Hi Don and Wrenches,<br>
<br>
I have commissioned four new Ensemble systems over the past two weeks.
All storage additions to existing PV systems with Enphase
microinverters. Although there are parts of the process that are a bit
clunky, we have not had the problems you mention. I followed the
instructions in the tech brief "Ensemble Commissioning via Installer
Toolkit <span style="display: inline; font-size: inherit; padding: 0px;"
class="__postbox-detected-content __postbox-detected-date"
__postbox-detected-content="__postbox-detected-date">3.0,"</span> linked
at <a
href="https://enphase.com/en-us/certification-support-program-guidelines">https://enphase.com/en-us/certification-support-program-guidelines</a>
(direct link to the PDF is <a
href="https://enphase.com/sites/default/files/Tech%20Brief%20-%20Ensemble%20Commissioning%20via%20Installer%20Toolkit%203.0.pdf">https://enphase.com/sites/default/files/Tech%20Brief%20-%20Ensemble%20Commissioning%20via%20Installer%20Toolkit%203.0.pdf</a>).<br>
<br>
My experience is that each of the four Enpower microgrid interconnection
devices we've installed started up in passthrough mode, so if input
breakers are on in the MID, backup loads have had power before
commissioning is completed, and power has remained on for those backup
loads even after we turned off the PV and ESS disconnects to wait for
utility PTO after doing commissioning and functional testing.<br>
<br>
It did take us some time to do the Envoy software update before
commissioning, and the system does require a second trip for functional
testing after the Encharge battery software updates have been done (up
to 12 hours). I haven't stuck on site for the Encharge/Enpower software
updates, but
it looks like they are taking <span style="display: inline; font-size:
inherit; padding: 0px;" class="__postbox-detected-content
__postbox-detected-date"
__postbox-detected-content="__postbox-detected-date">4-6</span> hours
for us, based on percentage done
by the time I've left the site (system sizes from <span style="display:
inline; font-size: inherit; padding: 0px; color: rgb(0, 0, 0);"
class="__postbox-detected-content __postbox-detected-date"
__postbox-detected-content="__postbox-detected-date">10.08</span> kWh to
<span style="display: inline; font-size: inherit; padding: 0px;"
class="__postbox-detected-content __postbox-detected-date"
__postbox-detected-content="__postbox-detected-date">20.16</span>
kWh). Yeah, it's a second trip. I've used the trip to meet with
electrical inspectors for these first systems. <br>
<br>
One "trick" I've used on the Envoy software update is that you once you
scan in the serial numbers of each Enpower & Encharge with the
installer
toolkit and plug in the cell modem and wireless communications kit, the
installer toolkit will allow the Envoy software update to work, and you
can get it taken care of early in the day, while still hanging boxes,
running conduit, etc. <br>
<br>
I would agree that there are definitely parts of the new installer
toolkit that aren't intuitive. I missed the "edit" button on the devices
page for a bit (which is not mentioned in the tech brief), and couldn't
figure out how to increase the device count, for example. I also had to
try the Envoy update twice for some of these systems, as it threw an
error code the first time around, so for some of the systems it took
closer to 45-50 minutes to get the Envoy software update done. <br>
<br>
Hope the next one goes more smoothly for you! New products, new
challenges,
I guess.<br>
<br>
Best,<br>
<br>
Louis Woofenden<br>
<br>
<span><a class="moz-txt-link-abbreviated" href="mailto:don@energysolarnow.com">don@energysolarnow.com</a> wrote on 9/30/20 2:59 PM:</span><br>
<blockquote type="cite"
cite="mid:20200930145904.8b71096d7d88573c67c7101a41a0e3ba.5fc4b4b1ea.wbe@email14.godaddy.com">
<meta http-equiv="content-type" content="text/html; charset=utf-8">
<span style="font-family:Verdana; color:#000000; font-size:10pt;"><div>Wrenches-</div><div>I'm
having a lot of difficulty commissioning my first Enphase Ensemble
installation. This is on a pre-existing microinverter installation.
Have been on the phone with tech support several times; each time they
forward a Tech Brief about commissioning that has different and slightly
conflicting instructions. It seems the order of turning on each box is
critical. Because of already-obsolete software that they ship with, the
software must be updated before activating the Envoy, Enpower, and
Encharge or they will not work. </div><div>And for some reason the Envoy
must have both Wifi and cell connection before even starting
commissioning, but the slower cell connection is used for software
download so it takes up to 12 hours. </div><div>This commissioning must
be done on-site using their latest version of
Installer Toolkit on a smart phone. Sure, there are buttons in
Enlighten's Activation page to add an Enpower and Encharge, but these
do not work "yet". </div><div>Enphase tech support says they are working
on making this a single-day process rather than the current multi-day
commissioning. This does not even count the actual hardware installation
time. <br></div><div><br></div><div>I would advise anyone against
moving any loads to a new subpanel before the entire system is
commissioned and operating. <br></div><div>As of now I have an Enpower
that mistakenly thinks it is off-grid when the grid is present, so it
has told the Envoy to shut down the PV microinverters and batteries.
These are relay controlled, therefore it is not possible to have them
connected without software control. It has already committed the major
crime of shutting down the backed-up loads while the grid is still
present. Enphase is working on it, but seem to be developing software on
the fly. I suppose their integration process has been hit hard by
pandemic distancing, and they are all working remotely. <br></div><div><br></div><div>Has
anyone else had a successful experience commissioning an Ensemble? </div><div>I'd
like to hear about the doos-and-don'ts. </div><div><br></div><div>Don
Barch</div><div><a href="mailto:don@energysolarnow.com"
moz-do-not-send="true">don@energysolarnow.com</a><br></div></span>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-freetext" href="http://www.re-wrenches.org/etiquette.htm">http://www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-freetext" href="http://www.members.re-wrenches.org">http://www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
<div class="moz-signature">-- <br><span><meta charset="utf-8"><span
style="color: rgb(80, 0, 80); font-family: arial, sans-serif; font-size:
12.8000001907349px; font-style: normal; font-variant: normal;
font-weight: normal; letter-spacing: normal; line-height: normal;
orphans: auto; text-align: start; text-indent: 0px; text-transform:
none; white-space: normal; widows: 1; word-spacing: 0px;
-webkit-text-stroke-width: 0px; display: inline !important; float: none;
background-color: rgb(255, 255, 255);">--<span
class="Apple-converted-space"> </span></span><br style="color: rgb(80,
0, 80); font-family: arial, sans-serif; font-size: 12.8000001907349px;
font-style: normal; font-variant: normal; font-weight: normal;
letter-spacing: normal; line-height: normal; orphans: auto; text-align:
start; text-indent: 0px; text-transform: none; white-space: normal;
widows: 1; word-spacing: 0px; -webkit-text-stroke-width: 0px;
background-color: rgb(255, 255, 255);"><div style="color: rgb(80, 0,
80); font-family: arial, sans-serif; font-size: 12.8000001907349px;
font-style: normal; font-variant: normal; font-weight: normal;
letter-spacing: normal; line-height: normal; orphans: auto; text-align:
start; text-indent: 0px; text-transform: none; white-space: normal;
widows: 1; word-spacing: 0px; -webkit-text-stroke-width: 0px;
background-color: rgb(255, 255, 255);"><div dir="ltr">Louis Woofenden<br>Engineering
Director<br>Net Zero Solar, LLC<br>101. W. 5th St., Tucson, AZ 85705<br>Arizona
ROC #248710, 259756, 259521<span class="Apple-converted-space"> </span><br><br>Phone:<span
class="Apple-converted-space"> </span><a href="tel:520.207.4053"
value="+15202074053" target="_blank" style="color: rgb(17, 85, 204);">520.207.4053</a><span
class="Apple-converted-space"> </span>Ex. 3<br>
<div>Cell:<span class="Apple-converted-space"> </span><a
href="tel:520.237.5040" value="+15202375040" target="_blank"
style="color: rgb(17, 85, 204);">520.237.5040</a><br>Fax:<span
class="Apple-converted-space"> </span><a href="tel:520.203.7230"
value="+15202037230" target="_blank" style="color: rgb(17, 85, 204);">520.203.7230</a><br><br>NABCEP
Certified PV Installation Professional\u2122<br><br>
</div></div></div> </span></div>
</body></html>