Thanks Ray,<div>I am going to use the 2kva DLO cable. It is dual rated as RHW-2, which is what inverter OEM recommends. AWC warehouse is also close by in PA. also.</div><div class="mb_sig"></div><blockquote class='history_container' type='cite' style='border-left-style:solid;border-width:1px; margin-top:20px; margin-left:0px;padding-left:10px;'>
<p style='color: #AAAAAA; margin-top: 10px;'>On 8/1/2020 8:16:16 PM, Ray <ray@solarray.com> wrote:</p><div style='font-family:Arial,Helvetica,sans-serif'>
<p>I would look at Diesel Locomotive Cable DLO, which is usually
dual rated RHH/RHW-2 for us non locomotive folks. 2000 v rated.
Its pretty easy to work with, flexible, but has a 2nd inner liner
that gives it the higher volt rating. Its also usually tinned
conductors too. <br>
</p>
<p><a href="https://www.awcwire.com/productspec.aspx?id=dlo">https://www.awcwire.com/productspec.aspx?id=dlo</a></p>
<pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
<div class="moz-cite-prefix">On 8/1/20 7:09 AM, Kirk Herander wrote:<br>
</div>
<blockquote type="cite" cite="mid:Mailbird-03b102ef-a1ab-4ac4-8691-60e160fbc8f2@icloud.com">
<div id="__MailbirdStyleContent" style="font-size: 12pt;font-family: Arial;color: #000000">I need to spec battery
cable for a nominal 850 vdc LFP bank. Several brands of power
cable list their rating at a dual 600/1000v. it is my
understanding that to be listed in this manner, the cable must
pass a test apply of over 600v for a short period without
breakdown. But under normal operation IMO, the voltage is not to
exceed 600v. And this test is done with AC voltage, not DC.
<div><span style="font-size: 12pt;color: rgb(51, 51,
51);font-family: oswald, sans-serif"><br>
</span></div>
<div><span style="font-size: 12pt;color: rgb(51, 51,
51);font-family: oswald, sans-serif">"<b>UL 1277: Power and
Control Tray Cable</b></span><br>
</div>
<div>
<p style="box-sizing: border-box; margin-bottom: 8px;
margin-top: 0px; padding-top: 0px; padding-bottom: 0px;
color: rgb(51, 51, 51); font-family: lato, sans-serif;
line-height: 22px; text-size-adjust: none;">UL 1277, the
standard for electrical power and control tray cable, was
recently updated, allowing manufacturers with UL approved
tray cable to market their product as 600V/1kV rated. To be
dual rated, products must use a recognized 1kV rated
conductor and pass a higher voltage AC Hipot test on the
completed cable. This test requires each insulated conductor
in finished cable to withstand a specified voltage range for
one minute without breakdown. If a product passes the AC
Hipot test, it is suitable for 1kV use."</p>
<div><br>
</div>
<div>Am I getting this right? And If so, one should not use
this 600/1000v wire if normal operating voltage is above
600v as is my case? Proper rating should be dual 1000/2000v
like PV wire?</div>
<div><br>
</div>
<div>What do you experienced high voltage battery gurus use in
my application? Thanks.</div>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
</div></blockquote>
</div></body>