<html><head><meta http-equiv="content-type" content="text/html; charset=utf-8"></head><body dir="auto">I had a similar scenario a few years ago and looked at the Generac SSM, but for some reason(s) I cannot recall, could not go this route.&nbsp;<div>The system was on a house and the auto transfer switch and generator were in a shack that was unreasonable to trench too, and we did not want to rely on a wireless option.&nbsp;</div><div><br></div><div>The solution we came up with was a contact that would disconnect the inverters from the house panelboard upon a loss of voltage (grid).&nbsp;</div><div>Unfortunately we did not come up with a solution that would automatically reconnect the inverters once the grid was restored... because we couldn\u2019t reliably distinguish between the generator and the grid, so it required a manual reset once the customer could confirm they had grid power and not running off the generator.&nbsp;</div><div>The client said they often did not know that there was a power outage so there could be times they would not even know the inverters had shut off... so I ran a low voltage line to a LED light <span style="background-color: rgba(255, 255, 255, 0);">in their kitchen area </span>that would come on upon loss of grid and would go out when the inverters were manually reset.&nbsp;</div><div><br><div id="AppleMailSignature" dir="ltr">Benn Kilburn<div>SkyFire Energy</div><div>780-906-7807</div></div><div dir="ltr"><br>On Feb 25, 2021, at 6:40 AM, Nik Ponzio, Building Energy &lt;<a href="mailto:nponzio@buildingenergyus.com">nponzio@buildingenergyus.com</a>&gt; wrote:<br><br></div><blockquote type="cite"><div dir="ltr"><div dir="ltr">We are installing 25kW of PV on a service with an existing backup generator (Eaton 30KW) and auto transfer switch. Because of the remote location&nbsp;of the generator and transfer switch, we can not easily connect on the grid-side of the transfer switch as we usually do (without cutting a very long trench.) So we're looking for a way to lock out the solar during generator use. And then, ideally, reconnect the solar automatically when the grid is restored.&nbsp;<div><br></div><div>Is there an off-the-shelf product available at this point to accomplish this?&nbsp;</div><div><br></div><div>I see <a href="https://mailtrack.io/trace/link/7643522e54e5bd30057d2e139c7b93d1c488b655?url=https%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmsg23906.html&amp;userId=6273276&amp;signature=c4db635fbd2d1225">a thread on here</a> from a couple years ago that recommended the Generac SMM for this type of scenario. Any current thoughts on this approach?<div><br></div><div>Any suggestions would&nbsp;be appreciated.</div><div><br></div><div><br clear="all"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div><div dir="ltr">--<br>Nik Ponzio&nbsp;<br>Building Energy<br>1570 South Brownell Road<br>Williston, VT 05495</div><div dir="ltr">direct: 802-318-7003<br></div><div dir="ltr"><a href="mailto:nponzio@buildingenergyus.com" target="_blank">nponzio@buildingenergyus.com</a><br><a href="https://mailtrack.io/trace/link/058e994a3bba9674653a69dd2a6976e0914d2761?url=http%3A%2F%2Fwww.BuildingEnergyVT.com&amp;userId=6273276&amp;signature=8b5247886585b42b" target="_blank">http://www.BuildingEnergyVT.com</a>&nbsp;<div style="display:inline"></div><div style="display:inline"></div></div></div><div dir="ltr"><br></div><div dir="ltr"><img src="https://docs.google.com/a/buildingenergyus.com/uc?id=0Bw3V5dT4GvUmdkZJYnpfYWdZSG8&amp;export=download" width="66" height="96">&nbsp;<br></div><div dir="ltr"><div style="font-size:12.8px">"Building Solutions for a Sustainable Future"</div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div><img width="0" height="0" class="mailtrack-img" alt="" style="display:flex" src="https://mailtrack.io/trace/mail/7d06e8d95e1e703921e6c3468ea9bca0b0ec675e.png?u=6273276"></div>
</div></blockquote><blockquote type="cite"><div dir="ltr"><span>_______________________________________________</span><br><span>List sponsored by Redwood Alliance</span><br><span></span><br><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change listserver email address &amp; settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>There are two list archives for searching. When one doesn't work, try the other:</span><br><span><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br><span><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List rules &amp; etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></div></body></html>