<p>This has been discussed to death in previous Wrench strings.
Just to cut to the chase:</p>
<p>please review NEC 2017, Figure 690.1(b) Note:(2). <i>The PV
system disconnect in these diagrams separates the PV system from
all other systems.</i><i><br>
</i></p>
<p>The inverter, charge controller, batteries etc are no longer part
of article 690, and are not subject to its requirements. Look at
articles 705, 706, and 480 for guidance for those <u><i>other
systems</i></u>.<br>
<i></i></p>
<pre class="moz-signature" cols="72"><i>Ray Walters</i>
Remote Solar
303 505-8760</pre>
<div class="moz-cite-prefix">On 2/13/20 12:55 PM, Dave Angelini
Offgrid Solar wrote:<br>
</div>
<blockquote type="cite"
cite="mid:e89e383931b76e89eeb3aa364eafea8a@127.0.0.1">
<pre class="moz-quote-pre" wrap="">Hi Chris,
A few times and my back-up with a schneider system is their rapid
shutdown. In the end the inspector comes around and realizes there is
little gain for an offgrid ground mounted array for fireman. You do have to
educate them and if they are insistent on being a bonehead, install the RS
for the inspection and then use the box for the next one or sell it.
After almost 30 years offgrid the last thing I want is something that can
fault out the solar or worse when I am away. Networks can be the enemy at
times. Less is more offgrid in my opinion.
Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a class="moz-txt-link-freetext" href="http://members.sti.net/offgridsolar/">http://members.sti.net/offgridsolar/</a>
e-mail <a class="moz-txt-link-abbreviated" href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a>
text 209 813 0060
On Thu, 13 Feb 2020 13:07:53 -0500, Christopher Warfel
<a class="moz-txt-link-rfc2396E" href="mailto:cwarfel@entech-engineering.com"><cwarfel@entech-engineering.com></a> wrote:
</pre>
<blockquote type="cite">
<pre class="moz-quote-pre" wrap="">I got involved in a long discussion on Rapid Shutdown compliance for
battery multimode, grid interconnect inverters that have a ground
mounted array. At one point, ground mounted array was not supposed to
be subject to Rapid Shutdown unless there were dc conductors on the
building. NEC 2017 seems to say it is if conductors are 3' in or on
buildings. The intent of Rapid Shutdown was supposed to protect fire
fighters from exposure to high dc voltage when the array was on a roof.
Every code cycle it morphs into something a little different. Has
anyone had to confront this situation, and was this type of project
subject to Rapid Shutdown? Thanks in advance for any clarity on this.
Chris
_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive:
</pre>
</blockquote>
<pre class="moz-quote-pre" wrap=""><a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
</pre>
<blockquote type="cite">
<pre class="moz-quote-pre" wrap="">
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
</body>
</html>