    <p>Is it at all weather related?  Rain, or high humidity?  High
      temperatures?  Do you have any indication what time of day it
      trips off at?<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 6/1/20 10:23 AM, Jason Szumlanski
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAE438R-1BD+7r_teuL0He6+khKWK1ewkPAtrxpcMdGK0LQWBmA@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="auto">Well, that didn't resolve it. The main breaker and
        a branch circuit breaker tripped again a few days ago. It was
        the same branch this time. 
        <div dir="auto"><br>
        </div>
        <div dir="auto">As my next diagnostic step I swapped two
          circuits (on which breaker they are landed). If history is a
          guide, it will work for about two weeks and then trip again.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">I'm dumbfounded. I really don't want to have to
          tear this whole system apart. At this point, if I have to
          remove all the modules, I feel that I need to replace all of
          the trunk cable which is an expensive proposition. I really
          don't know what else to do at this point.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Jason</div>
        <div dir="auto"><br>
        </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Mon, May 25, 2020, 10:43 AM
          Jason Szumlanski &lt;<a
            href="mailto:jason@floridasolardesigngroup.com"
            moz-do-not-send="true">jason@floridasolardesigngroup.com</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0 0 0
          .8ex;border-left:1px #ccc solid;padding-left:1ex">
          <div dir="ltr">
            <div dir="ltr">
              <div class="gmail_default"
                style="font-family:arial,helvetica,sans-serif">I
                strongly suspect the CH240 combined breaker was
                compromised (we will see). Since it happened that two
                different strings tripped, I doubt I have two
                microinverters with internal faults. It has to be the
                combined breaker. I was just surprised that branch
                circuit breakers were tripping simultaneously with the
                combined output breaker.</div>
              <div class="gmail_default"
                style="font-family:arial,helvetica,sans-serif"><br>
              </div>
              <div class="gmail_default"
                style="font-family:arial,helvetica,sans-serif">Of all
                the supply side connected systems I have installed, I
                have never seen a combined output fusible disconnect
                fuse blow, but I have seen many combined output breakers
                tripped. I was worried early on that I would be
                replacing fuses constantly, but that has not been an
                issue whatsoever.</div>
              <div class="gmail_default"
                style="font-family:arial,helvetica,sans-serif"><br>
              </div>
              <div class="gmail_default"
                style="font-family:arial,helvetica,sans-serif"><br>
              </div>
              <div>
                <div dir="ltr" data-smartmail="gmail_signature">
                  <div dir="ltr">
                    <div dir="ltr">
                      <div dir="ltr">
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <table style="font-family:&quot;helvetica
                                neue&quot;,helvetica,arial,sans-serif"
                                cellspacing="0" cellpadding="0"
                                border="0">
                                <tbody>
                                  <tr>
                                    <td rowspan="2"><br>
                                    </td>
                                    <td rowspan="2"><br>
                                    </td>
                                  </tr>
                                </tbody>
                              </table>
                              <b>
                                <div style="text-align:center"><br>
                                </div>
                              </b></div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
              <br>
            </div>
            <br>
            <div class="gmail_quote">
              <div dir="ltr" class="gmail_attr">On Thu, May 21, 2020 at
                11:15 AM &lt;<a href="mailto:scot.arey@solarcentex.com"
                  target="_blank" rel="noreferrer"
                  moz-do-not-send="true">scot.arey@solarcentex.com</a>&gt;
                wrote:<br>
              </div>
              <blockquote class="gmail_quote" style="margin:0px 0px 0px
                0.8ex;border-left:1px solid
                rgb(204,204,204);padding-left:1ex">
                <div lang="EN-US">
                  <div>
                    <p class="MsoNormal">Actually, we had a IQ7 string
                      loaded up to its max panel size and max string
                      length and in the spring on cool, clear day, it
                      tripped the string\u2019s associated breaker in the
                      Enphase combiner.</p>
                    <p class="MsoNormal"> </p>
                    <p class="MsoNormal">We reset but of course that
                      breaker was impaired and it tripped again. We
                      replaced and never had an issue going forward. We
                      suspect the breaker was less than perfect from the
                      start as we\u2019ve add equally nice days since.</p>
                    <p class="MsoNormal"> </p>
                    <p class="MsoNormal">This almost reminds me of
                      loading up Outback FM80. It says 4,000 watts but
                      in reality, 3,600 is the max when amps spike. I
                      will be extra careful going forward on IQ7 string
                      length when going to the max published\u2026</p>
                    <p class="MsoNormal"> </p>
                    <p class="MsoNormal">My story.</p>
                    <p class="MsoNormal"> </p>
                    <p class="MsoNormal">Scot</p>
                    <p class="MsoNormal"> </p>
                    <div
style="border-right:none;border-bottom:none;border-left:none;border-top:1pt
                      solid rgb(225,225,225);padding:3pt 0in 0in">
                      <p class="MsoNormal"><b>From:</b> RE-wrenches &lt;<a
href="mailto:re-wrenches-bounces@lists.re-wrenches.org" target="_blank"
                          rel="noreferrer" moz-do-not-send="true">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;
                        <b>On Behalf Of </b>Jason Szumlanski<br>
                        <b>Sent:</b> Thursday, May 21, 2020 8:57 AM<br>
                        <b>To:</b> RE-wrenches &lt;<a
                          href="mailto:re-wrenches@lists.re-wrenches.org"
                          target="_blank" rel="noreferrer"
                          moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                        <b>Subject:</b> [RE-wrenches] Enphase
                        intermittent breaker trippjng</p>
                    </div>
                    <p class="MsoNormal"> </p>
                    <div>
                      <p class="MsoNormal">I'm trying to resolve an
                        intermittent frustrating problem with and
                        Enphase IQ system. There are three AC Branch
                        circuits of 9 microinverters each coming into an
                        Enphase AC combiner. </p>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">What has been happening is
                          one of the BR220 branch circuit breakers and
                          the combine CH240 breaker in the main backfed
                          load center have been tripping simultaneously.
                          It has happened about four times in the last 6
                          months. It was always the same branch circuit
                          breaker, so we kept investigating that string,
                          checking the junction box, trunk cable, and
                          cap, etc. Finally we swapped out the BR220
                          breaker. </p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">Fast forward 4 weeks, and
                          we got another call. This time a different
                          branch circuit breaker and the main breaker
                          tripped simultaneously. We checked that branch
                          circuit and could not find any fault. It seems
                          unlikely that two branch circuit breakers
                          would be faulty, so we have now switched out
                          the CH240 main breaker in hopes that it is the
                          culprit.  </p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">I'm not totally confident
                          in this resolution and I have my fingers
                          crossed. If that doesn't work, does anyone
                          have any suggestions on another diagnostic
                          step? These intermittent problems are a major
                          hassle. One thought I had was to switch to a
                          supply side interconnection with a fusible
                          disconnect. Maybe the intermittent fault would
                          blow one of the two line fuses so at least I
                          could narrow it down to which line the fault
                          is on if there is in fact a fault.</p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">I have experienced two
                          other tripping breaker issues with Enphase
                          systems in the past. Neither of them were
                          systems I installed. One turned out to be
                          branch circuits that were not properly paired
                          up and landed on different breakers. Another
                          time we had an inverter with an internal fault
                          which eventually"blew up" with a loud popping
                          noise and smoke billowing out of it. That
                          happened after resetting a trip breaker
                          multiple times. This case seems to be
                          unrelated to those issues. I'm perplexed. </p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal">Jason Szumlanski</p>
                      </div>
                      <div>
                        <p class="MsoNormal">Florida Solar Design Group</p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                      <div>
                        <p class="MsoNormal"> </p>
                      </div>
                    </div>
                  </div>
                </div>
                _______________________________________________<br>
                List sponsored by Redwood Alliance<br>
                <br>
                List Address: <a
                  href="mailto:RE-wrenches@lists.re-wrenches.org"
                  target="_blank" rel="noreferrer"
                  moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                <br>
                Change listserver email address &amp; settings:<br>
                <a
href="https://mailtrack.io/trace/link/796b1796eb4c075a74298513a530f62e4a496cb2?notrack=1&amp;url=http%3A%2F%2Flists.re-wrenches.org%2Foptions.cgi%2Fre-wrenches-re-wrenches.org&amp;userId=1613865&amp;signature=c7dea131fd9cb45a"
                  rel="noreferrer noreferrer" target="_blank"
                  moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                <br>
                List-Archive: <a
href="https://mailtrack.io/trace/link/c06e48af2da3d129a58c08ef2043bd2d8fcbef6f?notrack=1&amp;url=http%3A%2F%2Fwww.mail-archive.com%2Fre-wrenches%40lists.re-wrenches.org%2Fmaillist.html&amp;userId=1613865&amp;signature=06899a19621f54d8"
                  rel="noreferrer noreferrer" target="_blank"
                  moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                <br>
                List rules &amp; etiquette:<br>
                <a
href="https://mailtrack.io/trace/link/215cb4d0fcfb04e4124aae9b2616249f1eef5542?notrack=1&amp;url=http%3A%2F%2Fwww.re-wrenches.org%2Fetiquette.htm&amp;userId=1613865&amp;signature=8bc84049c81c183c"
                  rel="noreferrer noreferrer" target="_blank"
                  moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                <br>
                Check out or update participant bios:<br>
                <a
href="https://mailtrack.io/trace/link/27c3e706e7f2b4836b1669b31c9454db7fee1b52?notrack=1&amp;url=http%3A%2F%2Fwww.members.re-wrenches.org&amp;userId=1613865&amp;signature=4a75a2d55681f39a"
                  rel="noreferrer noreferrer" target="_blank"
                  moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                <br>
              </blockquote>
            </div>
            <img alt="" style="display:flex" moz-do-not-send="true"
              width="0" height="0"></div>
        </blockquote>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>