<div dir="ltr"><div dir="ltr"><div>I would tend to agree with Ray&#39;s analysis, with one question:</div><div><ul><li>Does the Eq timer reset to 0 when the voltage dips?  It should basically hold the time the batteries were at Eq voltage when it drops below, sort of putting the EQ timer on hold until the voltage comes back up.  So eventually given enough sun and long enough day, or long enough generator run time, the mate should still report that equalization was reached.</li><li>If it doesn&#39;t reach equalization do that even though the battery voltage is being attained for enough time, then it might suggest a Mate issue...<br></li></ul><div>Howie<br></div></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Tue, Apr 28, 2020 at 2:12 PM Ray &lt;<a href="mailto:ray@solarray.com" target="_blank">ray@solarray.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div>
    <p>I would add to the chorus that it probably is a battery issue. 
      Here are the symptoms that lead to that conclusion:</p>
    <p> A) it started occurring recently, <br>
      B) it is somewhat intermittent, <br>
      C) the system has aging L 16s  (failures at 4 to 5 years are
      pretty  common)<br>
      D) they are the Trojan RE series  (dead cells at less than 2 years
      has been documented several times on this list)<br>
      E) the customer is trying to equalize regularly. (which causes
      over heating, and accelerates cell failures)<br>
    </p>
    <p>Besides checking battery voltages, an infared camera can quickly
      show over heating, bad cells.  Also, I would advise the customer
      to only equalize when the batteries are unequal, based on specific
      gravity readings.<br>
    </p>
    <pre cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div>On 4/28/20 12:20 PM, Dave Tedeyan
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      <div dir="ltr">Steve and Jerry, 
        <div>Thanks for the suggestions. I&#39;ll have to take a closer look
          at the battery bank next time I am out there. </div>
        <div>The solar setup is 4 strings of 3 kyocera 270&#39;s into each
          charge controller. So that is almost 65A @50V coming out of
          each charge controller for bulk. The parallel battery strings
          all have the same length of premade cable, so current
          should be balanced (unless there is a dead cell or two in
          there...).</div>
        <div>Cheers, </div>
        <div>Dave<br clear="all">
          <div>
            <div dir="ltr">
              <div dir="ltr">
                <div>
                  <div dir="ltr">
                    <div>
                      <div dir="ltr">
                        <div dir="ltr">
                          <div dir="ltr">
                            <div dir="ltr">
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div><br>
                                        </div>
                                        <div><b><font face="tahoma,
                                              sans-serif">Dave Tedeyan,
                                              PE</font></b></div>
                                        <div><font face="tahoma,
                                            sans-serif">Senior Engineer
                                            | Taitem Engineering, PC</font></div>
                                        <div><font face="tahoma,
                                            sans-serif"><img><br>
                                          </font></div>
                                        <div><font face="tahoma,
                                            sans-serif">110 South Albany
                                            Street</font><span style="font-family:tahoma,sans-serif"> |
                                            Ithaca, NY 14850</span></div>
                                        <div><font face="tahoma,
                                            sans-serif">o. <u>607.277.1118
                                              x121</u>  f. 607.277.2119</font></div>
                                        <div><font face="tahoma,
                                            sans-serif"><a href="http://www.taitem.com" target="_blank">www.taitem.com</a></font></div>
                                        <div><br>
                                        </div>
                                        <div><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Solar </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">\u2022</span><span style="font-family:tahoma,sans-serif;font-size:12.5pt;line-height:17.8333px"> </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Sustainability </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">\u2022 </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Energy </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">\u2022 </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Design</span><br>
                                        </div>
                                        <div><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px"><span style="font-family:Tahoma,sans-serif;font-size:13.3333px">Certified
                                              B-Corporation since 2013</span><span style="font-size:13.3333px"><br>
                                            </span></span></div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
          <br>
        </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Tue, Apr 28, 2020 at 11:52
          AM Jerry Shafer &lt;<a href="mailto:jerrysgarage01@gmail.com" target="_blank">jerrysgarage01@gmail.com</a>&gt;
          wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="auto">Sounds like a battery issue at first glance,
            as you EQ a battery it gets warm or even hot and this will
            effect ability to charge. If e en one of the L-16 is not
            exactly the same voltage you will not get to EQ untill
            another battery over voltages to show your overall volts.
            Need to look at each battery volts under this charge
            condition. Also if you have a battery acting up be very
            careful working around them.
            <div dir="auto">Jerry</div>
          </div>
          <br>
          <div class="gmail_quote">
            <div dir="ltr" class="gmail_attr">On Tue, Apr 28, 2020, 6:50
              AM Dave Tedeyan &lt;<a href="mailto:dtedeyan@taitem.com" target="_blank">dtedeyan@taitem.com</a>&gt;
              wrote:<br>
            </div>
            <blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
              <div dir="ltr">Hi All, 
                <div><br>
                </div>
                <div>I&#39;ve got an outback system (Radian 8048A, 2 FM80,
                  16 Trojan L16RE-B) where when the customer equalizes,
                  the batteries hover right around the EQ voltage, but
                  will often dip to 0.1v less. Because of this, the EQ
                  timer does not count down properly, and so left to its
                  own devices the system would equalize for way longer
                  than it should, potentially forever. This will happen
                  when doing an EQ from the solar on a bright sunny day,
                  or the generator, or both. The customer can manually
                  keep track of the time and manually stop the EQ after
                  3 hours, but that is not ideal. Has anyone dealt with
                  this before and have any suggestions on how they fixed
                  it? </div>
                <div><br>
                </div>
                <div>This system is 3-4 years old, and the issue only
                  started in the past year or so.</div>
                <div><br>
                </div>
                <div>Cheers, </div>
                <div>Dave</div>
                <div>
                  <div>
                    <div dir="ltr">
                      <div dir="ltr">
                        <div>
                          <div dir="ltr">
                            <div>
                              <div dir="ltr">
                                <div dir="ltr">
                                  <div dir="ltr">
                                    <div dir="ltr">
                                      <div dir="ltr">
                                        <div dir="ltr">
                                          <div dir="ltr">
                                            <div dir="ltr">
                                              <div dir="ltr">
                                                <div><br>
                                                </div>
                                                <div><b><font face="tahoma,
                                                      sans-serif">Dave
                                                      Tedeyan, PE</font></b></div>
                                                <div><font face="tahoma,
                                                    sans-serif">Senior
                                                    Engineer | Taitem
                                                    Engineering, PC</font></div>
                                                <div><font face="tahoma,
                                                    sans-serif"><img><br>
                                                  </font></div>
                                                <div><font face="tahoma,
                                                    sans-serif">110
                                                    South Albany Street</font><span style="font-family:tahoma,sans-serif"> | Ithaca, NY 14850</span></div>
                                                <div><font face="tahoma,
                                                    sans-serif">o. <u>607.277.1118
                                                      x121</u>  f.
                                                    607.277.2119</font></div>
                                                <div><font face="tahoma,
                                                    sans-serif"><a href="http://www.taitem.com" rel="noreferrer" target="_blank">www.taitem.com</a></font></div>
                                                <div><br>
                                                </div>
                                                <div><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Solar </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">\u2022</span><span style="font-family:tahoma,sans-serif;font-size:12.5pt;line-height:17.8333px"> </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Sustainability </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">\u2022 </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Energy </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">\u2022 </span><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px">Design</span><br>
                                                </div>
                                                <div><span style="font-family:tahoma,sans-serif;font-size:10pt;line-height:14.2667px"><span style="font-family:Tahoma,sans-serif;font-size:13.3333px">Certified
                                                      B-Corporation
                                                      since 2013</span><span style="font-size:13.3333px"><br>
                                                    </span></span></div>
                                              </div>
                                            </div>
                                          </div>
                                        </div>
                                      </div>
                                    </div>
                                  </div>
                                </div>
                              </div>
                            </div>
                          </div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
              _______________________________________________<br>
              List sponsored by Redwood Alliance<br>
              <br>
              List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Change listserver email address &amp; settings:<br>
              <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
              <br>
              List rules &amp; etiquette:<br>
              <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out or update participant bios:<br>
              <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
              <br>
            </blockquote>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset></fieldset>
      <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>
</div>