<div><div dir="auto">Alan,</div></div><div dir="auto">  It appears to me that everyone miss read your question.  If your customer does not need a generator, then his solar charge controller needs to be able to be set up for the lithium battery voltage settings.  So the inverter simply needs to be 48 volts and has nothing to do with charging battery.  You could use any 48 volt inverter and use the MATE. The inverter would only provide LBCO to protect the battery.  As far as a used VFX 3648 contact me off list.</div><div dir="auto"><br></div><div dir="auto">John Blittersdorf</div><div dir="auto"><br></div><div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sat, Mar 7, 2020 at 8:20 PM Sindelar Solar &lt;<a href="mailto:Allan@sindelarsolar.com">Allan@sindelarsolar.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  

    
  
  <div text="#000000" bgcolor="#FFFFFF">
    <p>Wrenches,</p>
    <p>I have a client who is looking at upgrading an older off grid
      system that has an Outback VFX3524 inverter to 48V<sub>nom</sub>
      in order to use a Blue Ion LiFePo battery. I installed the VFX
      about ten years ago and it has worked without any issues. The
      client has never had a generator and has enough array to equalize
      his FLA batteries with array only, so has never had or needed a
      Mate. If I upgrade to 48V with a new inverter, it will most likely
      be an FXR3048. First question: Can I use an original Mate (rather
      than a Mate3) to set up basic programming with a R series
      inverter, such as charger and LBCO settings? Second: anyone have
      an older FX3048 or VFX3648 for sale, if the answer to the first
      question is no?</p>
    <p>Thank you, <br>
    </p>
    <p>Allan<br>
    </p>
    <div>-- <br>
      
      
      
      
      
      
      
      
      
      
      <div>
        <p class="MsoNormal" style="line-height:normal"><b><span>Allan
              Sindelar</span></b><span><br>
          </span><a href="mailto:allan@sindelarsolar.com" target="_blank"><span>allan@sindelarsolar.com</span></a><span><br>
          </span><span>NABCEP
            Certified PV Installation
            Professional<br>
            New Mexico EE98J Journeyman Electrician<br>
            Founder (Retired), <span>Positive
              Energy, Inc<span>.</span></span><br>
            <b>505 780-2738 cell</b></span><span><u></u><u></u></span></p>
        <p class="MsoNormal"><u></u> <u></u></p>
      </div>
    </div>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div></div>