<div dir="auto"><span style="font-family:sans-serif;font-size:12.8px">0.5 to 6 mm2 is #20-#10 AWG</span></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Apr 27, 2021, 9:10 PM Sindelar Solar &lt;<a href="mailto:Allan@sindelarsolar.com">Allan@sindelarsolar.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  
    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <p>August,</p>
    <p>Thank you for this suggestion. I went to the site, and under &quot;Two
      Sizes for All Conductor Types&quot; on that page it appears that
      there&#39;s a model that&#39;ll work with 2-10AWG conductors:</p>
    <blockquote>
      <p>&quot;With the 6 mm2 (10 AWG) variant, you can connect all conductor
        types \u2013 with cross sections from 0.5 to 6 mm2 (2\u221210 AWG)&quot;.</p>
    </blockquote>
    <p>This would contradict what you wrote below, so I&#39;m just checking
      whether I missed something. <br>
    </p>
    <p>Thanks, Allan</p>
    <div>On 4/27/2021 12:55 PM, August Goers
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">Hi Jason - I noticed that Tesla is using the Wago
        connectors in their Powerwalls. They only go up to #10, but they
        certainly appear to have some advantages such as easy QC
        inspection, compactness, and price. We are in the process of
        trying a batch of these out, but I hadn&#39;t considered using them
        in exterior J-boxes. <br>
        <div><a href="https://www.wago.com/global/electrical-interconnections/discover-installation-terminal-blocks-and-connectors/221" target="_blank" rel="noreferrer">https://www.wago.com/global/electrical-interconnections/discover-installation-terminal-blocks-and-connectors/221</a></div>
        <div>August <br>
        </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Tue, Apr 27, 2021 at 10:42
          AM Jason Szumlanski &lt;<a href="mailto:jason@floridasolardesigngroup.com" target="_blank" rel="noreferrer">jason@floridasolardesigngroup.com</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="auto">I&#39;d be interested to hear thoughts on Wago
            221-6XX series connectors, specifically for THWN to Enphase
            IQ/DG/TC conductor transitions or just THWN splices. </div>
          <br>
          <div class="gmail_quote">
            <div dir="ltr" class="gmail_attr">On Mon, Apr 26, 2021, 8:40
              PM Blake Gleason &lt;<a href="mailto:blake@sunlightandpower.com" target="_blank" rel="noreferrer">blake@sunlightandpower.com</a>&gt;
              wrote:<br>
            </div>
            <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
              <div dir="ltr">Corey,
                <div>Thank you!  Agreed, the message from Staubli&#39;s Eng
                  dept is much less confusing (with the exception of the
                  statement about THHN tending to be solid vs stranded).</div>
                <div>All -</div>
                <div>What are you folks using to transition from PV Wire
                  to THHN/THWN-2 inside a junction box?  We used to use
                  split bolts, which make an awesome electrical
                  connection, but are time-consuming and not easily
                  serviceable.  Wire nuts (the right ones) are Listed,
                  but never felt reliable for that purpose.  Same for
                  WAGO levers.  I hear about people using Buchanan
                  splice caps, but I wonder about trading one set of
                  crimping problems for another.  And of course, the
                  only problem with using THHN in an MC4 is that the
                  compression gland may not be as watertight as it is
                  with PVWire, and the Buchanans certainly are not
                  watertight.  Terminal blocks generally aren&#39;t listed,
                  definitely aren&#39;t watertight, and raise inspectors&#39;
                  eyebrows.  Why is this so hard for me??</div>
                <div>Best,</div>
                <div>Blake</div>
                <div>Thanks</div>
              </div>
              <br>
              <div class="gmail_quote">
                <div dir="ltr" class="gmail_attr">On Mon, Apr 26, 2021
                  at 5:19 PM Corey Shalanski &lt;<a href="mailto:coresolar@gmail.com" rel="noreferrer noreferrer" target="_blank">coresolar@gmail.com</a>&gt;
                  wrote:<br>
                </div>
                <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
                  <div dir="ltr">
                    <div>Blake,</div>
                    <div>In addition to Bryan&#39;s notes, here is some
                      unconfusing information directly from Stäubli&#39;s
                      engineering dept:</div>
                    <div dir="ltr">
                      <div>
                        <blockquote style="margin:0px 0px 0px 40px;border:none;padding:0px">
                          <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">The
                            answer is categorically no: <b>you cannot
                              use THHN wires with MC4 connectors.</b>
                             There are several reasons for this:<br>
                            1.     <u>Certification</u>: our MC4
                            connectors are certified to UL6703, which
                            only covers UL4703 PV wire or USE2 cable. 
                            Any other wire type is not covered by our
                            certification<br>
                            2.     <u>Internal validation</u>: we have
                            no internal testing or validation of how MC4
                            or Evo2 connectors perform with THHN
                            cables.  We therefore cannot warranty /
                            accept the use of THHN cables with our PV
                            connectors.  The allowable cables and
                            applications for our PV connectors is
                            clearly stated in the assembly instructions.<br>
                            3.     <u>Construction</u>: THHN cables use
                            very rigid PVC insulators, which behave very
                            differently than XPLE or TPE insulators that
                            are the most widely used on PV wires.  PVC
                            has a very low elastic range and easily
                            deforms permanently under load/thermal
                            cycling.  It is not a well-suited cable for
                            higher temperature or high temperature
                            fluctuating applications where
                            compression-type cable seals (i.e. cable
                            glands) are used.  Also, THHN cables tend to
                            be single-conductor solid core cables, which
                            are absolutely not allowed with crimp
                            terminations like the MC4 (or any other PV
                            connector on the market for that matter). 
                            They also are not allowed by UL6703.   <br>
                          </blockquote>
                        </blockquote>
                      </div>
                    </div>
                    <div>These comments were forwarded to me by Jeff
                      Wang, who works for Stäubli North America.</div>
                    <div>--</div>
                    <div>Corey Shalanski</div>
                    <div>Jah Light Solar</div>
                    <div>Portland, Jamaica</div>
                    <div><br>
                    </div>
                    <div class="gmail_quote">
                      <div dir="ltr" class="gmail_attr">On Mon, Apr 26,
                        2021 at 9:23 AM &lt;<a href="mailto:blake@sunlightandpower.com" rel="noreferrer noreferrer" target="_blank">blake@sunlightandpower.com</a>&gt;
                        wrote:<br>
                      </div>
                      <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><br>
                        <div dir="ltr">Bryan,
                          <div>Thank you for the link.  I am confused by
                            the &quot;PVC&quot; section you referenced.  Here&#39;s
                            the complete text:</div>
                          <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">  For
                            safety reasons Stäubli prohibits the use of
                            PVC cables.
                            Cables made from PVC can be connected to
                            MC4-Evo 2 since
                            the insulation material of the connector
                            (Polyamide) is suitable to
                            be connected to PVC. PVC cables usually have
                            an upper limiting
                            temperature of 70 °C, in fixed installations
                            sometimes 80 °C.  <br>
                          </blockquote>
                          <div>THHN/THWN-2 is made with PVC insulation,
                            so I assume that it falls under the category
                            of a &quot;PVC cable.&quot;</div>
                          <div>So, the first sentence seems to say that
                            it&#39;s not allowed by Staubli.  But then the
                            second sentence seems to say that is IS
                            allowed.  And then the third sentence
                            doesn&#39;t seem to be contemplating the most
                            common PVC wire type of all (in the US),
                            which is THHN/THWN-2, which has a 90 degree
                            rating?!</div>
                          <div>Can you help un-confuse me?</div>
                          <div>Thank you!</div>
                          <div>Blake</div>
                        </div>
                      </blockquote>
                    </div>
                  </div>
                </blockquote>
              </div>
            </blockquote>
          </div>
        </blockquote>
      </div>
      <pre>List sponsored by Redwood Alliance

Pay optional member dues here: <a href="http://re-wrenches.org" target="_blank" rel="noreferrer">http://re-wrenches.org</a>

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn&#39;t work, try the other:
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank" rel="noreferrer">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">http://www.members.re-wrenches.org</a>
</pre>
    </blockquote>
    <div>-- <br>
      
      
      
      
      
      
      
      
      
      
      <div>
        <p class="MsoNormal" style="line-height:normal"><b><span>Allan
              Sindelar</span></b><span><br>
          </span><a href="mailto:allan@sindelarsolar.com" target="_blank" rel="noreferrer"><span>allan@sindelarsolar.com</span></a><span><br>
          </span><span>NABCEP
            Certified PV Installation
            Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            Founder (Retired), <span>Positive
              Energy, Inc<span>.</span></span><br>
            <b>505 780-2738 cell</b></span><span><u></u><u></u></span></p>
        <p class="MsoNormal"><u></u> <u></u></p>
      </div>
    </div>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
Pay optional member dues here: <a href="http://re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://re-wrenches.org</a><br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
There are two list archives for searching. When one doesn&#39;t work, try the other:<br>
<a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" rel="noreferrer noreferrer" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>