    Jay,<br>
    <br>
    My point is that even if the diversion load can handle all of the
    watts and the PLC is fast enough to react to changes in the ac
    voltage, the system will probably still be unstable because the
    battery charger is in the control loop.<br>
    <br>
    Kent Osterberg<br>
    Blue Mountain Solar<br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 3/4/2020 9:25 AM, Jay wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:B10DE151-3755-4977-B96E-06BF17D13B5A@gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">Hi Kent,</div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr">Johns diversion load/controller would take have to
        take care of watts and ac voltage parameters. </div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr">Jay</div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr"><br>
      </div>
      <div dir="ltr"><br>
        <blockquote type="cite">On Mar 4, 2020, at 9:00 AM, Kent
          Osterberg <a class="moz-txt-link-rfc2396E" href="mailto:kent@coveoregon.com">&lt;kent@coveoregon.com&gt;</a> wrote:<br>
          <br>
        </blockquote>
      </div>
      <blockquote type="cite">
        <div dir="ltr">\ufeff
          <meta http-equiv="Content-Type" content="text/html;
            charset=UTF-8">
          If using an ac battery charger to get power around the
          inverter to the batteries it would have to be rated for the
          full power of the PV array. Otherwise, you couldn't divert the
          full power of the array on the dc side. For a 24-volt battery,
          it would require a battery charger rated for over 80 amps.
          That alone seems risky with a 100Ah battery. To add to the
          difficulty of this approach the battery charger would add a
          delay time in the control loop that would almost certainly
          result in an unstable system. <br>
          <br>
          Kent Osterberg<br>
          <br>
          <br>
          <div class="moz-cite-prefix">On 3/3/2020 7:53 PM, Jay wrote:<br>
          </div>
          <blockquote type="cite"
            cite="mid:DCB3538C-E68F-406E-B8AA-AEE8971EB597@gmail.com">
            <meta http-equiv="content-type" content="text/html;
              charset=UTF-8">
            <div dir="ltr">Or a charger such as Iota, or power max. </div>
            <div dir="ltr"><br>
            </div>
            <div dir="ltr">Jay</div>
            <div dir="ltr">Peltz power. </div>
            <div dir="ltr"><br>
              <blockquote type="cite">On Mar 3, 2020, at 7:24 PM, <a
                  class="moz-txt-link-abbreviated"
                  href="mailto:don@energysolarnow.com"
                  moz-do-not-send="true">don@energysolarnow.com</a>
                wrote:<br>
                <br>
              </blockquote>
            </div>
            <blockquote type="cite">
              <div dir="ltr">\ufeff<span style="font-family:Verdana;
                  color:#000000; font-size:10pt;">
                  <div>You wrote that you would connect the Exeltech to
                    just one of the service phases. </div>
                  <div>But most GT inverters are 240 and require both
                    phases. Is yours different? You did not mention
                    which model it is. </div>
                  <div>Also, as Kent Osterberg mentioned, the Exeltech
                    will not charge its batteries from the AC output. </div>
                  <div>Your scheme with the PLC controlling an SCR
                    leaves unaddressed how any charge current gets
                    directed into the batteries to allegedly raise their
                    voltage. Is there a charger somewhere in this
                    scheme?<br>
                  </div>
                  <div>You still need some way to charge batteries from
                    solar. How about connecting a charge controller to
                    some of the solar panels?</div>
                  <div><br>
                  </div>
                  <div>Don Barch</div>
                  <div>Energy Solar<br>
                  </div>
                  <blockquote id="replyBlockquote" webmail="1"
                    style="border-left: 2px solid blue; margin-left:
                    8px; padding-left: 8px; font-size:10pt; color:black;
                    font-family:verdana;">
                    <div id="wmQuoteWrapper"> -------- Original Message
                      --------<br>
                      Subject: RE-wrenches Digest, Vol 13, Issue 59<br>
                      From: <a
                        href="mailto:re-wrenches-request@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches-request@lists.re-wrenches.org</a><br>
                      Date: Sun, March 01, 2020 2:19 pm<br>
                      To: <a
                        href="mailto:re-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Send RE-wrenches mailing list submissions to<br>
                      <a href="mailto:re-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      To subscribe or unsubscribe via the World Wide
                      Web, visit<br>
                      <a
href="http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org"
                        moz-do-not-send="true">http://lists.re-wrenches.org/listinfo.cgi/re-wrenches-re-wrenches.org</a><br>
                      or, via email, send a message with subject or body
                      'help' to<br>
                      <a
                        href="mailto:re-wrenches-request@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches-request@lists.re-wrenches.org</a><br>
                      <br>
                      You can reach the person managing the list at<br>
                      <a
                        href="mailto:re-wrenches-owner@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches-owner@lists.re-wrenches.org</a><br>
                      <br>
                      When replying, please edit your Subject line so it
                      is more specific<br>
                      than "Re: Contents of RE-wrenches digest..."<br>
                      <br>
                      <br>
                      When responding to posts within the Digest, be
                      sure to restore the Subject: line to the original,
                      and please edit out any extraneous lines from the
                      quoted message.<br>
                      <br>
                      <br>
                      Today's Topics:<br>
                      <br>
                      1. OK, so what iwould happen if I do this... (Mark
                      Frye)<br>
                      2. Re: OK, so what iwould happen if I do this...
                      (frenergy)<br>
                      3. Re: OK, so what iwould happen if I do this...
                      (Kent Osterberg)<br>
                      4. Re: OK, so what iwould happen if I do this...
                      (Jerry Shafer)<br>
                      <br>
                      <br>
----------------------------------------------------------------------<br>
                      <br>
                      Message: 1<br>
                      Date: Sat, 29 Feb 2020 15:27:32 -0800<br>
                      From: Mark Frye &lt;<a
                        href="mailto:markf@berkeleysolar.com"
                        moz-do-not-send="true">markf@berkeleysolar.com</a>&gt;<br>
                      To: RE-wrenches &lt;<a
                        href="mailto:re-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                      Subject: [RE-wrenches] OK, so what iwould happen
                      if I do this...<br>
                      Message-ID: &lt;<a
                        href="mailto:93731c38-40b5-7c63-1d74-a879fbdd9d74@berkeleysolar.com"
                        moz-do-not-send="true">93731c38-40b5-7c63-1d74-a879fbdd9d74@berkeleysolar.com</a>&gt;<br>
                      Content-Type: text/plain; charset=utf-8;
                      format=flowed<br>
                      <br>
                      I have 2kw of grid tied PV on my house.<br>
                      <br>
                      Suppose I:<br>
                      <br>
                      - Open the main breaker to disconnect from the
                      grid<br>
                      <br>
                      - I open the PV breaker<br>
                      <br>
                      - I connect a small good quality inverter like an
                      Exeltech XP 500 to one <br>
                      of the phases of the service (120 VAC)<br>
                      <br>
                      - I put a small battery pack, 100 AH at 24 VDC on
                      the inverter<br>
                      <br>
                      OK so far, I could run some small loads for a
                      relatively short period of <br>
                      time before the batteries get low<br>
                      <br>
                      -I have a PLC with an AD input and DA output. On
                      the input I measure the <br>
                      battery voltage, on the output I control a SCR.
                      The SCR controls a 2kw <br>
                      immersion heater sitting in a big bucket of water.
                      The PLC has a scan <br>
                      time of 2 mS and I program it to increase the duty
                      cycle of the SCR as <br>
                      voltage of the battery rises above 24 VDC.<br>
                      <br>
                      OK so far nothing has really changed from above.<br>
                      <br>
                      - I close the PV breaker, the GT inverters see the
                      battery inverter, <br>
                      sync and connect after five minutes.<br>
                      <br>
                      Voila, I can run house loads from 0 to 2kw with my
                      existing GT PV with <br>
                      the balance of energy dumped as needed to the
                      immersion heater.<br>
                      <br>
                      Right?<br>
                      <br>
                      Mark Frye<br>
                      <br>
                      <br>
                      <br>
                      ------------------------------<br>
                      <br>
                      Message: 2<br>
                      Date: Sun, 1 Mar 2020 06:26:27 -0800<br>
                      From: frenergy &lt;<a
                        href="mailto:frenergy@psln.com"
                        moz-do-not-send="true">frenergy@psln.com</a>&gt;<br>
                      To: <a
                        href="mailto:re-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a><br>
                      Subject: Re: [RE-wrenches] OK, so what iwould
                      happen if I do this...<br>
                      Message-ID: &lt;<a
                        href="mailto:c97234cd-4441-34d7-740c-51f07837b081@psln.com"
                        moz-do-not-send="true">c97234cd-4441-34d7-740c-51f07837b081@psln.com</a>&gt;<br>
                      Content-Type: text/plain; charset=utf-8;
                      format=flowed<br>
                      <br>
                      Mark,<br>
                      <br>
                      ??? ??? ??? OR, you change-out your inverter to an
                      SMA with Secure <br>
                      Power Supply and during grid power outage, while
                      there is some sun on <br>
                      the panels, you would have up to 2KW of 120VAC
                      power on the SPS circuit <br>
                      by just flipping a switch. We usually install a 4X
                      outdoor box with a <br>
                      120 VAC outlet ganged with a switch right under
                      the inverter and let the <br>
                      customer run the power to the : frig, lights,
                      battery charger, TV or <br>
                      whatever during an outage, though some romex could
                      be run to close to <br>
                      the frig.<br>
                      <br>
                      Bill<br>
                      <br>
                      Feather River Solar Electric<br>
                      Bill Battagin, Owner<br>
                      4291 Nelson St.<br>
                      Taylorsville, CA 95983<br>
                      530.284.7849<br>
                      CA Lic 874049<br>
                      <a href="http://www.frenergy.net"
                        moz-do-not-send="true">www.frenergy.net</a><br>
                      <br>
                      On 2/29/2020 3:27 PM, Mark Frye wrote:<br>
                      &gt; I have 2kw of grid tied PV on my house.<br>
                      &gt;<br>
                      &gt; Suppose I:<br>
                      &gt;<br>
                      &gt; - Open the main breaker to disconnect from
                      the grid<br>
                      &gt;<br>
                      &gt; - I open the PV breaker<br>
                      &gt;<br>
                      &gt; - I connect a small good quality inverter
                      like an Exeltech XP 500 to <br>
                      &gt; one of the phases of the service (120 VAC)<br>
                      &gt;<br>
                      &gt; - I put a small battery pack, 100 AH at 24
                      VDC on the inverter<br>
                      &gt;<br>
                      &gt; OK so far, I could run some small loads for a
                      relatively short period <br>
                      &gt; of time before the batteries get low<br>
                      &gt;<br>
                      &gt; -I have a PLC with an AD input and DA output.
                      On the input I measure <br>
                      &gt; the battery voltage, on the output I control
                      a SCR. The SCR controls a <br>
                      &gt; 2kw immersion heater sitting in a big bucket
                      of water. The PLC has a <br>
                      &gt; scan time of 2 mS and I program it to
                      increase the duty cycle of the <br>
                      &gt; SCR as voltage of the battery rises above 24
                      VDC.<br>
                      &gt;<br>
                      &gt; OK so far nothing has really changed from
                      above.<br>
                      &gt;<br>
                      &gt; - I close the PV breaker, the GT inverters
                      see the battery inverter, <br>
                      &gt; sync and connect after five minutes.<br>
                      &gt;<br>
                      &gt; Voila, I can run house loads from 0 to 2kw
                      with my existing GT PV with <br>
                      &gt; the balance of energy dumped as needed to the
                      immersion heater.<br>
                      &gt;<br>
                      &gt; Right?<br>
                      &gt;<br>
                      &gt; Mark Frye<br>
                      &gt;<br>
                      &gt;
                      _______________________________________________<br>
                      &gt; List sponsored by Redwood Alliance<br>
                      &gt;<br>
                      &gt; List Address: <a
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                      &gt;<br>
                      &gt; Change listserver email address &amp;
                      settings:<br>
                      &gt; <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      &gt;<br>
                      &gt; List-Archive: <br>
                      &gt; <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                        moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                      &gt;<br>
                      &gt; List rules &amp; etiquette:<br>
                      &gt; <a
                        href="http://www.re-wrenches.org/etiquette.htm"
                        moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                      &gt;<br>
                      &gt; Check out or update participant bios:<br>
                      &gt; <a href="http://www.members.re-wrenches.org"
                        moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                      &gt;<br>
                      &gt;<br>
                      -- <br>
                      <br>
                      <br>
                      -- <br>
                      This email has been checked for viruses by Avast
                      antivirus software.<br>
                      <a href="https://www.avast.com/antivirus"
                        moz-do-not-send="true">https://www.avast.com/antivirus</a><br>
                      <br>
                      <br>
                      <br>
                      <br>
                      ------------------------------<br>
                      <br>
                      Message: 3<br>
                      Date: Sun, 1 Mar 2020 08:58:45 -0800<br>
                      From: Kent Osterberg &lt;<a
                        href="mailto:kent@coveoregon.com"
                        moz-do-not-send="true">kent@coveoregon.com</a>&gt;<br>
                      To: <a
                        href="mailto:re-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a><br>
                      Subject: Re: [RE-wrenches] OK, so what iwould
                      happen if I do this...<br>
                      Message-ID: &lt;<a
                        href="mailto:9e32901e-c5d4-ff70-9c44-406cc6d48d50@coveoregon.com"
                        moz-do-not-send="true">9e32901e-c5d4-ff70-9c44-406cc6d48d50@coveoregon.com</a>&gt;<br>
                      Content-Type: text/plain; charset=utf-8;
                      format=flowed<br>
                      <br>
                      Mark,<br>
                      <br>
                      I believe that your plan would fail because you
                      are forcing power to <br>
                      flow through the XP inverter backwards to charge
                      the batteries. I don't <br>
                      believe the XP inverter can do that. The grid tied
                      inverter would <br>
                      probably connect then immediately shut down, or
                      connect and immediately <br>
                      ruin the XP inverter. It would work if you had a
                      inverter with a <br>
                      bidirectional architecture like a Magnum, Outback,
                      or Schneider <br>
                      inverter. But even then you'd have a hazardous
                      situation because the <br>
                      cooling water is going to evaporate.<br>
                      <br>
                      Kent Osterberg<br>
                      Blue Mountain Solar<br>
                      <br>
                      <br>
                      On 2/29/2020 3:27 PM, Mark Frye wrote:<br>
                      &gt; I have 2kw of grid tied PV on my house.<br>
                      &gt;<br>
                      &gt; Suppose I:<br>
                      &gt;<br>
                      &gt; - Open the main breaker to disconnect from
                      the grid<br>
                      &gt;<br>
                      &gt; - I open the PV breaker<br>
                      &gt;<br>
                      &gt; - I connect a small good quality inverter
                      like an Exeltech XP 500 to <br>
                      &gt; one of the phases of the service (120 VAC)<br>
                      &gt;<br>
                      &gt; - I put a small battery pack, 100 AH at 24
                      VDC on the inverter<br>
                      &gt;<br>
                      &gt; OK so far, I could run some small loads for a
                      relatively short period <br>
                      &gt; of time before the batteries get low<br>
                      &gt;<br>
                      &gt; -I have a PLC with an AD input and DA output.
                      On the input I measure <br>
                      &gt; the battery voltage, on the output I control
                      a SCR. The SCR controls a <br>
                      &gt; 2kw immersion heater sitting in a big bucket
                      of water. The PLC has a <br>
                      &gt; scan time of 2 mS and I program it to
                      increase the duty cycle of the <br>
                      &gt; SCR as voltage of the battery rises above 24
                      VDC.<br>
                      &gt;<br>
                      &gt; OK so far nothing has really changed from
                      above.<br>
                      &gt;<br>
                      &gt; - I close the PV breaker, the GT inverters
                      see the battery inverter, <br>
                      &gt; sync and connect after five minutes.<br>
                      &gt;<br>
                      &gt; Voila, I can run house loads from 0 to 2kw
                      with my existing GT PV with <br>
                      &gt; the balance of energy dumped as needed to the
                      immersion heater.<br>
                      &gt;<br>
                      &gt; Right?<br>
                      &gt;<br>
                      &gt; Mark Frye<br>
                      &gt;<br>
                      &gt;
                      _______________________________________________<br>
                      &gt; List sponsored by Redwood Alliance<br>
                      &gt;<br>
                      &gt; List Address: <a
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                      &gt;<br>
                      &gt; Change listserver email address &amp;
                      settings:<br>
                      &gt; <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      &gt;<br>
                      &gt; List-Archive: <br>
                      &gt; <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                        moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                      &gt;<br>
                      &gt; List rules &amp; etiquette:<br>
                      &gt; <a
                        href="http://www.re-wrenches.org/etiquette.htm"
                        moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                      &gt;<br>
                      &gt; Check out or update participant bios:<br>
                      &gt; <a href="http://www.members.re-wrenches.org"
                        moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                      &gt;<br>
                      &gt;<br>
                      <br>
                      <br>
                      <br>
                      ------------------------------<br>
                      <br>
                      Message: 4<br>
                      Date: Sun, 1 Mar 2020 07:31:36 -1000<br>
                      From: Jerry Shafer &lt;<a
                        href="mailto:jerrysgarage01@gmail.com"
                        moz-do-not-send="true">jerrysgarage01@gmail.com</a>&gt;<br>
                      To: RE-wrenches &lt;<a
                        href="mailto:re-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                      Subject: Re: [RE-wrenches] OK, so what iwould
                      happen if I do this...<br>
                      Message-ID:<br>
                      &lt;<a
href="mailto:CAMUFgmVYBnMmzgE__tjDS9xpFsOU59jdf3wwSkFhjw291VGH0g@mail.gmail.com"
                        moz-do-not-send="true">CAMUFgmVYBnMmzgE__tjDS9xpFsOU59jdf3wwSkFhjw291VGH0g@mail.gmail.com</a>&gt;<br>
                      Content-Type: text/plain; charset="utf-8"<br>
                      <br>
                      Mark<br>
                      What you are saying is to AC couple but most
                      likely this would fail as your<br>
                      battery fills not enough loads HBCO or to much
                      loads and your battery does<br>
                      a LBCO, either way you would be better off
                      spending the money in a maybe a<br>
                      Outback Skybox easy install and is high voltage PV
                      input and even a small<br>
                      48 volt bank but think about storage<br>
                      Jerry<br>
                      <br>
                      On Sat, Feb 29, 2020 at 1:27 PM Mark Frye &lt;<a
                        href="mailto:markf@berkeleysolar.com"
                        moz-do-not-send="true">markf@berkeleysolar.com</a>&gt;
                      wrote:<br>
                      <br>
                      &gt; I have 2kw of grid tied PV on my house.<br>
                      &gt;<br>
                      &gt; Suppose I:<br>
                      &gt;<br>
                      &gt; - Open the main breaker to disconnect from
                      the grid<br>
                      &gt;<br>
                      &gt; - I open the PV breaker<br>
                      &gt;<br>
                      &gt; - I connect a small good quality inverter
                      like an Exeltech XP 500 to one<br>
                      &gt; of the phases of the service (120 VAC)<br>
                      &gt;<br>
                      &gt; - I put a small battery pack, 100 AH at 24
                      VDC on the inverter<br>
                      &gt;<br>
                      &gt; OK so far, I could run some small loads for a
                      relatively short period of<br>
                      &gt; time before the batteries get low<br>
                      &gt;<br>
                      &gt; -I have a PLC with an AD input and DA output.
                      On the input I measure the<br>
                      &gt; battery voltage, on the output I control a
                      SCR. The SCR controls a 2kw<br>
                      &gt; immersion heater sitting in a big bucket of
                      water. The PLC has a scan<br>
                      &gt; time of 2 mS and I program it to increase the
                      duty cycle of the SCR as<br>
                      &gt; voltage of the battery rises above 24 VDC.<br>
                      &gt;<br>
                      &gt; OK so far nothing has really changed from
                      above.<br>
                      &gt;<br>
                      &gt; - I close the PV breaker, the GT inverters
                      see the battery inverter,<br>
                      &gt; sync and connect after five minutes.<br>
                      &gt;<br>
                      &gt; Voila, I can run house loads from 0 to 2kw
                      with my existing GT PV with<br>
                      &gt; the balance of energy dumped as needed to the
                      immersion heater.<br>
                      &gt;<br>
                      &gt; Right?<br>
                      &gt;<br>
                      &gt; Mark Frye<br>
                      &gt;<br>
                      &gt;
                      _______________________________________________<br>
                      &gt; List sponsored by Redwood Alliance<br>
                      &gt;<br>
                      &gt; List Address: <a
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                      &gt;<br>
                      &gt; Change listserver email address &amp;
                      settings:<br>
                      &gt; <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      &gt;<br>
                      &gt; List-Archive:<br>
                      &gt; <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                        moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                      &gt;<br>
                      &gt; List rules &amp; etiquette:<br>
                      &gt; <a
                        href="http://www.re-wrenches.org/etiquette.htm"
                        moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                      &gt;<br>
                      &gt; Check out or update participant bios:<br>
                      &gt; <a href="http://www.members.re-wrenches.org"
                        moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                      &gt;<br>
                      &gt;<br>
                      -------------- next part --------------<br>
                      An HTML attachment was scrubbed...<br>
                      URL: &lt;<a
href="http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200301/a993182d/attachment-0001.html"
                        moz-do-not-send="true">http://lists.re-wrenches.org/pipermail/re-wrenches-re-wrenches.org/attachments/20200301/a993182d/attachment-0001.html</a>&gt;<br>
                      <br>
                      ------------------------------<br>
                      <br>
                      Subject: Digest Footer<br>
                      <br>
                      _______________________________________________<br>
                      List sponsored by Redwood Alliance<br>
                      <br>
                      List Address: <a
                        href="mailto:RE-wrenches@lists.re-wrenches.org"
                        moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                      <br>
                      Change listserver email address &amp; settings:<br>
                      <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                        moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
                      <br>
                      List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                        moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
                      <br>
                      List rules &amp; etiquette:<br>
                      <a href="http://www.re-wrenches.org/etiquette.htm"
                        moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                      <br>
                      Check out or update participant bios:<br>
                      <a href="http://www.members.re-wrenches.org"
                        moz-do-not-send="true">www.members.re-wrenches.org</a><br>
                      <br>
                      <br>
                      ------------------------------<br>
                      <br>
                      End of RE-wrenches Digest, Vol 13, Issue 59<br>
                      *******************************************<br>
                    </div>
                  </blockquote>
                </span> <span>_______________________________________________</span><br>
                <span>List sponsored by Redwood Alliance</span><br>
                <span></span><br>
                <span>List Address: <a class="moz-txt-link-abbreviated"
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a></span><br>
                <span></span><br>
                <span>Change listserver email address &amp; settings:</span><br>
                <span><a class="moz-txt-link-freetext"
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                    moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
                <span></span><br>
                <span>List-Archive:
                  <a class="moz-txt-link-freetext"
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                    moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br>
                <span></span><br>
                <span>List rules &amp; etiquette:</span><br>
                <span><a class="moz-txt-link-abbreviated"
                    href="http://www.re-wrenches.org/etiquette.htm"
                    moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a></span><br>
                <span></span><br>
                <span>Check out or update participant bios:</span><br>
                <span><a class="moz-txt-link-abbreviated"
                    href="http://www.members.re-wrenches.org"
                    moz-do-not-send="true">www.members.re-wrenches.org</a></span><br>
                <span></span><br>
              </div>
            </blockquote>
            <br>
            <fieldset class="mimeAttachmentHeader"></fieldset>
            <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
          </blockquote>
          <br>
          <span>_______________________________________________</span><br>
          <span>List sponsored by Redwood Alliance</span><br>
          <span></span><br>
          <span>List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a></span><br>
          <span></span><br>
          <span>Change listserver email address &amp; settings:</span><br>
          <span><a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a></span><br>
          <span></span><br>
          <span>List-Archive:
<a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a></span><br>
          <span></span><br>
          <span>List rules &amp; etiquette:</span><br>
          <span><a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a></span><br>
          <span></span><br>
          <span>Check out or update participant bios:</span><br>
          <span><a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a></span><br>
          <span></span><br>
        </div>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>