    Peter,<br>
    <br>
    The 210-amp rating is probably for a 105°C insulation temperature in
    free air. For comparison, #2 THHN (90°C) copper in free air is rated
    for 190 amps. Not sure that it makes sense to use a free-air rating
    in a small closed box.  For outside use a temperature de-rating for
    ambient temperature, maybe around -10%, should be included too. <br>
    <br>
    It looks like Cotek recommends a minimum cable size of 1/0, so out
    of fear of starving the inverter of enough voltage, I wouldn't use
    any smaller.<br>
    <br>
    Kent Osterberg<br>
    Blue Mountain Solar<br>
    <br>
    <div class="moz-cite-prefix">On 8/11/2020 3:18 PM,
      <a class="moz-txt-link-abbreviated" href="mailto:petertor@pobox.com">petertor@pobox.com</a> wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:1493095530.2040140.1597184302348@mailbusiness.ionos.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <meta charset="UTF-8">
      <div> I have been designing a off-grid system that can fit in an
        outside-accessible compartment with an approximate 24" square
        footprint and space above about 18" - 24". </div>
      <div> <br>
      </div>
      <div> I am using two Battle Born LiFePO4 batteries rated at 24 V /
        50 Ah, a Cotek pure sine wave inverter with an output power of
        4,000 VA , a MorningStar TS-MPPT-60 charge controller, a Victron
        BMV-712 "coulomb counter" and a Battle Born surge limiter CL500.
      </div>
      <div> <br>
      </div>
      <div> The current limiter limits the current to 120 continuous,
        and 200 A for 30 sec. </div>
      <div> <br>
      </div>
      <div> I have been able to fit everything in and I am designing the
        cabling, and here is my problem. </div>
      <div> <br>
      </div>
      <div> I have one vendor that recommends Ancor brand Tinned Marine
        Grade Battery Cable. It is "resistant to salt water, battery
        acid, oil, gasoline, heat, abrasion and ultra-violet radiation.
        Exceeds UL 1426, ABYC and US Coast Guard Charter boat (CFR Title
        46) standards. Highest quality ultra-flexible (Type 3) tinned
        copper stranding. Vinyl insulation. -50 deg-C to 105 deg-C." 2
        AWG is composed of 665 ea 30 AWG stands. </div>
      <div> <br>
      </div>
      <div> The same vendor has "welding cable" with an EPDM insulation
        rated at 600 V, water/chemical/grease/abrasion resistant, -50
        deg-C to 105 deg-C, "marine grade". Not UL listed. 624 ea 30 AWG
        strands. </div>
      <div> <br>
      </div>
      <div> Roughly comparable pricing. </div>
      <div> <br>
      </div>
      <div> They claim both 2 AWG cables are rated at 210 A. Not sure if
        this is continuous duty or whether I should derate this for what
        will be continuous duty. </div>
      <div> <br>
      </div>
      <div> This is new territory for me, and any help would be
        appreciated. </div>
      <div> <br>
      </div>
      <div> Peter T. Parrish, Ph.D. <br>
        President, California Solar Engineering </div>
      <div class="io-ox-signature">
        <p><br>
        </p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>