    Ray,<br>
    <br>
    Per NEC 480 batteries below 48 volts didn't need a readily
    accessible disconnect within site of the batteries. That's unchanged
    in the 2020 Code, you don't have to have a readily accessible
    disconnect within site of the batteries. That's a good thing
    considering the environment near lead acid batteries. A disconnect
    switch still isn't required in the 48-volt battery room.<br>
    <br>
    Yes, if you put a 48-volt battery in a one or two-family dwelling,
    an outside (remote) emergency disconnect is required. That is going
    to be a pain that may add hundreds of dollars to the cost of small
    off-grid systems. You might get away with a mushroom switch and a
    24-volt tap on the batteries to activate a remote trip breaker. But
    considering that it is a fire-safety related circuit it is probably
    best to spend the money for the bird box.<br>
    <br>
    At the very least 480.7(B) should make off-grid folks think about
    using a power shed. The power shed is not a dwelling so 2020 NEC
    480.7(B) doesn't apply. <br>
    <br>
    Kent Osterberg<br>
    Blue Mountain Solar<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/19/2020 8:34 PM, Ray wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:e40934be-85dc-c624-4261-6d886b34a4ce@solarray.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <p>I've used Blue Planet, so I guess I have used an actual UL
        listed ESS, even though they don't include the charge controller
        or inverter.  I knew they were UL, but I double checked and it
        is the UL 9540 standard mentioned in 706. So in this case, we
        could ignore 480, but are held to 706.  Regardless of 480 or
        706, both are possibly requiring the outside remote disconnect. 
        Besides Midnite's remote trip breakers, and the dreaded Bird
        House, what other options are there to meet this new
        requirement?   Can the Blue Planet be tripped remotely?<br>
      </p>
      <p>and still my initial question: <br>
      </p>
      <p>Under 480.7, are batteries below 60v still required to have the
        remote disconnect?  They are exempted from having a disconnect
        at all in 480.7(A)......quite confusing.  <br>
      </p>
      <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
      <div class="moz-cite-prefix">On 10/19/20 7:06 PM, Jerry Shafer
        wrote:<br>
      </div>
      <blockquote type="cite"
cite="mid:CAMUFgmV0cpB_PCN724mVZ+nsjsRH7ZW5n=M3o7EkH5SoKVGAyQ@mail.gmail.com">
        <meta http-equiv="content-type" content="text/html;
          charset=UTF-8">
        <div dir="auto">Wrenches
          <div dir="auto">Blue planet are fire and UL listed systems
            both on there 48 Volt and the LX flavors</div>
          <div dir="auto">Jerry</div>
        </div>
        <br>
        <div class="gmail_quote">
          <div dir="ltr" class="gmail_attr">On Mon, Oct 19, 2020, 5:51
            PM Ray &lt;<a href="mailto:ray@solarray.com"
              moz-do-not-send="true">ray@solarray.com</a>&gt; wrote:<br>
          </div>
          <blockquote class="gmail_quote" style="margin:0 0 0
            .8ex;border-left:1px #ccc solid;padding-left:1ex">
            <div>
              <p>The notes in the NEC 2020 Handbook for article 706
                clearly state that 706 only covers ESS which is an
                assembly of components, and that the total assembly must
                be listed under UL 9540.  <br>
              </p>
              <p>Further it states: "<i> A group of separate components
                  that includes storage batteries, that is provided with
                  support systems (racks), charge controllers, and
                  inverters, and that does NOT have an overall listing
                  as an ESS is a storage battery system and as such is
                  subject to the requirements of article 480"</i></p>
              <p>and just in case someone says the notes don't matter,
                706.5 says: "<i>Energy Storage systems shall be listed"</i>.</p>
              <p>So, since I have never used an actual listed ESS, I'm
                back to 480. Specifically, 480.7 (A) says we need a
                disconnect for batteries over 60 vdc (48v should be
                exempt) and then 480.7(B) says houses need to have an
                outside disconnect for the batteries labeled "Emergency
                Disconnect".  <br>
              </p>
              <p>So here's the real question:   Does 480.7(A) exempt us
                from 480.7(B)?  <br>
              </p>
              <pre cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
              <div>On 3/9/19 8:08 PM, Brian Mehalic wrote:<br>
              </div>
              <blockquote type="cite">
                <div dir="ltr">Hi Glenn, I don't completely agree with
                  your interpretation of ESS systems and the application
                  of Article 706.  Yes, an ESS <i>could</i> provide
                  120/240 VAC (e.g. the Powerwall), but the figures in
                  Article 690 show three different configurations where
                  the output of the ESS is not AC, and where the ESS
                  disconnect comes before any power electronics (like a
                  multimode inverter, as shown in the AC and DC coupled
                  systems) or loads (as shown in the stand-alone
                  system). Are those ESS connected to other systems
                  which utilize stored energy to provide AC power? Yes,
                  but the key is "connected to other systems" - in many
                  cases the ESS only provides DC.  In fact the
                  definition of ESS clearly states this - it <i>can</i> have
                  AC or DC output, and it <i>may</i> include power
                  electronics (but may not).
                  <div><br>
                  </div>
                  <div>
                    <div>
                      <div>
                        <div dir="ltr" data-smartmail="gmail_signature">
                          <div dir="ltr">
                            <div>
                              <div dir="ltr">
                                <div>
                                  <div dir="ltr">
                                    <div>
                                      <div dir="ltr">
                                        <div>
                                          <div dir="ltr">
                                            <div>My understanding is
                                              that the 60 volt limit
                                              (which is obviously
                                              problematic in a world
                                              where 48 VDC batteries and
                                              ESS are very common) was
                                              inserted in order to
                                              exempt other devices that
                                              store energy (such as UPS,
                                              or battery backup in fire
                                              alarms/exit signage/etc.)
                                              from the 706 requirements.</div>
                                            <div><br>
                                            </div>
                                            <div>Cheers,</div>
                                            <div><br>
                                            </div>
                                            <div>Brian Mehalic <br>
                                              NABCEP Certified Solar PV
                                              Installation
                                              Professional\u2122 R031508-59</div>
                                            <div>National Electrical
                                              CodeŽ CMP-4 Member</div>
                                            <div>(520) 204-6639<br>
                                              <div><br>
                                              </div>
                                              <div>
                                                <div>
                                                  <div>Solar Energy
                                                    International<br>
                                                    <a
                                                      href="http://www.solarenergy.org"
                                                      target="_blank"
                                                      rel="noreferrer"
                                                      moz-do-not-send="true">http://www.solarenergy.org</a></div>
                                                </div>
                                              </div>
                                            </div>
                                            <div><br>
                                            </div>
                                            <div>SEI Professional
                                              Services</div>
                                            <div><a
                                                href="http://www.seisolarpros.com"
                                                target="_blank"
                                                rel="noreferrer"
                                                moz-do-not-send="true"><span
style="font-size:12.8px">http://www.s</span>eisolarpros.com</a><br>
                                            </div>
                                            <div><br>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                      <br>
                    </div>
                  </div>
                </div>
                <br>
                <div class="gmail_quote">
                  <div dir="ltr" class="gmail_attr">On Sat, Mar 9, 2019
                    at 4:07 PM Glenn Burt &lt;<a
                      href="mailto:glenn.burt@glbcc.com" target="_blank"
                      rel="noreferrer" moz-do-not-send="true">glenn.burt@glbcc.com</a>&gt;
                    wrote:<br>
                  </div>
                  <blockquote class="gmail_quote" style="margin:0px 0px
                    0px 0.8ex;border-left:1px solid
                    rgb(204,204,204);padding-left:1ex">Hi Ray,<br>
                    <br>
                    This is a conversation I have had some time ago with
                    a number of my fellow inspectors and code experts.
                    When the 2017 NEC came out, I agreed with Mike Holt
                    and Bill Brooks' assessment that the new article was
                    poorly written and did not apply to most systems
                    being installed today. After much discussion through
                    my Cadmus network of authorities, it emerged that
                    indeed 706 apples to the typical residential
                    systems.<br>
                    So Energy Storage Systems (ESS) are the point of
                    article 706, and I believe that the key point is
                    that the SYSTEM is generating AC voltage of 120VAC
                    or 240VAC, making the system fall under article 706.<br>
                    <br>
                    Batteries themselves are minimally covered by NEC
                    480, NFPA 1, and the IFC as applicable locally.<br>
                    So, the bottom line is that the new article does
                    cover the work we do when systems provide or
                    interface with 120VAC or above (making the system
                    operation exceeding the 60V AC trigger).<br>
                    <br>
                    My initial problem was believing that the article
                    applied to a component (the battery bank), and not
                    the system (all components taken together as a
                    generator/storage system). It is an easy
                    misunderstanding to make.<br>
                    <br>
                    Hope this helps!<br>
                    <br>
                    -Glenn Burt<br>
                    <br>
                    -----Original Message-----<br>
                    From: RE-wrenches &lt;<a
                      href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                      target="_blank" rel="noreferrer"
                      moz-do-not-send="true">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;
                    On Behalf Of Ray<br>
                    Sent: Saturday, March 09, 2019 12:41 PM<br>
                    To: RE-wrenches &lt;<a
                      href="mailto:re-wrenches@lists.re-wrenches.org"
                      target="_blank" rel="noreferrer"
                      moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                    Cc: Bill Brooks &lt;<a
                      href="mailto:billb@energy808.com" target="_blank"
                      rel="noreferrer" moz-do-not-send="true">billb@energy808.com</a>&gt;;
                    Bill Brooks &lt;<a
                      href="mailto:billbrooks7@yahoo.com"
                      target="_blank" rel="noreferrer"
                      moz-do-not-send="true">billbrooks7@yahoo.com</a>&gt;<br>
                    Subject: [RE-wrenches] NEC for Batteries &lt; 60v ??<br>
                    <br>
                    Hi Everyone;<br>
                    <br>
                    I'm updating all my verbage on plansets, and I just
                    realized that the newly created article 706 covering
                    Energy Storage Systems is only for Over 60 VDC
                    (706.1)  Also article 480 for batteries only
                    requires disconnecting means over 60 VDC ?!
                    (480.7).   I'm not about to not have a disconnect,
                    so now that NEC pulled battery systems out of 690, 
                    where do we go for guidance on normal battery
                    systems: 12, 24, 48 VDC?<br>
                    <br>
                    Overall, I welcome most of the changes in NEC 2017,
                    like separating off grid systems into articles 706,
                    and 710, but it seems us off grid installers need
                    some more clarification.<br>
                    <br>
                    Thanks,<br>
                    <br>
                    --<br>
                    Ray Walters<br>
                    Remote Solar<br>
                    303 505-8760<br>
                    <br>
                    _______________________________________________<br>
                    List sponsored by Redwood Alliance<br>
                    <br>
                    List Address: <a
                      href="mailto:RE-wrenches@lists.re-wrenches.org"
                      target="_blank" rel="noreferrer"
                      moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                    <br>
                    Change listserver email address &amp; settings:<br>
                    <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                    <br>
                    List rules &amp; etiquette:<br>
                    <a href="http://www.re-wrenches.org/etiquette.htm"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                    <br>
                    Check out or update participant bios:<br>
                    <a href="http://www.members.re-wrenches.org"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                    <br>
                    <br>
                    _______________________________________________<br>
                    List sponsored by Redwood Alliance<br>
                    <br>
                    List Address: <a
                      href="mailto:RE-wrenches@lists.re-wrenches.org"
                      target="_blank" rel="noreferrer"
                      moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                    <br>
                    Change listserver email address &amp; settings:<br>
                    <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                    <br>
                    List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                    <br>
                    List rules &amp; etiquette:<br>
                    <a href="http://www.re-wrenches.org/etiquette.htm"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                    <br>
                    Check out or update participant bios:<br>
                    <a href="http://www.members.re-wrenches.org"
                      rel="noreferrer noreferrer" target="_blank"
                      moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                    <br>
                  </blockquote>
                </div>
                <br>
                <fieldset></fieldset>
                <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noreferrer" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
              </blockquote>
            </div>
            _______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a
              href="mailto:RE-wrenches@lists.re-wrenches.org"
              target="_blank" rel="noreferrer" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              rel="noreferrer noreferrer" target="_blank"
              moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            There are two list archives for searching. When one doesn't
            work, try the other:<br>
            <a
              href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/"
              rel="noreferrer noreferrer" target="_blank"
              moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a><br>
            <a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org"
              rel="noreferrer noreferrer" target="_blank"
              moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm"
              rel="noreferrer noreferrer" target="_blank"
              moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a href="http://www.members.re-wrenches.org" rel="noreferrer
              noreferrer" target="_blank" moz-do-not-send="true">http://www.members.re-wrenches.org</a><br>
            <br>
          </blockquote>
        </div>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/" moz-do-not-send="true">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org" moz-do-not-send="true">http://www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

There are two list archives for searching. When one doesn't work, try the other:
<a class="moz-txt-link-freetext" href="https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/">https://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/</a>
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>