    Dave,<br>
    <br>
    If the AHJ is happy with the remote power down of the inverter (and
    now the PV array if on the roof or if it enters a building other
    than a power shed) I'd say that's great. You can't make the inverter
    much safer than shutting it down. A remote battery disconnect may
    only de-energize another few feet of battery cable anyway. But I
    know in California it will be a while until the 2020 NEC is adopted,
    when it is adopted, you might find the AHJ just saying it has to be
    done with a battery disconnect.<br>
    <br>
    If you are putting in a remote power off circuit or remote
    disconnect: does it get treated as fire safety equipment? Special MC
    cable? Metal conduit? Remote shut switch off grouped with the
    service disconnect? Is all of the equipment listed for emergency
    shut use? Is it good enough for a nuclear power plant safety system
    too? Where do we stop?<br>
    <br>
    Does anyone wonder why the cabin in the woods flies under the radar
    rather than attempting to comply with the excess of regulations that
    get heaped on a small power system?<br>
    <br>
    Kent Osterberg<br>
    Blue Mountain Solar<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/20/2020 8:50 AM, Dave Angelini
      Offgrid Solar wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:5daa715ad07949ac8f05a48c17ca4624@127.0.0.1">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <p>Thanks Kent,</p>
      <p>A question, most of the Sierra AHJ's only care, and that is
        rare, that there is a remote power off like Outback and
        Schneider have already. I understand it is not a battery disco,
        and even though there is one in these systems, what is your
        response please? </p>
      <p>I mostly dislike power sheds as people need an excuse to go
        there and observe. I mostly use a garage or outside house wall
        to build a bat room. Appreciate your thoughts. Insurance issues
        are not as important these days as many of us no longer can get
        it<img title="Cry"
          src="cid:part1.317BB829.8F17CCB4@coveoregon.com" alt="Cry"
          class="" border="0"></p>
      <div>
        <pre> </pre>
        <pre><strong><span style="font-size: small;">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank" moz-do-not-send="true">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net" moz-do-not-send="true">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
      </div>
      <p>On Mon, 19 Oct 2020 22:33:03 -0700, Kent Osterberg <a
          class="moz-txt-link-rfc2396E"
          href="mailto:kent@coveoregon.com" moz-do-not-send="true">&lt;kent@coveoregon.com&gt;</a>
        wrote:</p>
      <blockquote type="cite" style="padding-left:5px;
        border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- html ignored -->
        <!-- head ignored -->
        <!-- meta ignored -->Ray,<br>
        <br>
        Per NEC 480 batteries below 48 volts didn't need a readily
        accessible disconnect within site of the batteries. That's
        unchanged in the 2020 Code, you don't have to have a readily
        accessible disconnect within site of the batteries. That's a
        good thing considering the environment near lead acid batteries.
        A disconnect switch still isn't required in the 48-volt battery
        room.<br>
        <br>
        Yes, if you put a 48-volt battery in a one or two-family
        dwelling, an outside (remote) emergency disconnect is required.
        That is going to be a pain that may add hundreds of dollars to
        the cost of small off-grid systems. You might get away with a
        mushroom switch and a 24-volt tap on the batteries to activate a
        remote trip breaker. But considering that it is a fire-safety
        related circuit it is probably best to spend the money for the
        bird box.<br>
        <br>
        At the very least 480.7(B) should make off-grid folks think
        about using a power shed. The power shed is not a dwelling so
        2020 NEC 480.7(B) doesn't apply. <br>
        <br>
        Kent Osterberg<br>
        Blue Mountain Solar<br>
        <br>
        <br>
        <div class="moz-cite-prefix">On 10/19/2020 8:34 PM, Ray wrote:</div>
        <blockquote type="cite" style="padding-left:5px;
          border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- meta ignored -->
          <p>I've used Blue Planet, so I guess I have used an actual UL
            listed ESS, even though they don't include the charge
            controller or inverter.  I knew they were UL, but I double
            checked and it is the UL 9540 standard mentioned in 706. So
            in this case, we could ignore 480, but are held to 706. 
            Regardless of 480 or 706, both are possibly requiring the
            outside remote disconnect.  Besides Midnite's remote trip
            breakers, and the dreaded Bird House, what other options are
            there to meet this new requirement?   Can the Blue Planet be
            tripped remotely?</p>
          <p>and still my initial question: </p>
          <p>Under 480.7, are batteries below 60v still required to have
            the remote disconnect?  They are exempted from having a
            disconnect at all in 480.7(A)......quite confusing.  </p>
          <pre class="moz-signature">Ray Walters
Remote Solar
303 505-8760</pre>
          <div class="moz-cite-prefix">On 10/19/20 7:06 PM, Jerry Shafer
            wrote:</div>
          <blockquote type="cite" style="padding-left:5px;
            border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- meta ignored -->
            <div dir="auto">Wrenches
              <div dir="auto">Blue planet are fire and UL listed systems
                both on there 48 Volt and the LX flavors</div>
              <div dir="auto">Jerry</div>
            </div>
            <br>
            <div class="gmail_quote">
              <div class="gmail_attr" dir="ltr">On Mon, Oct 19, 2020,
                5:51 PM Ray &lt;<a href="mailto:ray@solarray.com"
                  moz-do-not-send="true">ray@solarray.com</a>&gt; wrote:</div>
              <blockquote class="gmail_quote" style="margin: 0 0 0 .8ex;
                border-left: 1px #ccc solid; padding-left: 1ex;">
                <div>
                  <p>The notes in the NEC 2020 Handbook for article 706
                    clearly state that 706 only covers ESS which is an
                    assembly of components, and that the total assembly
                    must be listed under UL 9540.  </p>
                  <p>Further it states: "<em> A group of separate
                      components that includes storage batteries, that
                      is provided with support systems (racks), charge
                      controllers, and inverters, and that does NOT have
                      an overall listing as an ESS is a storage battery
                      system and as such is subject to the requirements
                      of article 480"</em></p>
                  <p>and just in case someone says the notes don't
                    matter, 706.5 says: "<em>Energy Storage systems
                      shall be listed"</em>.</p>
                  <p>So, since I have never used an actual listed ESS,
                    I'm back to 480. Specifically, 480.7 (A) says we
                    need a disconnect for batteries over 60 vdc (48v
                    should be exempt) and then 480.7(B) says houses need
                    to have an outside disconnect for the batteries
                    labeled "Emergency Disconnect".  </p>
                  <p>So here's the real question:   Does 480.7(A) exempt
                    us from 480.7(B)?  </p>
                  <pre>Ray Walters
Remote Solar
303 505-8760</pre>
                  <div>On 3/9/19 8:08 PM, Brian Mehalic wrote:</div>
                  <blockquote type="cite" style="padding-left:5px;
                    border-left:#1010ff 2px solid; margin-left:5px;
                    width:100%">
                    <div dir="ltr">Hi Glenn, I don't completely agree
                      with your interpretation of ESS systems and the
                      application of Article 706.  Yes, an ESS <em>could</em>
                      provide 120/240 VAC (e.g. the Powerwall), but the
                      figures in Article 690 show three different
                      configurations where the output of the ESS is not
                      AC, and where the ESS disconnect comes before any
                      power electronics (like a multimode inverter, as
                      shown in the AC and DC coupled systems) or loads
                      (as shown in the stand-alone system). Are those
                      ESS connected to other systems which utilize
                      stored energy to provide AC power? Yes, but the
                      key is "connected to other systems" - in many
                      cases the ESS only provides DC.  In fact the
                      definition of ESS clearly states this - it <em>can</em> have
                      AC or DC output, and it <em>may</em> include
                      power electronics (but may not).
                      <div> </div>
                      <div>
                        <div>
                          <div>
                            <div dir="ltr">
                              <div dir="ltr">
                                <div>
                                  <div dir="ltr">
                                    <div>
                                      <div dir="ltr">
                                        <div>
                                          <div dir="ltr">
                                            <div>
                                              <div dir="ltr">
                                                <div>My understanding is
                                                  that the 60 volt limit
                                                  (which is obviously
                                                  problematic in a world
                                                  where 48 VDC batteries
                                                  and ESS are very
                                                  common) was inserted
                                                  in order to exempt
                                                  other devices that
                                                  store energy (such as
                                                  UPS, or battery backup
                                                  in fire alarms/exit
                                                  signage/etc.) from the
                                                  706 requirements.</div>
                                                <div> </div>
                                                <div>Cheers,</div>
                                                <div> </div>
                                                <div>Brian Mehalic <br>
                                                  NABCEP Certified Solar
                                                  PV Installation
                                                  Professional\u2122 R031508-59</div>
                                                <div>National Electrical
                                                  CodeŽ CMP-4 Member</div>
                                                <div>(520) 204-6639<br>
                                                  <div> </div>
                                                  <div>
                                                    <div>
                                                      <div>Solar Energy
                                                        International<br>
                                                        <a
                                                          href="http://www.solarenergy.org"
moz-do-not-send="true">http://www.solarenergy.org</a></div>
                                                    </div>
                                                  </div>
                                                </div>
                                                <div> </div>
                                                <div>SEI Professional
                                                  Services</div>
                                                <div><a
                                                    href="http://www.seisolarpros.com"
moz-do-not-send="true"><span style="font-size: 12.8px;">http://www.s</span>eisolarpros.com</a></div>
                                                <div> </div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                    <br>
                    <div class="gmail_quote">
                      <div class="gmail_attr" dir="ltr">On Sat, Mar 9,
                        2019 at 4:07 PM Glenn Burt &lt;<a
                          href="mailto:glenn.burt@glbcc.com"
                          moz-do-not-send="true">glenn.burt@glbcc.com</a>&gt;
                        wrote:</div>
                      <blockquote class="gmail_quote" style="margin: 0px
                        0px 0px 0.8ex; border-left: 1px solid #cccccc;
                        padding-left: 1ex;">Hi Ray,<br>
                        <br>
                        This is a conversation I have had some time ago
                        with a number of my fellow inspectors and code
                        experts. When the 2017 NEC came out, I agreed
                        with Mike Holt and Bill Brooks' assessment that
                        the new article was poorly written and did not
                        apply to most systems being installed today.
                        After much discussion through my Cadmus network
                        of authorities, it emerged that indeed 706
                        apples to the typical residential systems.<br>
                        So Energy Storage Systems (ESS) are the point of
                        article 706, and I believe that the key point is
                        that the SYSTEM is generating AC voltage of
                        120VAC or 240VAC, making the system fall under
                        article 706.<br>
                        <br>
                        Batteries themselves are minimally covered by
                        NEC 480, NFPA 1, and the IFC as applicable
                        locally.<br>
                        So, the bottom line is that the new article does
                        cover the work we do when systems provide or
                        interface with 120VAC or above (making the
                        system operation exceeding the 60V AC trigger).<br>
                        <br>
                        My initial problem was believing that the
                        article applied to a component (the battery
                        bank), and not the system (all components taken
                        together as a generator/storage system). It is
                        an easy misunderstanding to make.<br>
                        <br>
                        Hope this helps!<br>
                        <br>
                        -Glenn Burt<br>
                        <br>
                        -----Original Message-----<br>
                        From: RE-wrenches &lt;<a
                          href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                          moz-do-not-send="true">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;
                        On Behalf Of Ray<br>
                        Sent: Saturday, March 09, 2019 12:41 PM<br>
                        To: RE-wrenches &lt;<a
                          href="mailto:re-wrenches@lists.re-wrenches.org"
                          moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                        Cc: Bill Brooks &lt;<a
                          href="mailto:billb@energy808.com"
                          moz-do-not-send="true">billb@energy808.com</a>&gt;;
                        Bill Brooks &lt;<a
                          href="mailto:billbrooks7@yahoo.com"
                          moz-do-not-send="true">billbrooks7@yahoo.com</a>&gt;<br>
                        Subject: [RE-wrenches] NEC for Batteries &lt;
                        60v ??<br>
                        <br>
                        Hi Everyone;<br>
                        <br>
                        I'm updating all my verbage on plansets, and I
                        just realized that the newly created article 706
                        covering Energy Storage Systems is only for Over
                        60 VDC (706.1)  Also article 480 for batteries
                        only requires disconnecting means over 60 VDC ?!
                        (480.7).   I'm not about to not have a
                        disconnect, so now that NEC pulled battery
                        systems out of 690,  where do we go for guidance
                        on normal battery systems: 12, 24, 48 VDC?<br>
                        <br>
                        Overall, I welcome most of the changes in NEC
                        2017, like separating off grid systems into
                        articles 706, and 710, but it seems us off grid
                        installers need some more clarification.<br>
                        <br>
                        Thanks,<br>
                        <br>
                        --<br>
                        Ray Walters<br>
                        Remote Solar<br>
                        303 505-8760<br>
                        <br>
                        _______________________________________________<br>
                        List sponsored by Redwood Alliance<br>
                        <br>
                        List Address: <a
                          href="mailto:RE-wrenches@lists.re-wrenches.org"
                          moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                        <br>
                        Change listserver email address &amp; settings:<br>
                        <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                          moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                        <br>
                        List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                          moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                        <br>
                        List rules &amp; etiquette:<br>
                        <a
                          href="http://www.re-wrenches.org/etiquette.htm"
                          moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                        <br>
                        Check out or update participant bios:<br>
                        <a href="http://www.members.re-wrenches.org"
                          moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                        <br>
                        <br>
                        _______________________________________________<br>
                        List sponsored by Redwood Alliance<br>
                        <br>
                        List Address: <a
                          href="mailto:RE-wrenches@lists.re-wrenches.org"
                          moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                        <br>
                        Change listserver email address &amp; settings:<br>
                        <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                          moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                        <br>
                        List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                          moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                        <br>
                        List rules &amp; etiquette:<br>
                        <a
                          href="http://www.re-wrenches.org/etiquette.htm"
                          moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                        <br>
                        Check out or update participant bios:<br>
                        <a href="http://www.members.re-wrenches.org"
                          moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                      </blockquote>
                    </div>
                    <br>
                    <fieldset></fieldset>
                    <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
                  </blockquote>
                </div>
                _______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                List Address: <a
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address &amp; settings:<br>
                <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                  moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                There are two list archives for searching. When one
                doesn't work, try the other:<br>
                <a
                  href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
                  moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
                <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
                  moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
                <br>
                List rules &amp; etiquette:<br>
                <a href="http://www.re-wrenches.org/etiquette.htm"
                  moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a href="http://www.members.re-wrenches.org"
                  moz-do-not-send="true">http://www.members.re-wrenches.org</a><br>
              </blockquote>
            </div>
            <br>
            <fieldset class="mimeAttachmentHeader"></fieldset>
            <pre class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org" moz-do-not-send="true">http://www.members.re-wrenches.org</a>

</pre>
          </blockquote>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <pre class="moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org" moz-do-not-send="true">http://www.members.re-wrenches.org</a>

</pre>
        </blockquote>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org" moz-do-not-send="true">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>