifies dimensions and thickness, and
      specifically mentions bare iron or steel. 250.52(A)(3)(<i>1</i>)
      for Concrete encased electrodes (UFER) also allows bare steel
      reinforcing rod, while section (<i>2</i>) allows your #4 copper
      UFER.  <br>
    </p>
    <p>Lacking further information, I just go with the code, and my own
      ground impedance measurements over the years.  My small sampling
      of measurements has found steel rebar grounds and large steel pipe
      (4"D and larger) to be under 25 ohms, while I have measured copper
      coated rods as high as 700 ohms in dry soil.  I haven't measure
      copper UFER or compared it to steel, so again, I don't know. It
      might be better than steel, but all are allowed by code.  <br>
    </p>
    <p>Ultimately it might come down to soil and weather conditions for
      different areas?<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 6/25/21 10:35 AM, Dana Orzel wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:001f01d769cf$54e130f0$fea392d0$@solarwork.com">
      <pre class="moz-quote-pre" wrap="">That\u2019s why we use the Ufer, our AHJ assumes that once a layer of rust develops this is not valid...........



Dana Orzel                              Great Solar Works, Inc. 
C - 208.721.7003                       <a class="moz-txt-link-abbreviated" href="mailto:dana@solarwork.com">dana@solarwork.com</a>
Idaho Contractor - # 028765         Idaho PV # 028374
NABCEP # 051112-136                       <a class="moz-txt-link-abbreviated" href="http://www.greatsolarworks.com">www.greatsolarworks.com</a>
"Responsible Technologies for Responsible People since 1988"  
\uf050 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">&lt;re-wrenches-bounces@lists.re-wrenches.org&gt;</a> On Behalf Of Ray
Sent: Thursday, June 24, 2021 4:51 PM
To: <a class="moz-txt-link-abbreviated" href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>
Subject: Re: [RE-wrenches] Grounding Top of Pole Mount Array with a Ufer

We always put our assumption in our plan notes, based on our interpretation of 250.52(A)(7).  AHJs have never questioned it, and we also tie the pole to any rebar, so its all one big happy grounding electrode.

Ray Walters
Remote Solar
303 505-8760

On 6/24/21 6:49 PM, frenergy wrote:
</pre>
      <blockquote type="cite">
        <pre class="moz-quote-pre" wrap="">Ray,

            I couldn't agree more, its been my experience over the 
years that using 20 feet of #4 rebar in a building's footing was 
kosher and accepted NEC 250.52(3).  There's a heck of a lot more 
surface area in 8" pipe 5-6 feet into the earth than rebar in a 
foundation footing.  The ground at the bottom of the pole footing is 
also more likely to be damper.  Our AHJ has always accepted the steel 
pole as a ground rod....common sense prevails sometimes.

Bill

Feather River Solar Electric
Bill Battagin, Owner
4291 Nelson St.
Taylorsville, CA 95983
530.284.7849
CA Lic 874049
<a class="moz-txt-link-abbreviated" href="http://www.frenergy.net">www.frenergy.net</a>

On 6/24/2021 7:31 AM, Ray wrote:
</pre>
        <blockquote type="cite">
          <pre class="moz-quote-pre" wrap="">Usually a steel pole in concrete has enough surface area to qualify 
as a plate electrode under 250.52(A)(7).  It needs to be at least 2 
sq ft and 1/4" thick, and have an electrically conductive surface. So 
we just drill and tap our ground connection into the pole, near the 
combiner box.

Ray Walters
Remote Solar
303 505-8760

On 6/24/21 8:16 AM, Dana Orzel wrote:
</pre>
          <blockquote type="cite">
            <pre class="moz-quote-pre" wrap="">For all of our free standing arrays we now use a Ufer clamp to the 
rebar either cage or just anti spin rebar that is welded to the pole 
in the concrete, with #4 braided copper up to the pole combiner box, 
inverter, etc. for our ground.
With a pole mount &amp; a concrete base it is way easier &amp; less 
expensive than a ground rod, &amp; the inspector seems happier with this 
approach.



Dana Orzel                              Great Solar Works, Inc.
C - 208.721.7003                       <a class="moz-txt-link-abbreviated" href="mailto:dana@solarwork.com">dana@solarwork.com</a> Idaho 
Contractor - # 028765         Idaho PV # 028374 NABCEP # 051112-136 
<a class="moz-txt-link-abbreviated" href="http://www.greatsolarworks.com">www.greatsolarworks.com</a> "Responsible Technologies for Responsible 
People since 1988"
\uf050 Please consider the environment before printing this email.


-----Original Message-----
From: RE-wrenches <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches-bounces@lists.re-wrenches.org">&lt;re-wrenches-bounces@lists.re-wrenches.org&gt;</a> On 
Behalf Of <a class="moz-txt-link-abbreviated" href="mailto:palumbo131m@gmail.com">palumbo131m@gmail.com</a>
Sent: Wednesday, June 23, 2021 9:33 PM
To: RE-wrenches <a class="moz-txt-link-rfc2396E" href="mailto:re-wrenches@lists.re-wrenches.org">&lt;re-wrenches@lists.re-wrenches.org&gt;</a>
Subject: Re: [RE-wrenches] Top of Pole Mount Array on Ledge

Ben,
There is a way if the ledge is solid and true. Twice I have done the 
following with ledge at 18\u201d to 24\u201d below grade. Excavate down to 
ledge, drill down into the ledge and you will determine the 
suitability of the following method. Drill for a pattern of many 
rebar penetrations in to the ledge. Drill to a reasonable depth (as 
deep into the ledge as you are able) in my case it was based on our 
drilling tool and bit length capabilities. We used a large sono 
tube. 42\u201d as a recall, both of these jobs were over 12 years ago and 
my recall on the exact size may be off.
Determine the best adhesive product to use in your drilled holes for 
the rebar, again my memory fails as to what we used based on 
recommendation from a local civil engineer. The sono tube height 
above grade was determined to be 2\u2019 for one TPM12 and 3.5\u2019 above 
grade for a TPM16. Depth down to the ledge determines how high above 
grade you need the concrete footing/base. Use rebar lengths that 
will end a few inches below the finished surface. For grounding you 
can coil up ground wire and lay it on the surface of the ledge 
before your concrete pour. I ran the ground wire through a short 
length of 1/2\u201d or 3/4\u201d PVC conduit, to protect the copper ground 
wire where it comes out of the concrete. Place the conduit coming 
out of the concrete with the ground wire just to the side of where 
the mounting plate base for the TPM will be and fill the PVC conduit 
with a good caulk sealer to keep air and water out of this hole as a 
nexus of concrete, and air will corrode the copper. The TPM\u2019s for 
those two jobs were made of 8\u201d SCHD 80 steel, we had a large plate 
welded to the bottom with 4 vertical side supports on the pipe up 
about a foot. Place the appropriate sized anchor bolts in the 
concrete pour to match your TPM base. Both of these TPM\u2019s have 
worked out well over the years. Local conditions will determine the 
suitability of this method.


Sent from my iPhone
</pre>
          </blockquote>
        </blockquote>
        <pre class="moz-quote-pre" wrap="">

</pre>
      </blockquote>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>


_______________________________________________
List sponsored by Redwood Alliance

Pay optional member dues here: <a class="moz-txt-link-freetext" href="http://re-wrenches.org">http://re-wrenches.org</a>

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>