<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto">It\u2019s a good idea to make sure only one set as Master the others are slave. Start by adding one slave at a time. Turn off Search, Charger and Grid Support until you know they are playing happy.&nbsp;<div><br></div><div>I prefer using the XW Config and walking through the wizard, but you can use Multi Unit setup, which will put everything in standby. I have several 8-12 unit XW sites 3-4 Inverters, SCP, AGS and Combox/ Gateway, etc.&nbsp;</div><div><br></div><div>It can be done.&nbsp;<br><br><div dir="ltr"><div class="" style="caret-color: rgb(0, 0, 0); color: rgb(0, 0, 0); font-family: Helvetica; font-size: 12px; -webkit-text-size-adjust: auto;"><div class="ApplePlainTextBody">Maverick Brown<br>Off-Grid Solar Commander since 2006<br><b>Maverick Solar Enterprises, Inc.</b></div><div class="ApplePlainTextBody"><b>&nbsp;\u2022 Solar Commander Remote Power</b></div><div class="ApplePlainTextBody"><b>&nbsp;\u2022 SunFlow Systems Cathodic Protection&nbsp;<br></b>maverick@mavericksolar.com<br>512-460-9825</div><div class="ApplePlainTextBody"><br></div></div></div><div dir="ltr"><br><blockquote type="cite">On Jun 12, 2021, at 1:32 PM, greg egan &lt;greg@remotepowerinc.com&gt; wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<span>Wrenches, I'm getting ready to go outside the building and shoot myself.&nbsp; AC Coupling is turned off.&nbsp; The XW+ inverters are selling to each other.&nbsp; XW+'s are disconnected from the load and from generator input.&nbsp; System is off grid.&nbsp; When I switch the ATS the inverters are supposed to pick up the load.&nbsp; ~ 12 kW, maybe 18 worst case.&nbsp; They are selling to each other and when I make the switch the lights flicker and the inverters go off, then they try to go on, and go off, etc.</span><br><span></span><br><span>Sync cables are hooked up.&nbsp; 4 XW+ and 1 SCP on one xanbus network. No gateway hooked up at this time.&nbsp; PV will be on it's own Xbus network.&nbsp; Not planning on using the Gateway if I can help it.</span><br><span></span><br><span>Thanks for any light you can shed on this.&nbsp; Not sure why Schneider would ever want their inverters to sell to each other especially with AC Coupling OFF.&nbsp; Arrgh.</span><br><span></span><br><span>Greg Egan</span><br><span>Remote Power Inc.</span><br><span></span><br><span></span><br><span></span><br><span></span><br><span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>Pay optional member dues here: http://re-wrenches.org</span><br><span></span><br><span>List Address: RE-wrenches@lists.re-wrenches.org</span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</span><br><span>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span>http://www.re-wrenches.org/etiquette.htm</span><br><span></span><br><span>Check out or update participant bios:</span><br><span>http://www.members.re-wrenches.org</span><br><span></span><br></div></blockquote></div></body></html>