<div dir="ltr"><div>Mark <br></div><div>What you are saying is to AC couple but most likely this would fail as your battery fills not enough loads HBCO or to much loads and your battery does a LBCO, either way you would be better off spending the money in a maybe a Outback Skybox easy install and is high voltage PV input and even a small 48 volt bank but think about storage <br></div><div>Jerry<br></div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Sat, Feb 29, 2020 at 1:27 PM Mark Frye &lt;<a href="mailto:markf@berkeleysolar.com">markf@berkeleysolar.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">I have 2kw of grid tied PV on my house.<br>
<br>
Suppose I:<br>
<br>
- Open the main breaker to disconnect from the grid<br>
<br>
- I open the PV breaker<br>
<br>
- I connect a small good quality inverter like an Exeltech XP 500 to one <br>
of the phases of the service (120 VAC)<br>
<br>
- I put a small battery pack, 100 AH at 24 VDC on the inverter<br>
<br>
OK so far, I could run some small loads for a relatively short period of <br>
time before the batteries get low<br>
<br>
-I have a PLC with an AD input and DA output. On the input I measure the <br>
battery voltage, on the output I control a SCR. The SCR controls a 2kw <br>
immersion heater sitting in a big bucket of water. The PLC has a scan <br>
time of 2 mS and I program it to increase the duty cycle of the SCR as <br>
voltage of the battery rises above 24 VDC.<br>
<br>
OK so far nothing has really changed from above.<br>
<br>
- I close the PV breaker, the GT inverters see the battery inverter, <br>
sync and connect after five minutes.<br>
<br>
Voila, I can run house loads from 0 to 2kw with my existing GT PV with <br>
the balance of energy dumped as needed to the immersion heater.<br>
<br>
Right?<br>
<br>
Mark Frye<br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>