<html><head><meta http-equiv="Content-Type" content="text/html; charset=UTF-8" /></head><body style='font-size: 10pt; font-family: Verdana,Geneva,sans-serif'>
<p>We had a similar situation, and are now feeding a battery bank with a pair of 48 V Iota chargers. Iota can run on very low voltages. We have one Iota on each leg of the the 120/240 split phase to balance the load. It works. </p>
<div id="signature">---<br />
<div class="pre" style="margin: 0; padding: 0; font-family: monospace"> </div>
</div>
<p><br /></p>
<p id="reply-intro">On 2020-04-18 21:25, Ray wrote:</p>
<blockquote type="cite" style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0">
<div id="replybody1">
<div>
<p>When doing the volt drop calculation, be sure to correct for temperature, per the note after table 8, chapter 9 of the NEC. The table values default at 167 deg F (75 C). An underground cable will be operating closer to earth temperature. When I run volt drop for a 4/0 copper cable at 60 deg F, I'm seeing that you could go over 60 amps and maintain a volt drop of 3%. </p>
<p>Not sure what the requirements for the building are, but that exceeds most of my off grid systems. 60+ amps at a final voltage of 232 v is almost 14kW. Is there air conditioning? What are the calculated loads for this building? Is the inspector actually calling this a problem? </p>
<p>I would do a proof of concept: turn every light on in the place, along with some typical appliances (hair dryer, microwave) hit a circular saw to really make the point, with a DMM plugged in. I found long ago that actual measured volt drop was not as bad as Chapter 9 first predicts.</p>
<p><br /></p>
<pre class="v1moz-signature">Ray Walters
Remote Solar
303 505-8760</pre>
<div class="v1moz-cite-prefix">On 4/18/20 3:41 PM, Darryl Thayer wrote:</div>
<blockquote type="cite" style="padding: 0 0.4em; border-left: #1010ff 2px solid; margin: 0">
<div dir="ltr">
<div class="v1gmail_default" style="font-family: times new roman,serif; font-size: large;">Hi Mac, There are a few questions like is it Al or Cu wire, What makes it unusable? </div>
<div class="v1gmail_default" style="font-family: times new roman,serif; font-size: large;">for Voltage drop, I use Vd=2KIL/CMA for your case the unknown is the current. The installation of an inverter with grid support. Many inverters have this, you want a multimode inverter such as a Schneider, Outback, SolArk and I could name at least 4 more. A normal house will run on 30 amps. So assume 30 amps, Vd=2x21.6x30x1100/211600 =6.7 volts</div>
<div class="v1gmail_default" style="font-family: times new roman,serif; font-size: large;">So if the main house is at 240 Volts the remote house is at 233 Volts. The multimode inverter could be set at grid support beyond 30 Amps. For higher house loads the inverter can support up to 30 to 50 amps additional. (SolArk is 50 amp) I would add a balancing transformer at the end of the line to make the 120 loads balance. (an Autotransformer) such that 120 volts loads are balanced and the load is shared between 240-Volt conductors. Based on my customers' experiences I would use AGM LA batteries, as I expect low usage of the battery and quick recharge, but that is the customer's choice. I had one customer that had 10 years on the float-AGM battery set. </div>
</div>
<br />
<div class="v1gmail_quote">
<div class="v1gmail_attr" dir="ltr">On Fri, Apr 17, 2020 at 8:15 AM Mac Lewis <<a href="mailto:maclewis1@gmail.com" rel="noreferrer">maclewis1@gmail.com</a>> wrote:</div>
<blockquote class="v1gmail_quote" style="margin: 0px 0px 0px 0.8ex; border-left: 1px solid #cccccc; padding-left: 1ex;">
<div dir="ltr">Hi wrenches,
<div> </div>
<div>I've got a architect client with a sub-optimal power situation on one of the projects he is working on. I'm running through a couple of scenarios that may work. Its a ADU (accessory dwelling unit) that is about 1100' from power. The farmer had taken it upon himself to bury some 4/0 a few years ago to run power out there. Voltage drop is the big issue and its not going to pass the AHJ inspection. We could just ditch the grid and go off-grid, but it seems like a shame to not tap into the grid resource. Instead of dealing with the voltage drop, I was thinking it may make sense to rectify that low AC voltage input and parallel a smallish battery bank (size is yet to be determined), then use an off-grid inverter to serve the loads at good voltage.</div>
<div> </div>
<div>I am looking for feedback on this concept. What do you think?</div>
<div> </div>
<div>Also, are there any recommendations for good quality rectifiers with wide input voltage window? </div>
<div> </div>
<div>Thanks in advance for your help</div>
<div>
<div> </div>
-- <br />
<div dir="ltr">
<div> </div>
<div><span style="color: #305a78; font-family: 'times new roman', serif;"> </span></div>
<div> </div>
Mac Lewis<br /><br />
<p align="left"><span style="color: #000000; font-family: Verdana, Arial, Helvetica, sans-serif;"><span style="font-size: small;"><span style="font-family: arial; font-weight: normal; color: #305a78;"><span style="font-family: 'times new roman', serif;">"Yo solo sé que no sé nada." </span><span style="font-weight: bold; color: #686868;"><span style="font-family: 'times new roman', serif;">-Sócrates</span></span></span></span></span></p>
</div>
</div>
</div>
_______________________________________________<br />List sponsored by Redwood Alliance<br /><br />List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br /><br />Change listserver email address & settings:<br /><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br /><br />List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noopener noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br /><br />List rules & etiquette:<br /><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noopener noreferrer">www.re-wrenches.org/etiquette.htm</a><br /><br />Check out or update participant bios:<br /><a href="http://www.members.re-wrenches.org" target="_blank" rel="noopener noreferrer">www.members.re-wrenches.org</a><br /><br /></blockquote>
</div>
<br /><fieldset class="v1mimeAttachmentHeader"></fieldset>
<pre class="v1moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="v1moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="v1moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="v1moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noopener noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="v1moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noopener noreferrer">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="v1moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank" rel="noopener noreferrer">www.members.re-wrenches.org</a>
</pre>
</blockquote>
</div>
</div>
<br />
<div class="pre" style="margin: 0; padding: 0; font-family: monospace">_______________________________________________<br />List sponsored by Redwood Alliance<br /><br />List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br /><br />Change listserver email address & settings:<br /><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noopener noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br /><br />List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noopener noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br /><br />List rules & etiquette:<br /><a href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noopener noreferrer">www.re-wrenches.org/etiquette.htm</a><br /><br />Check out or update participant bios:<br /><a href="http://www.members.re-wrenches.org" target="_blank" rel="noopener noreferrer">www.members.re-wrenches.org</a><br /><br /></div>
</blockquote>
</body></html>