<html>
  <head>

    <meta http-equiv="content-type" content="text/html; charset=UTF-8">
  </head>
  <body>
    <p><font face="Times New Roman, Times, serif">The issue with EV
        chargers is that they create a lot of reactive power. Think of
        it as "slosh" in the waveform. That means that charging at 2,000
        watts sloshes a lot more than 2kW through the cable, plug,
        outlet, and from the inverter. If you've got a reasonably good
        sinewave inverter the charger will like it fine. However, the
        inverter might not like the charger if you cut things too close.
        Make sure to have a lot of top end left in your inverter. Always
        use a transformer based inverter. The SW series has a big chunk
        of metal in it, so that's good. At 120V the Bolt will only draw
        1440 watts max.<br>
      </font></p>
    <p><font face="Times New Roman, Times, serif">An aftermarket Bolt
        240V charger can draw up to 32 amps. That's 7.7 kW, so too big
        for an SW. Treat it more like 40 amps. The OEM 120/240 EVSE
        (smart charging cord) that comes with the car can draw 8 or 12
        amps at 120V or 12 at 240V. Assume that the 8 amps is really 12
        and the 12 is really 15 or a bit more. I have seen 15 amp plugs
        and outlets with the hot prong melting plastic around it. The
        plug on the OEM EVSE is 20A rated but make sure your outlet is
        as well.</font><br>
    </p>
    <pre class="moz-signature" cols="72">-- 
Hilton Dier III
Missisquoi River Hydro
Renewable Energy Design
</pre>
  </body>
</html>