<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p>Thanks Jay,</p>
    <p>I talked again with Magnum.<br>
    </p>
    <p>I have the latest Rev 6.1 MS-PAE 4448 so the exact implementation
      has changed from that described in AN002, 5/10. The current Rev.
      has changes designed to improve interaction with the GT inverters.
      I didn't really get to the bottom of that. But the critical aspect
      of this remains unchanged:<br>
    </p>
    <p>- the Magnum will have shifted the frequency &lt;down now&gt; by
      0.5 Hz &lt;sufficient to knock the GT inverters off-line&gt; when
      the DC voltage rises to Absorb + 4V.<br>
    </p>
    <p>This makes more sense than the 6V I had in my notes (which may
      have meant 6V above Float.)</p>
    <p>With all this in mind, I think I will plan on using this feature
      as a backup to an AC dump load controller set to maintain Float
      voltage.<br>
    </p>
    <p><br>
    </p>
    <div class="moz-cite-prefix">On 6/12/2020 7:12 AM, Jay wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:686E2BE0-0091-4EC7-A4BA-B5C3F89584E4@gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Hi Mark</div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr">I found this which might be of help. </div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr"><a
href="https://www.magnum-dimensions.com/sites/default/files/MagArchive/AN-0002-AC-Coupling-Rev-5-10.pdf"
          moz-do-not-send="true">https://www.magnum-dimensions.com/sites/default/files/MagArchive/AN-0002-AC-Coupling-Rev-5-10.pdf</a></div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr">Jay</div>
      <div dir="ltr">Peltz power. </div>
      <div dir="ltr"><br>
        <blockquote type="cite">On Jun 12, 2020, at 6:59 AM, Mark Frye
          <a class="moz-txt-link-rfc2396E" href="mailto:markf@berkeleysolar.com">&lt;markf@berkeleysolar.com&gt;</a> wrote:<br>
          <br>
        </blockquote>
      </div>
      <blockquote type="cite">
        <div dir="ltr">\ufeff<span>Looking for confirmation from Wrenches who
            know Magnum inverters:</span><br>
          <span></span><br>
          <span>- MS-PAE</span><br>
          <span></span><br>
          <span>-ME-RC</span><br>
          <span></span><br>
          <span>- Frequency shift enabled (battery type "Custom")</span><br>
          <span></span><br>
          <span>- AC coupled PV inverters w/o frequency shift capability</span><br>
          <span></span><br>
          <span>Function:</span><br>
          <span></span><br>
          <span>At Absorb voltage frequency shift is zero, at Absorb
            voltage + 6 V, shift is 0.5 Hz &lt;grid ties pushed
            off-line&gt; (in 0.3 volt increments)</span><br>
          <span></span><br>
          <span>This is from my notes from a tech support call, but I am
            wondering if I have it mixed up. Protecting at 6 volts above
            the Absorb seems a bit high.</span><br>
          <span></span><br>
          <span>Thanks,</span><br>
          <span></span><br>
          <span>Mark</span><br>
          <span></span><br>
          <span></span><br>
          <span>_______________________________________________</span><br>
          <span>List sponsored by Redwood Alliance</span><br>
          <span></span><br>
          <span>List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Change listserver email address &amp; settings:</span><br>
          <span><a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive:
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br>
          <span></span><br>
          <span>List rules &amp; etiquette:</span><br>
          <span><a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out or update participant bios:</span><br>
          <span><a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>