<!DOCTYPE html PUBLIC "-//W3C//DTD HTML 4.01 Transitional//EN"><html><head><meta content="text/html;charset=UTF-8" http-equiv="Content-Type"></head><body ><div style="font-family: Verdana, Arial, Helvetica, sans-serif; font-size: 10pt;"><div><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">The Time of Use feature can support this request. I do understand that programming can be somewhat confusing in completely covering what you are wanting the generator can do. However, if you are wanting the generator to turn on only when the batteries are low and getting through the night then we can set the Time of Use to only turn on with specific&nbsp; hours and also charge up to specific SOC. We implemented this setting so that there is the ability to control how much fuel is used and not run the gen for long periods of time. The Time of Use settings are very customizable, if you would like to give our support team a call and we can help customize it to best fit your scenario.</span></span><br></div><div><br></div><div><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">As for updating the system itself, we offer different avenues of doing so. The first is the Wi-fi dongle that is connected to the inverter and to the customers home network. We also offer different aftermarket versions for customers with specific needs or if they don't have internet altogether. There is a ethernet version for those that don't want the over the air (OTA) connection to there wireless network or possibly if there router itself is a little to far away from where the unit is located. Simply running a ethernet cable to this specific dongle will connect them for monitoring and also allow for updates. The final version is for those true off grid installs where they are not worried about monitoring but do need to get the system updated. We have developed a custom design dongle that once inserted into the unit will perform the update on the inverter locally. Plug it in and wait for the final part of the software to finish and now your system will have the current version of software. You can then remove it and adjust the settings for the new features that were added.</span></span></div><div><br></div><div data-zbluepencil-ignore="true" id="Zm-_Id_-Sgn"><p style="margin: 0px" class=""><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">Thank you and have a blessed day,</span><span class="size" style="font-size:16px"><br></span></span></p><p style="margin: 0px" class=""><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">Dustin Douglas</span><span class="size" style="font-size:16px"><br></span></span></p><p style="margin: 0px" class=""><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">Sol Ark Engineering Support</span><span class="size" style="font-size:16px"><br></span></span></p><p style="margin: 0px" class=""><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">(972) 575-8875 x 108</span><span class="size" style="font-size:16px"><br></span></span></p><div><a href="http://www.sol-ark.com/" target="_blank"><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">www.sol-ark.com</span></span></a><br></div></div><div><br></div><div style="" data-zbluepencil-ignore="true" class="zmail_extra"><div><br></div><div id="Zm-_Id_-Sgn1">---- On Fri, 13 Nov 2020 08:46:31 -0600 <b>Jay &lt;jay.peltz@gmail.com&gt;</b> wrote ----<br></div><div><br></div><blockquote style="border-left: 1px solid rgb(204, 204, 204); padding-left: 6px; margin: 0px 0px 0px 5px;"><div dir="auto"><div dir="ltr">I\u2019m wondering how the firmware is updated? &nbsp;USB or other? &nbsp;I\u2019ve looked on the website but I couldn\u2019t find any instructions.&nbsp;<br></div><div dir="ltr"><br></div><div dir="ltr">Thx<br></div><div dir="ltr">Jay<br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><div><br></div><blockquote>On Nov 12, 2020, at 7:58 PM, Jeff Clearwater &lt;<a href="mailto:jeffc@villagepowerdesign.com" target="_blank">jeffc@villagepowerdesign.com</a>&gt; wrote:<br><br></blockquote></div><blockquote><div dir="ltr"><div>\ufeff  Thanks Dustin for keeping 
us up to date on Sol-Arks feature progress.<br></div><div> <br></div><div> While you are upgrading your firmware: :)<br></div><div> <br></div><div> So an essential feature for off-grid with a generator is to be able to 
program various SOC levels for generator start AND shuf-off after 
charge.&nbsp; 90% is way too high for many sunny climes and other 
configurations.&nbsp; Often batteries need a boost in the wee morning hours -
 when they drop below the preferred recharge point but that's only 
perhaps a few hours before the sun comes up - So say you want to start a
 gen to charge a Lead-acid battery at 50% or an LFP batter at 20% SOC 
but you only want to bring it through to the next often or possibly 
sunny morning.&nbsp; So you set it to run from 50% to 65% (or from 20%-40% 
for LFP) - knowing that the morning sun will take it the rest of the 
way.&nbsp; 90% would waste a ton of fuel in this scenario not too mention 
unwanted noise and wear and tear on the genny.&nbsp; Depending on the clients
 use profile, the climate, and relative size of the array and battery 
and gen, these figures could vary anywhere from 20% to 100%.&nbsp; So it's 
essential us off-grid installers have that flexibility.<br></div><div> <br></div><div> Also I know that your TOU settings might cover this (though not in all 
modes I believe) but another nice feature is to have 2 or 3 time periods
 with different start and stop settings (Sunny Island does this 
nicely).&nbsp; So if the minimum SOC is reached in the evening you might as 
well bring it up to a higher SOC for gen shut down as it needs to get 
through the entire night whereas if that minimum SOC start trigger is 
met after 3 AM&nbsp; it needs to only bring it to a lower SOC as described 
above.<br></div><div> <br></div><div> <span></span>I'm loving the Sol-Ark product so far but it is obvious the
 software is a work in progress - the architecture and thought behind it
 is an excellent foundation - thanks for your work and openness for 
input to make it even better.<br></div><div> <br></div><div> Best,<br></div><div> <br></div><div> Jeff<br></div><div> <br></div><div> <span>~~~~~~~~~~~<br> </span> </div><div class="x_-837807589moz-signature"><span>Jeff Clearwater</span><span><span><br> </span>Village Power Design<br> </span><span><span><span><a href="https://www.linkedin.com/in/jeff-clearwater-0622a312/" target="_blank">linkedin</a> </span></span></span><br> <span><span><a href="http://www.villagepowerdesign.com" target="_blank">www.villagepowerdesign.com</a></span><br> cell - <span class="colour" style="color:rgb(80, 80, 80)"><span class="size" style="font-size: inherit; display: inline; padding: 0px;">413-559-9763<br> ~~~~~~~~~~~~~~~~~~~~~~~</span></span></span></div><div><br></div><div><br></div><div><br></div><blockquote style="border: 0.0px none;"><div style="margin: 30.0px 25.0px 10.0px 25.0px;" class="x_-837807589__pbConvHr"><div style="width: 100.0%;border-top: 2.0px solid rgb(237,241,244);padding-top: 10.0px;"><div style="display: inline-block;white-space: nowrap;vertical-align: middle;width: 49.0%;"><a style="color: rgb(72,86,100);padding-right: 6.0px;font-weight: 500;text-decoration: none;" href="mailto:dustin@sol-ark.com" target="_blank">Dustin
 Douglas</a><br></div><div style="display: inline-block;white-space: nowrap;vertical-align: middle;width: 48.0%;text-align: right;"><span class="colour" style="color:#909AA4"><span style="padding-left: 6.0px;">November
 12, 2020 at 11:46 AM</span></span><br></div></div></div><div style="color: rgb(144,154,164);margin-left: 24.0px;margin-right: 24.0px;" class="x_-837807589__pbConvBody"><div style="font-family: Verdana, Arial, Helvetica, sans-serif;font-size: 10.0pt;"><div>Hi All,<br></div><div><br></div><div>First and foremost 
thank you for sharing your experiences the the Sol-Ark system. We try 
very hard to have different capabilities and add new features that make 
it flexible for the customer. The two-wire start is a feature however 
that we want to be seamless. In the instance where the customer is 
seeing the system shutdown once the generator shuts off has been 
addressed and fixed with a software update. With this update we are able
 to handle larger generators that tend to drift from 60hz. Please give 
our support team a call so that we can update the customer accordingly. 
We are also looking at adding more features including the ability 
exercise the generator in the near feature.<span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">&nbsp;<br></span></span></div><div><br></div><div><p class="" style="margin: 0.0px;"><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">Thank 
you and have a blessed day,</span><span class="size" style="font-size:16px"><br></span></span></p><p class="" style="margin: 0.0px;"><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">Dustin
 Douglas</span><span class="size" style="font-size:16px"><br></span></span></p><p class="" style="margin: 0.0px;"><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">Sol Ark Engineering Support</span><span class="size" style="font-size:16px"><br></span></span></p><p class="" style="margin: 0.0px;"><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">(972) 575-8875 x 108</span><span class="size" style="font-size:16px"><br></span></span></p><div><a href="http://www.sol-ark.com/" target="_blank"><span class="font" style="font-family:Calibri, Verdana, Arial, sans-serif, sans-serif"><span class="size" style="font-size:16px">www.sol-ark.com</span></span></a><br></div></div><div><br></div><div class="x_-837807589zmail_extra"><div><br></div><div>---- On Thu, 12 Nov 2020 08:08:51 -0600 <b>Jay <a class="x_-837807589moz-txt-link-rfc2396E" href="mailto:jay.peltz@gmail.com" target="_blank">&lt;jay.peltz@gmail.com&gt;</a></b> wrote ----<br></div><div><br></div></div><div><br></div></div><div><br></div><div>_______________________________________________<br>List sponsored 
by Redwood Alliance<br><br>List Address: <a class="x_-837807589moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change
 listserver email address
 &amp; settings:<br><a class="x_-837807589moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn't work, try the 
other:<br><a class="x_-837807589moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a class="x_-837807589moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a class="x_-837807589moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a class="x_-837807589moz-txt-link-freetext" href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div></div><div style="margin: 30.0px 25.0px 10.0px 25.0px;" class="x_-837807589__pbConvHr"><div style="width: 100.0%;border-top: 2.0px solid rgb(237,241,244);padding-top: 10.0px;"><div style="display: inline-block;white-space: nowrap;vertical-align: middle;width: 49.0%;"><a style="color: rgb(72,86,100);padding-right: 6.0px;font-weight: 500;text-decoration: none;" href="mailto:jay.peltz@gmail.com" target="_blank">Jay</a><br></div><div style="display: inline-block;white-space: nowrap;vertical-align: middle;width: 48.0%;text-align: right;"><span class="colour" style="color:#909AA4"><span style="padding-left: 6.0px;">November
 12, 2020 at 9:08 AM</span></span><br></div></div></div><div style="color: rgb(144,154,164);margin-left: 24.0px;margin-right: 24.0px;" class="x_-837807589__pbConvBody"><div dir="ltr">Hi Bill<br></div><div dir="ltr"><br></div><div dir="ltr">In the 
past I\u2019ve had similar issues with generators/inverters. Usually a relay 
on the output power wires that opens( disconnects) when the stop signal 
is sent works as the frequency doesn\u2019t slowly go down, it drops to 0 
instantly.&nbsp;<br></div><div dir="ltr">I don\u2019t know if it will fix your issue.&nbsp;<br></div><div dir="ltr"><br></div><div dir="ltr">Seems like solark needs to greatly 
improve their firmware.&nbsp;<br></div><div dir="ltr"><br></div><div dir="ltr">Jay<br></div><div dir="ltr"><br></div><div dir="ltr">Peltz power.&nbsp;<br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div><br></div><div><br></div><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>List Address: <a class="x_-837807589moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change
 listserver email address
 &amp; settings:<br><a class="x_-837807589moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn't work, try the 
other:<br><a class="x_-837807589moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a class="x_-837807589moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a class="x_-837807589moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a class="x_-837807589moz-txt-link-freetext" href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div></div><div style="margin: 30.0px 25.0px 10.0px 25.0px;" class="x_-837807589__pbConvHr"><div style="width: 100.0%;border-top: 2.0px solid rgb(237,241,244);padding-top: 10.0px;"><div style="display: inline-block;white-space: nowrap;vertical-align: middle;width: 49.0%;"><a style="color: rgb(72,86,100);padding-right: 6.0px;font-weight: 500;text-decoration: none;" href="mailto:bill@berkssolar.com" target="_blank">Bill
 Hennessy</a><br></div><div style="display: inline-block;white-space: nowrap;vertical-align: middle;width: 48.0%;text-align: right;"><span class="colour" style="color:#909AA4"><span style="padding-left: 6.0px;">November
 11, 2020 at 10:03 PM</span></span><br></div></div></div><div style="color: rgb(144,154,164);margin-left: 24.0px;margin-right: 24.0px;" class="x_-837807589__pbConvBody"><div style="font-family: Helvetica Neue, Helvetica, Arial, sans-serif;font-size: 16.0px;" class="x_-837807589ydp8c86a3ceyahoo-style-wrap"><div><div dir="ltr">Hi folks--We've also been disappointed with the 
Sol-Ark two-wire generator start. The unit starts at the charge set 
point, but the inverter will shut down for about a minute every time the
 generator stops running. After the minute wait, the inverter restarts 
and everything is fine. But it is aggravating for the homeowners to be 
left wondering in the dark.<br></div><div dir="ltr"><br></div><div dir="ltr">Sol-Ark says that when the generator 
shuts off, the frequency drops out of the Sol-Ark range and causes the 
inverter shut down. <br></div><div dir="ltr">They 
suggested we find a way to increase the generator speed to avoid the 
frequency drop at shutdown. This seems like a lame suggestion, since the
 generator has no idea of when the batteries will be satisfied--it only 
responds to the on/off signal from the Sol-Ark. I would think that the 
unit could be programmed to ignore the frequency drop when it sends the 
shut off signal to the generator. <span>The system has an an Ecogen 
15kW.</span><br></div><div dir="ltr"><br></div><div dir="ltr">Not having an exercise function is also a
 miss. As mentioned below, the time of use can be used, but one has to 
go out and play with the programming to check the generator.<br></div><div dir="ltr"><br></div><div dir="ltr">regards, bill<br></div><div dir="ltr"><br></div><div class="x_-837807589ydp8c86a3cesignature"><div>Bill
 Hennessy<br>Berks Solar, LLC<br>371 Centennial Rd<br>Mertztown, PA 
19539<br><br>o 610 682 4300<br>c 484 560 4666<br>NABCEP certified 
installer<br>PA contractor #44411<br><a class="x_-837807589moz-txt-link-abbreviated" href="http://www.berkssolar.com" target="_blank">www.berkssolar.com</a></div></div></div><div><br></div><div><br></div></div><div class="x_-837807589ydp84fbc9deyahoo_quoted"><div style="font-family: &quot;Helvetica Neue&quot;, Helvetica, Arial, sans-serif;font-size: 13.0px;color: rgb(38,40,42);"><div>On Wednesday, November 11, 2020, 8:20:57 PM EST, 
Chris Sparadeo <a class="x_-837807589moz-txt-link-rfc2396E" href="mailto:sparadeo.chris@gmail.com" target="_blank">&lt;sparadeo.chris@gmail.com&gt;</a> wrote:<br></div><div><br></div><div><br></div><div><div><div><div dir="ltr"><div><div>Thanks for the suggestion, Jay.&nbsp;<br></div><div><br></div><div>Yes,
 the Sol-Ark has a very basic and limited&nbsp;AGS for 2 wire compatible gen 
sets. Gen start can be programmed with voltage or SOC, however gen stop 
is not a function&nbsp;that can not be readily programmed. Instead, the 
Sol-Ark is programmed to charge the battery bank to 90% of&nbsp; the rated Ah
 capacity of the battery bank before&nbsp;turning off the generator. You can 
ultimately adjust this gen stop parameter to be based on a specific SOC 
or voltage, but I believe that doing so requires a call into tech 
support. The tech I spoke with updated&nbsp;a setting (having to do with 
a&nbsp;TOU&nbsp;parameter I believe) that was not accessible&nbsp;via the system 
interface. AGS&nbsp; from Schnieder, Outback and even Magnum are less clunky,
 but I am hoping that Sol-Ark will eventually come out with new 
programming to remediate these minor but nevertheless, important issues<br></div></div><div><br></div><div>-Chris<br></div></div><div><br></div><div class="x_-837807589ydp84fbc9deyiv4104453845gmail_quote"><div class="x_-837807589ydp84fbc9deyiv4104453845yqt6477094269"><div dir="ltr" class="x_-837807589ydp84fbc9deyiv4104453845gmail_attr">On Wed, Nov 11, 
2020 at 3:58 PM Jay &lt;<a rel="nofollow" href="mailto:jay.peltz@gmail.com" target="_blank">jay.peltz@gmail.com</a>&gt; wrote:<br></div></div></div><div><br></div><div><br></div><div>-- <br></div><div dir="ltr" class="x_-837807589ydp84fbc9deyiv4104453845gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div>Chris 
Sparadeo<br></div><div><br></div><div><br></div><div>C_802-369-4458<br></div><div>H_802-728-3059<br></div></div></div></div></div></div></div></div><div class="x_-837807589ydp84fbc9deyqt6477094269">_______________________________________________<br>List sponsored by Redwood Alliance<br><br>List Address: <a rel="nofollow" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change listserver email address &amp; 
settings:<br><a rel="nofollow" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There are two list archives for 
searching. When one doesn't work, try the other:<br><a rel="nofollow" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a rel="nofollow" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List rules &amp; etiquette:<br><a rel="nofollow" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check out or update participant bios:<br><a rel="nofollow" href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div></div></div></div><div><br></div><div><br></div><div>_______________________________________________<br>List
 sponsored by Redwood Alliance<br><br>List Address: <a class="x_-837807589moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change
 listserver email address
 &amp; settings:<br><a class="x_-837807589moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>There
 are two list archives for searching. When one doesn't work, try the 
other:<br><a class="x_-837807589moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br><a class="x_-837807589moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
 rules &amp; etiquette:<br><a class="x_-837807589moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a><br><br>Check
 out or update participant bios:<br><a class="x_-837807589moz-txt-link-freetext" href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a><br><br></div></div></blockquote><div><br></div><div><span>_______________________________________________</span><br></div><div><span>List sponsored by Redwood Alliance</span><br></div><div><span></span><br></div><div><span>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br></div><div><span></span><br></div><div><span>Change listserver email address &amp; settings:</span><br></div><div><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br></div><div><span></span><br></div><div><span>There are two list archives for searching. When one doesn't work, try the other:</span><br></div><div><span><a href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" target="_blank">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a></span><br></div><div><span><a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br></div><div><span></span><br></div><div><span>List rules &amp; etiquette:</span><br></div><div><span><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">http://www.re-wrenches.org/etiquette.htm</a></span><br></div><div><span></span><br></div><div><span>Check out or update participant bios:</span><br></div><div><span><a href="http://www.members.re-wrenches.org" target="_blank">http://www.members.re-wrenches.org</a></span><br></div><div><span></span><br></div></div></blockquote></div><div>_______________________________________________ <br></div><div>List sponsored by Redwood Alliance <br></div><div> <br></div><div>List Address: RE-wrenches@lists.re-wrenches.org <br></div><div> <br></div><div>Change listserver email address &amp; settings: <br></div><div>http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org <br></div><div> <br></div><div>There are two list archives for searching. When one doesn't work, try the other: <br></div><div>https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/ <br></div><div>http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org <br></div><div> <br></div><div>List rules &amp; etiquette: <br></div><div>http://www.re-wrenches.org/etiquette.htm <br></div><div> <br></div><div>Check out or update participant bios: <br></div><div>http://www.members.re-wrenches.org <br></div><div> <br></div></blockquote></div><div><br></div></div><br></body></html>