    <p>It all comes down to where you install the PV disconnect.  We put
      it on the wall before the conductors enter the building or at the
      array, therefore 690 doesn't apply.  Proper signage is required
      indicating multiple power sources and listing the locations of
      their disconnects.  <br>
    </p>
    <p>Also, this isn't just my opinion, many others on the list have
      said this, including folks involved in the code writing process,
      and the code says this.  The fact that your inspector didn't catch
      the note on the figure is to be expected, as it is not out in
      flashing neon lights.  It is however a clear statement of where
      690 stops: at the PV disconnect. <br>
    </p>
    <p>Unfortunately, this is not further clarified in 2020 from what I
      can tell, so we will all continue to suffer inspectors incorrectly
      expecting 690.12 on ground mounted systems.  I would politely ask
      your inspector to review that ruling with his higher ups.  We
      can't start setting precedents that are unreasonable and
      incorrect.  The array wiring is already required to be protected
      by either height, protective panels or fencing.  <br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 2/13/20 1:56 PM, Christopher Warfel
      wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:e7b0c1d2-c021-d5fb-7688-b20d0a0e2ede@entech-engineering.com">
      <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
      <p>Ray, I spent a bit of time today with a person who inspects for
        several state renewable energy programs and to summarize, this
        person said the opposite of what you said, and finish saying
        "seems pretty clear cut".  We did review three sections of 690,
        and one from 705.  I pointed out that these are not controlled
        conductors as I interpret them but they should have been
        defined.   I did not see any earlier posts regarding this, so I
        apologize for the redundancy. <br>
      </p>
      <div class="moz-cite-prefix">On 2/13/2020 3:16 PM, Ray wrote:<br>
      </div>
      <blockquote type="cite"
        cite="mid:9d3305f0-5a60-28ee-696b-e292126d8ba4@solarray.com">
        <meta http-equiv="Content-Type" content="text/html;
          charset=UTF-8">
        <p>This has been discussed to death in previous Wrench strings. 
          Just to cut to the chase:</p>
        <p>please review NEC 2017, Figure 690.1(b) Note:(2). <i>The PV
            system disconnect in these diagrams separates the PV system
            from all other systems.</i><i><br>
          </i></p>
        <p>The inverter, charge controller, batteries etc are no longer
          part of article 690, and are not subject to its requirements. 
          Look at articles 705, 706, and 480 for guidance for those <u><i>other
              systems</i></u>.<br>
        </p>
        <pre class="moz-signature" cols="72"><i>Ray Walters</i>
Remote Solar
303 505-8760</pre>
        <div class="moz-cite-prefix">On 2/13/20 12:55 PM, Dave Angelini
          Offgrid Solar wrote:<br>
        </div>
        <blockquote type="cite"
          cite="mid:e89e383931b76e89eeb3aa364eafea8a@127.0.0.1">
          <pre class="moz-quote-pre" wrap="">Hi Chris,

A few times and my back-up with a schneider system is their rapid
shutdown. In the end the inspector comes around and realizes there is
little gain for an offgrid ground mounted array for fireman. You do have to
educate them and if they are insistent on being a bonehead, install the RS
for the inspection and then use the box for the next one or sell it.

 After almost 30 years offgrid the last thing I want is something that can
fault out the solar or worse when I am away. Networks can be the enemy at
times. Less is more offgrid in my opinion.


Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a class="moz-txt-link-freetext" href="http://members.sti.net/offgridsolar/" moz-do-not-send="true">http://members.sti.net/offgridsolar/</a>
e-mail <a class="moz-txt-link-abbreviated" href="mailto:offgridsolar@sti.net" moz-do-not-send="true">offgridsolar@sti.net</a>
text 209 813 0060

On Thu, 13 Feb 2020 13:07:53 -0500, Christopher Warfel
<a class="moz-txt-link-rfc2396E" href="mailto:cwarfel@entech-engineering.com" moz-do-not-send="true">&lt;cwarfel@entech-engineering.com&gt;</a> wrote:
</pre>
          <blockquote type="cite">
            <pre class="moz-quote-pre" wrap="">I got involved in a long discussion on Rapid Shutdown compliance for 
battery multimode, grid interconnect inverters that have a ground 
mounted array.  At one point, ground mounted array was not supposed to 
be subject to Rapid Shutdown unless there were dc conductors on the 
building.  NEC 2017 seems to say it is if conductors are 3' in or on 
buildings.  The intent of Rapid Shutdown was supposed to protect fire 
fighters from exposure to high dc voltage when the array was on a roof. 
Every code cycle it morphs into something a little different.  Has 
anyone had to confront this situation, and was this type of project 
subject to Rapid Shutdown?  Thanks in advance for any clarity on this.  
Chris

_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:

</pre>
          </blockquote>
          <pre class="moz-quote-pre" wrap=""><a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
</pre>
          <blockquote type="cite">
            <pre class="moz-quote-pre" wrap="">List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>
</pre>
          </blockquote>
          <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
        </blockquote>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>