<html><body style="word-wrap: break-word; -webkit-nbsp-mode: space; line-break: after-white-space;" class="">This, from a&nbsp;Nov&nbsp;03, 2017&nbsp;Powerwall 2 document, makes sense. Generator input in place of utility&nbsp;syncs with PV inverters&nbsp;and Powerwall inverter.<br class=""><div class=""><img apple-inline="yes" id="0815996F-C274-415A-B7D6-C377A66D295E" width="304" height="357" src="cid:69DD7A6D-70FE-4706-8455-E4CD89244600@jetpack" class=""><br class="">Thank you,<br class=""><br class="">Larry Crutcher<br class="">Starlight Solar Power Systems<br class=""><br class=""><br class=""><br class=""><br class=""><br class=""></div><br class="">On Jul 20, 2020, at 1:25 PM, August Goers &lt;<a href="mailto:august@luminalt.com" class="">august@luminalt.com</a>&gt; wrote:<br class=""><br class="">Tesla released new offgrid design and installation instructions April of this year. As a Powerwall dealer, we're under NDA not to share the&nbsp;document, but the Powerwall will now charge from the generator when it hits a certain SOC threshold if the PV is not running. I'm not&nbsp;sure about that caveat of not allowing the generator to run while the PV is running. It seems like there are plenty of times where there is&nbsp;low solar production and you want to fire up the generator to top off the batteries. They also have a low state of charge mode when SOC&nbsp;reaches 10%, that the Powerwall will turn on during the day for short periods of time just to test to see if the PV system will couple up to&nbsp;charge the battery. This AC-coupling method of reviving the battery may or not work depending on loads and PV sizing / production&nbsp;levels.<br class=""><br class="">One limitation to the NMC battery technology is that it doesn't work well particularly in the cold, so offrige Powerwall batteries should be&nbsp;installed in the heated envelope of the home.&nbsp;<br class=""><br class="">August<br class=""><br class=""><br class="">On Mon, Jul 20, 2020 at 10:09 AM Jason Szumlanski &lt;<a href="mailto:jason@floridasolardesigngroup.com" class="">jason@floridasolardesigngroup.com</a>&gt; wrote:<br class="">The Powerwall 2 is now supported by Tesla in an off-grid configuration from what I heard. It is AC coupled. It cannot interact with&nbsp;generators whatsoever. You can't charge the battery with a generator and you can't AC couple a generator to it. If you want a&nbsp;generator, you put a transfer switch on the load side of the gateway device. If the battery dies, the generator starts. The generator&nbsp;powers loads, but does not recharge the battery because it becomes isolated via the transfer switch. The big downside I see with that&nbsp;is there would be a loss of power to the loads until the generator fires up. I don't see a way around that.<br class=""><br class="">I'm not a Tesla certified installer, but I have seen some of these batteries out in the wild and that's just the way it is - it's an integrated&nbsp;unit. I'd call it an "AC Battery," kind of like an AC PV Module. To answer another point in this thread, if the battery reaches its LBCO it&nbsp;can only recharge with PV in an off-grid scenario. It reserves battery capacity to turn on occasionally to see if there is PV input. At&nbsp;least that's how I understand it to work. I don't know what would happen if the battery actually reached 0%. Seems risky. I'm not sure&nbsp;how you would "jump start" it. Publicly available details seem scant on this, but there are a few system owners talking about it if you&nbsp;dig deep on the Interwebs.<br class=""><br class="">It will be interesting to see what Enphase comes up with. There are generator inputs on their Ensemble system, but no software&nbsp;support for this yet. The concept is very similar to Tesla in that there is a gateway device, essentially a transfer switch with battery&nbsp;controls inside. The Gateway acts as the AC point of coupling for everything to tie in together.&nbsp;<br class=""><br class="">I'm not sure why you couldn't use a generator to charge the Powerwall battery the same way you would charge with the grid.&nbsp;However, you would need a way to disable PV AC coupling when the generator is running. I can see how Enphase would be able to&nbsp;do this pretty easily. But Tesla is clear in that they do not allow a generator to interact with the Powerwall in any way.<br class=""><br class="">Jason Szumlanski<br class=""><br class=""><br class=""><br class=""><br class=""><br class="">On Sun, Jul 19, 2020 at 11:43 AM Hilton Dier III &lt;hiltondier@gmail.com&gt; wrote:<br class="">Greetings, Wrenches,<br class=""><br class="">I have an off-grid&nbsp;client who has been reading the buzz about the Tesla Powerwall&nbsp;2.0. I have been reading the data sheets and manual for it and&nbsp;it appears to be AC coupled only. There was talk of a DC input&nbsp;version, but apparently that fell by the wayside. I try to be&nbsp;agnostic about&nbsp;technology, and I'd be willing to subcontract a&nbsp;Tesla-approved installer if, in fact, this was the best&nbsp;solution.<br class=""><br class="">Does anybody have&nbsp;experience using the Powerwall 2.0 in an off grid PV system? Is&nbsp;it AC coupled only? Can it take generator power without&nbsp;barfing?&nbsp;What is the lead time on these?<br class=""><br class="">Many Thanks,<br class=""><br class="">Hilton<br class=""><br class=""><div class="">--&nbsp;</div><div class="">Hilton Dier III</div><div class="">Missisquoi River Hydro</div><div class="">Renewable Energy Design</div><br class="Apple-interchange-newline">_______________________________________________<br class="">List sponsored by Redwood Alliance<br class=""><br class="">List Address:&nbsp;RE-wrenches@lists.re-wrenches.org<br class=""><br class="">Change listserver email address &amp; settings:<br class="">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br class=""><br class="">List-Archive:&nbsp;http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br class=""><br class="">List rules &amp; etiquette:<br class="">www.re-wrenches.org/etiquette.htm<br class=""><br class="">Check out or update participant bios:<br class="">www.members.re-wrenches.org<br class=""><br class=""><br class="">_______________________________________________<br class="">List sponsored by Redwood Alliance<br class=""><br class="">List Address:&nbsp;RE-wrenches@lists.re-wrenches.org<br class=""><br class="">Change listserver email address &amp; settings:<br class="">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br class=""><br class="">List-Archive:&nbsp;http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br class=""><br class="">List rules &amp; etiquette:<br class="">www.re-wrenches.org/etiquette.htm<br class=""><br class="">Check out or update participant bios:<br class="">www.members.re-wrenches.org<br class=""><br class="">_______________________________________________<br class="">List sponsored by Redwood Alliance<br class=""><br class="">List Address: RE-wrenches@lists.re-wrenches.org<br class=""><br class="">Change listserver email address &amp; settings:<br class="">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org<br class=""><br class="">List-Archive: http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org<br class=""><br class="">List rules &amp; etiquette:<br class="">www.re-wrenches.org/etiquette.htm<br class=""><br class="">Check out or update participant bios:<br class="">www.members.re-wrenches.org<br class=""><br class=""><br class=""></body></html>