<div dir="ltr">Jeff,<div><br></div><div>I don't have answers to many of your questions but one thing I wanted to point out as that some lithium-ion manufacturers like Blue Planet underrate the capacity of their batteries so they can get to the 100% DOD without impacting cycle life. For example, Their 16 kWh battery is actually something like a 17.2 kWh battery. Whereas other manufacturers give you the actual capacity of the battery but suggest limiting the DOD to 80%. This makes it a bit hard to compare apples to apples. </div><div><br></div><div>Also from what I've seen the cycle life curve for 80% DOD or less with lithium-ion batteries is relatively flat. </div><div><br></div><div>Thanks,</div><div>Will</div><div><br></div><div> -- <br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><b style="font-size:12.8px">Will White</b><div style="font-size:12.8px">Curriculum Developer</div><div style="font-size:12.8px"><br></div><div style="font-size:12.8px"><img src="https://docs.google.com/uc?export=download&id=12H3Cu2gnX7TKTeETn1WsYqa8cp6gsEj1&revid=0B7yAwArWHgPbNzhGK00wT0diY1c1NWhlRlNocDRVd045eTFjPQ" width="420" height="52"><br></div><div style="font-size:12.8px"><span style="font-size:12.8px">e: </span><a href="mailto:will@solarenergy.org" style="font-size:12.8px" target="_blank">will@solarenergy.org</a><span style="font-size:12.8px"> </span><br></div><div><div style="font-size:12.8px"><span style="font-size:12.8px">w: <a href="http://www.solarenergy.org/" target="_blank">www.solarenergy.org</a> </span></div><div style="font-size:12.8px">p: 802-272-3092<br></div><div style="font-size:12.8px"><span style="font-size:12.8px"><br></span></div><div style="font-size:12.8px"><span style="font-size:12.8px"><div>NABCEP Certified PV Installation Professional</div><div># 093006-34</div></span></div><div><span style="color:rgb(102,102,102);font-family:Arial,sans-serif;font-size:x-small">Do you envision a world powered by renewable energy? </span><a href="http://solarenergy.org/donate" style="font-family:Arial,sans-serif;font-size:x-small" target="_blank">Be the change</a><span style="color:rgb(102,102,102);font-family:Arial,sans-serif;font-size:x-small">.</span></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Aug 11, 2020 at 2:30 PM Jeff Clearwater <<a href="mailto:jeffc@villagepowerdesign.com">jeffc@villagepowerdesign.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
<div bgcolor="#FFFFFF">Hey All,<br>
<br>
Great Thread - so does anyone have the missing cycle life information
for the Discover AES and Fortress Eflex below?<br>
<br>
<ul>
<li>Discover AES (42-48-6650) (Spec sheet does not list cycles) (but
does give 38MWh warranty</li>
</ul>
see analysis sheet here: <a href="https://aeesolar.com/wp-content/uploads/2019/02/DISCOVER-AES-The-AES-LiFePO-Battery-Solar-Off-grid-Advantage-20190124-AEE.pdf" target="_blank">https://aeesolar.com/wp-content/uploads/2019/02/DISCOVER-AES-The-AES-LiFePO-Battery-Solar-Off-grid-Advantage-20190124-AEE.pdf</a><br>
<br>
that sheet says "With a designed DOD of 50% lead-acid batteries are
expected to last ~1500 cycles or 4 Years of daily cycling.
With the Discover AES 10 Year 38 MWh Warranty, you\u2019ll be half way into
your 3rd Set of lead-acid batteries."<br>
<br>
That would imply 5250 cycles under warranty - but surely it has more in
it than that for an expensive LFP! Can't find a reference anywhere. 38
MWH/6.65 KWH = 5700 cycles - their own spreadsheet says "Cycle Life
(@DOD rating): NA" Impressive warranty but how much past the warranty
they don't seem to want to venture. It's the most expensive of the
options listed here (well comparable to BI) and comes with highest
quality recommendation and has great closed loop communications - but
would love to know the top end cycle figure.<br>
<br>
<ul>
<li>Fortress EVault (18KWH) (Spec sheet says 6000)</li>
<li>Fortress EFlex (5.4 KWH) ( Spec sheet does not list cycles)</li>
<li>Simpliphi 3.8 (spec sheet says 10,000+ @ 80%)</li>
<li>Blue Ion 2.0 spec sheet says 8000 @ 100% DOD</li>
</ul>
<p>Does anyone know why Simpliphi and BI an claim such high cycle life
whereas Fortress says 6000 and AES won't venture it? same chemistry?
so is Fortress underselling or the other folks over selling?<br>
</p>
Has anyone even seen a curve of cycle life vs. DOD for LFP? or is that
not so much a curve as a flat line?<br>
<br>
thanks!<br>
<br>
Jeff<br>
<br>
~~~~~~~~~~~<br>
<span>Jeff Clearwater<br></span><span><span>VillageLab<br>
</span>Village Power Design</span><span><span><span><br>
</span></span><a href="http://www.villagelab.net" target="_blank">www.villagelab.net</a></span><br>
<span><span><a href="http://www.villagepowerdesign.com" target="_blank">www.villagepowerdesign.com</a></span><br>
cell - <span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span><br>
<br>
<br>
<br>
<br>
<span>Richard Scott wrote on 8/11/20 10:35 AM:</span><br>
<blockquote type="cite">
<div dir="ltr">Also keep in mind that the battery charge/discharge
efficiency is much higher for lithium batteries compared to lead acid.<div><br></div><div>Richard</div><div><br></div></div>
<br>
<div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Aug
11, 2020 at 8:17 AM Jay <<a href="mailto:jay.peltz@gmail.com" target="_blank">jay.peltz@gmail.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex"><div dir="auto"><div dir="ltr">Hi
William,</div><div dir="ltr"><br></div><div dir="ltr">I dont do the
math based on up front kwh cost, but on lifetime kWh based on the number
of cycles per average DOD that are going to be used. I use this same
formula to compare all batteries to each other. </div><div dir="ltr"><br></div><div dir="ltr">Jay</div><div dir="ltr"><br></div><div dir="ltr">Peltz
power. </div><div dir="ltr"><br></div><div dir="ltr">For example, a
Rolls L16 ex has 3500 cycles at 50% DOD, and it\u2019s a 371 amp hr at 6v or
2.226 kWh </div><div dir="ltr">Retail is $400 </div><div dir="ltr"><br></div><div dir="ltr">3500 cycles x 1.1 kWh At 50 DOD=3850 kWh </div><div dir="ltr">$400
/ 3850 kWh = $.10 kWh </div><div dir="ltr">10 years of 50% cycling
daily </div><div dir="ltr"><br></div><div dir="ltr">Compared to say a
mid grade US battery, 1400 cycles to 50%, 400 amp hr. 2.4 kWh </div><div dir="ltr">$325/1680 kWh = $.19 kWh. </div><div dir="ltr">3.8 yrs life</div><div dir="ltr"><br></div><div dir="ltr">Compare to say BI</div><div dir="ltr">$1000 kWh roughly. </div><div dir="ltr">If you get 10,000
cycles, that works out to same cost. $.10 per kWh. </div><div dir="ltr">27
yrs, but will the chemistry actually last that long?</div><div dir="ltr">However, you have a massive upfront money cost. </div><div dir="ltr">And for those of us off grid, you can\u2019t really cycle 100%. And
many lithium in the fine print don\u2019t want you to charge to 100% daily.
Let\u2019s assume you start the generator at 10% and charge to 95%, now your
usable amount is actually 85%, not 100%. </div><div dir="ltr">Cost per
kWh goes to $.12. </div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><br></div><div dir="ltr"><blockquote type="cite">On Aug 11, 2020, at 6:04 AM, William Miller <<a href="mailto:william@millersolar.com" target="_blank">william@millersolar.com</a>> wrote:<br><br></blockquote></div><blockquote type="cite"><div dir="ltr">\ufeff<div><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">Friends:</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">I am hoping
y\u2019all can tell me I am doing something wrong with my arithmetic. I have
registered to purchase Blue Planet batteries and priced the product. I
come up with math that indicates that comparing usable amp/hours to
usable amp/hours, that the Blue Planet is 5 times the cost of a flooded
L-16 battery array on a cost per kilowatt/hour. Can this be true?</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">I am using
these parameters:</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p style="margin-left:0.75in"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"><span>1.<span style="font:7pt "Times New Roman""> </span></span></span><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">DOD for
flooded L16s: 50%</span></p><p style="margin-left:0.75in"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"><span>2.<span style="font:7pt "Times New Roman""> </span></span></span><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">DOD for
Blue Planet: 100%</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">I hope I am
wrong.</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">Also, we
often install battery arrays that are upwards of 4,000 AH. For example,
we installed 5,668 of East Penn flooded batteries on a couple of
projects. To acquire the same capacity in Blue Planet would require 9
cabinets (again 50% DOD versus 100% DOD). Is this correct design? Is
it practical to install 9 cabinets? Does the system detect and
compensate for circulating currents in this many parallel strings?</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">Thanks in
advance.</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)">William
Miller</span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><span style="font-family:Verdana,sans-serif;color:rgb(31,73,125)"> </span></p><p class="MsoNormal"><b><span style="font-size:10pt;font-family:Tahoma,sans-serif">From:</span></b><span style="font-size:10pt;font-family:Tahoma,sans-serif"> RE-wrenches
[mailto:<a href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank">re-wrenches-bounces@lists.re-wrenches.org</a>]
<b>On Behalf Of </b>Jerry Shafer<br><b>Sent:</b> Sunday, August 9, 2020
12:02 PM<br><b>To:</b> RE-wrenches<br><b>Subject:</b> Re: [RE-wrenches]
Best Battery</span></p><p class="MsoNormal"> </p><div><p class="MsoNormal">Wrenchel have been very happy with all my Blue Planet
battery systems, best battery you will install.</p><div><p class="MsoNormal">Jerry</p></div></div><p class="MsoNormal"> </p><div><div><p class="MsoNormal">On Sun, Aug 9, 2020, 11:19 AM <<a href="mailto:drake.chamberlin@redwoodalliance.org" target="_blank">drake.chamberlin@redwoodalliance.org</a>>
wrote:</p></div><blockquote style="border-top:none;border-right:none;border-bottom:none;border-left:1pt solid rgb(204,204,204);padding:0in 0in 0in 6pt;margin-left:4.8pt;margin-right:0in"><p class="MsoNormal" style="margin-bottom:12pt">Hello Wrenches,<br><br>What is the best
Li-Ion battery to use with an off grid system?<br><br>Thanks,<br><br>Drake<br>Athens
Electric<br><br>-- <br>_______________________________________________<br>List
sponsored by Redwood Alliance<br><br>List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br><br>Change
listserver email address & settings:<br><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br><br>List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br><br>List
rules & etiquette:<br><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a><br><br>Check
out or update participant bios:<br><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a></p></blockquote></div></div>
<span>_______________________________________________</span><br><span>List
sponsored by Redwood Alliance</span><br><span></span><br><span>List
Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a></span><br><span></span><br><span>Change
listserver email address & settings:</span><br><span><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List-Archive:
<a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a></span><br><span></span><br><span>List
rules & etiquette:</span><br><span><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a></span><br><span></span><br><span>Check
out or update participant bios:</span><br><span><a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a></span><br><span></span><br></div></blockquote></div>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br></blockquote></div>
<br>
<fieldset></fieldset>
<br>
<pre>_______________________________________________
List sponsored by Redwood Alliance
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
<div>-- <br><span>~~~~~~~~~~~<br>
</span>
<div>
<span>Jeff Clearwater</span><span><span><br>
</span>Village Power Design<br>
</span><span><span><span><a href="https://www.linkedin.com/in/jeff-clearwater-0622a312/" target="_blank">linkedin</a>
</span></span></span><br>
<span><span><a href="http://www.villagepowerdesign.com" target="_blank">www.villagepowerdesign.com</a></span><br>
cell - <span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span></div>
<span><span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)"></span></span></div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><b style="font-size:12.8px">Will White</b><div style="font-size:12.8px">Curriculum Developer</div><div style="font-size:12.8px"><br></div><div style="font-size:12.8px"><img src="https://docs.google.com/uc?export=download&id=12H3Cu2gnX7TKTeETn1WsYqa8cp6gsEj1&revid=0B7yAwArWHgPbNzhGK00wT0diY1c1NWhlRlNocDRVd045eTFjPQ" width="420" height="52"><br></div><div style="font-size:12.8px"><span style="font-size:12.8px">e: </span><a href="mailto:will@solarenergy.org" style="color:rgb(17,85,204);font-size:12.8px" target="_blank">will@solarenergy.org</a><span style="font-size:12.8px"> </span><br></div><div><div style="font-size:12.8px"><span style="font-size:12.8px">w: <a href="http://www.solarenergy.org/" style="color:rgb(17,85,204)" target="_blank">www.solarenergy.org</a> </span></div><div style="font-size:12.8px">p: 802-272-3092<br></div><div style="font-size:12.8px"><span style="font-size:12.8px"><br></span></div><div style="font-size:12.8px"><span style="font-size:12.8px"><div>NABCEP Certified PV Installation Professional</div><div># 093006-34</div></span></div><div><span style="color:rgb(102,102,102);font-family:Arial,sans-serif;font-size:x-small">Do you envision a world powered by renewable energy? </span><a href="http://solarenergy.org/donate" style="font-family:Arial,sans-serif;font-size:x-small;color:rgb(17,85,204)" target="_blank">Be the change</a><span style="color:rgb(102,102,102);font-family:Arial,sans-serif;font-size:x-small">.</span><br></div></div></div></div></div></div></div></div></div></div></div></div></div></div>