    <p>I should also add to my post and others' comments, that SAE rated
      and welding cables are not NEC legal for building wiring.  That
      used to be a common bust by the AHJ, and as others have pointed
      out:  Cobra Xflex, Arctic, etc are all UL listed building cable. 
      Its got to have something listed on the NEC chart such as RHH,
      RHW, THHN, THWN etc.<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 8/12/20 1:25 PM, Ray wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:ded607e3-3ed3-a4d2-211d-32a24289366e@solarray.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <p>Also, welding and automotive cables use totally different
        rating systems like SAE, that are much more liberal than NEC. 
        For instance, golf carts are traditionally wired with #6 battery
        cables, and can see a continuous draw of 125 A and surges to
        200.  We would never do that by NEC, but the cables just get
        warm to the touch in golf carts.<br>
      </p>
      <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
      <div class="moz-cite-prefix">On 8/11/20 6:04 PM, Kent Osterberg
        wrote:<br>
      </div>
      <blockquote type="cite"
        cite="mid:ac33b8f4-ec73-84f7-ad51-d2a382307fe3@coveoregon.com">
        <meta http-equiv="Content-Type" content="text/html;
          charset=UTF-8">
        Peter,<br>
        <br>
        The 210-amp rating is probably for a 105°C insulation
        temperature in free air. For comparison, #2 THHN (90°C) copper
        in free air is rated for 190 amps. Not sure that it makes sense
        to use a free-air rating in a small closed box.  For outside use
        a temperature de-rating for ambient temperature, maybe around
        -10%, should be included too. <br>
        <br>
        It looks like Cotek recommends a minimum cable size of 1/0, so
        out of fear of starving the inverter of enough voltage, I
        wouldn't use any smaller.<br>
        <br>
        Kent Osterberg<br>
        Blue Mountain Solar<br>
        <br>
        <div class="moz-cite-prefix">On 8/11/2020 3:18 PM, <a
            class="moz-txt-link-abbreviated"
            href="mailto:petertor@pobox.com" moz-do-not-send="true">petertor@pobox.com</a>
          wrote:<br>
        </div>
        <blockquote type="cite"
          cite="mid:1493095530.2040140.1597184302348@mailbusiness.ionos.com">
          <meta http-equiv="content-type" content="text/html;
            charset=UTF-8">
          <meta charset="UTF-8">
          <div> I have been designing a off-grid system that can fit in
            an outside-accessible compartment with an approximate 24"
            square footprint and space above about 18" - 24". </div>
          <div> <br>
          </div>
          <div> I am using two Battle Born LiFePO4 batteries rated at 24
            V / 50 Ah, a Cotek pure sine wave inverter with an output
            power of 4,000 VA , a MorningStar TS-MPPT-60 charge
            controller, a Victron BMV-712 "coulomb counter" and a Battle
            Born surge limiter CL500. </div>
          <div> <br>
          </div>
          <div> The current limiter limits the current to 120
            continuous, and 200 A for 30 sec. </div>
          <div> <br>
          </div>
          <div> I have been able to fit everything in and I am designing
            the cabling, and here is my problem. </div>
          <div> <br>
          </div>
          <div> I have one vendor that recommends Ancor brand Tinned
            Marine Grade Battery Cable. It is "resistant to salt water,
            battery acid, oil, gasoline, heat, abrasion and ultra-violet
            radiation. Exceeds UL 1426, ABYC and US Coast Guard Charter
            boat (CFR Title 46) standards. Highest quality
            ultra-flexible (Type 3) tinned copper stranding. Vinyl
            insulation. -50 deg-C to 105 deg-C." 2 AWG is composed of
            665 ea 30 AWG stands. </div>
          <div> <br>
          </div>
          <div> The same vendor has "welding cable" with an EPDM
            insulation rated at 600 V, water/chemical/grease/abrasion
            resistant, -50 deg-C to 105 deg-C, "marine grade". Not UL
            listed. 624 ea 30 AWG strands. </div>
          <div> <br>
          </div>
          <div> Roughly comparable pricing. </div>
          <div> <br>
          </div>
          <div> They claim both 2 AWG cables are rated at 210 A. Not
            sure if this is continuous duty or whether I should derate
            this for what will be continuous duty. </div>
          <div> <br>
          </div>
          <div> This is new territory for me, and any help would be
            appreciated. </div>
          <div> <br>
          </div>
          <div> Peter T. Parrish, Ph.D. <br>
            President, California Solar Engineering </div>
          <div class="io-ox-signature">
            <p><br>
            </p>
          </div>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
        </blockquote>
        <br>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>