    <p>When doing the volt drop calculation, be sure to correct for
      temperature, per the note after table 8, chapter 9 of the NEC. 
      The table values default at 167 deg F (75 C).  An underground
      cable will be operating closer to earth temperature.   When I run
      volt drop for a 4/0 copper cable at 60 deg F, I'm seeing that you
      could go over 60 amps and maintain a volt drop of 3%.  <br>
    </p>
    <p>Not sure what the requirements for the building are, but that
      exceeds most of my off grid systems.  60+ amps at a final voltage
      of 232 v is almost 14kW. Is there air conditioning?  What are the
      calculated loads for this building?  Is the inspector actually
      calling this a problem?  <br>
    </p>
    <p>I would do a proof of concept: turn every light on in the place,
      along with some typical appliances (hair dryer, microwave) hit a
      circular saw to really make the point, with a DMM plugged in.  I
      found long ago that actual measured volt drop was not as bad as
      Chapter 9 first predicts.<br>
    </p>
    <p><br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 4/18/20 3:41 PM, Darryl Thayer
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAHsrUiT6=c5nOV9cb2TQapCXOOyQ4jc3S6raqRLDCPS-iO660Q@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div class="gmail_default" style="font-family:times new
          roman,serif;font-size:large">Hi Mac, There are a few questions
          like is it Al or Cu wire, What makes it unusable?  </div>
        <div class="gmail_default" style="font-family:times new
          roman,serif;font-size:large">for Voltage drop, I use
          Vd=2KIL/CMA for your case the unknown is the current.  The
          installation of an inverter with grid support.  Many inverters
          have this,  you want a multimode inverter such as a Schneider,
          Outback, SolArk and I could name at least 4 more.  A normal
          house will run on 30 amps.  So assume 30 amps,
          Vd=2x21.6x30x1100/211600 =6.7 volts</div>
        <div class="gmail_default" style="font-family:times new
          roman,serif;font-size:large">So if the main house is at 240
          Volts the remote house is at 233 Volts.  The multimode
          inverter could be set at grid support beyond 30 Amps.  For
          higher house loads the inverter can support up to 30 to 50
          amps additional.  (SolArk is 50 amp) I would add a balancing
          transformer at the end of the line to make the 120 loads
          balance.  (an Autotransformer) such that  120 volts loads are
          balanced and the load is shared between 240-Volt conductors. 
          Based on my customers' experiences I would use AGM LA
          batteries, as I expect low usage of the battery and quick
          recharge, but that is the customer's choice.  I had one
          customer that had 10 years on the float-AGM battery set.     </div>
      </div>
      <br>
      <div class="gmail_quote">
        <div dir="ltr" class="gmail_attr">On Fri, Apr 17, 2020 at 8:15
          AM Mac Lewis &lt;<a href="mailto:maclewis1@gmail.com"
            moz-do-not-send="true">maclewis1@gmail.com</a>&gt; wrote:<br>
        </div>
        <blockquote class="gmail_quote" style="margin:0px 0px 0px
          0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
          <div dir="ltr">Hi wrenches,
            <div><br>
            </div>
            <div>I've got a architect client with a sub-optimal power
              situation on one of the projects he is working on.  I'm
              running through a couple of scenarios that may work.  Its
              a ADU (accessory dwelling unit) that is about 1100' from
              power.  The farmer had taken it upon himself to bury some
              4/0 a few years ago to run power out there.  Voltage drop
              is the big issue and its not going to pass the AHJ
              inspection.  We could just ditch the grid and go off-grid,
              but it seems like a shame to not tap into the grid
              resource.  Instead of dealing with the voltage drop, I was
              thinking it may make sense to rectify that low AC voltage
              input and parallel a smallish battery bank (size is yet to
              be determined), then use an off-grid inverter to serve the
              loads at good voltage.</div>
            <div><br>
            </div>
            <div>I am looking for feedback on this concept.  What do you
              think?</div>
            <div><br>
            </div>
            <div>Also, are there any recommendations for good quality
              rectifiers with wide input voltage window?  </div>
            <div><br>
            </div>
            <div>Thanks in advance for your help</div>
            <div>
              <div><br>
              </div>
              -- <br>
              <div dir="ltr">
                <div><br>
                </div>
                <div><font face="'times new roman', serif"
                    color="#305A78"><br>
                  </font></div>
                <div><br>
                </div>
                Mac Lewis<br>
                <br>
                <span style="font-family:&quot;Times New
                  Roman&quot;;font-size:medium;color:rgb(255,153,0)"><b><font
                      size="3" face="Arial, Helvetica, sans-serif">
                      <p align="left"><font face="Verdana, Arial,
                          Helvetica, sans-serif" color="#000000"><span
                            style="font-size:small"><span
                              style="font-family:arial;font-weight:normal;color:rgb(48,90,120)"><font
                                face="'times new roman', serif">"Yo solo
                                sé que no sé nada." </font><span
                                style="font-weight:700;color:rgb(104,104,104)"><font
                                  face="'times new roman', serif">-Sócrates</font></span></span></span></font></p>
                    </font></b></span></div>
            </div>
          </div>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          List Address: <a
            href="mailto:RE-wrenches@lists.re-wrenches.org"
            target="_blank" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
            rel="noreferrer" target="_blank" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm"
            rel="noreferrer" target="_blank" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" rel="noreferrer"
            target="_blank" moz-do-not-send="true">www.members.re-wrenches.org</a><br>
          <br>
        </blockquote>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>