<div dir="ltr"><div>Blake,</div><div><br></div><div>In addition to Bryan's notes, here is some unconfusing information directly from Stäubli's engineering dept:</div><div dir="ltr"><br></div><div dir="ltr"><div><blockquote style="margin:0 0 0 40px;border:none;padding:0px"><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">The answer is categorically no: <b>you cannot use THHN wires with MC4 connectors.</b> There are several reasons for this:<br>1. <u>Certification</u>: our MC4 connectors are certified to UL6703, which only covers UL4703 PV wire or USE2 cable. Any other wire type is not covered by our certification<br>2. <u>Internal validation</u>: we have no internal testing or validation of how MC4 or Evo2 connectors perform with THHN cables. We therefore cannot warranty / accept the use of THHN cables with our PV connectors. The allowable cables and applications for our PV connectors is clearly stated in the assembly instructions.<br>3. <u>Construction</u>: THHN cables use very rigid PVC insulators, which behave very differently than XPLE or TPE insulators that are the most widely used on PV wires. PVC has a very low elastic range and easily deforms permanently under load/thermal cycling. It is not a well-suited cable for higher temperature or high temperature fluctuating applications where compression-type cable seals (i.e. cable glands) are used. Also, THHN cables tend to be single-conductor solid core cables, which are absolutely not allowed with crimp terminations like the MC4 (or any other PV connector on the market for that matter). They also are not allowed by UL6703. </blockquote></blockquote></div></div><div><br></div><div>These comments were forwarded to me by Jeff Wang, who works for Stäubli North America.</div><div><br></div><div>--</div><div>Corey Shalanski</div><div>Jah Light Solar</div><div>Portland, Jamaica</div><div><br></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Mon, Apr 26, 2021 at 9:23 AM <<a href="mailto:blake@sunlightandpower.com">blake@sunlightandpower.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><br><div dir="ltr">Bryan,<div><br></div><div>Thank you for the link. I am confused by the "PVC" section you referenced. Here's the complete text:</div><div><br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"> For safety reasons Stäubli prohibits the use of PVC cables.
Cables made from PVC can be connected to MC4-Evo 2 since
the insulation material of the connector (Polyamide) is suitable to
be connected to PVC. PVC cables usually have an upper limiting
temperature of 70 °C, in fixed installations sometimes 80 °C. </blockquote><div><br></div><div>THHN/THWN-2 is made with PVC insulation, so I assume that it falls under the category of a "PVC cable."</div><div><br></div><div>So, the first sentence seems to say that it's not allowed by Staubli. But then the second sentence seems to say that is IS allowed. And then the third sentence doesn't seem to be contemplating the most common PVC wire type of all (in the US), which is THHN/THWN-2, which has a 90 degree rating?!</div><div><br></div><div>Can you help un-confuse me?</div><div><br></div><div>Thank you!</div><div>Blake</div></div>
</blockquote></div></div>