<div dir="ltr"><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">(System installed by another contractor...)</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif">I have been tasked with assisting in the investigation of damage in a subpanel used to combine inverter output circuits (5 strings of microinverters). There appears to be no damage to conductors or other system components. It looks like the damage started at the stabs of the bus bar where the breakers connect. Picture attached. Here are a few clues:</div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><ul><li>Monitoring indicates that damage occurred overnight a few weeks ago. That night we had rain as a winter front came through Florida, possibly lightning. The prior day everything was fine.</li><li>The next morning, only 2 of 5 strings started producing power, but 4 of 5 strings were reporting data to the Envoy. The two strings that were reporting but not producing power reported 0Vac and Voc on the DC side of the microinverters. </li><li>A couple of weeks later, 1 of the 2 strings that was producing power quit doing so, but continued reporting data.</li><li>Customer discovered damage yesterday.</li><li>About a week before the initial damage apparently manifested itself, another contractor installed a whole house generator transfer switch on the line side of the PV interconnection. The generator has never been run (there is not even a LP fuel source on site yet). I pointed out that the solar interconnection, which was previously on the supply side, would need to be moved to the supply side of the generator transfer switch&#39;s main breaker before operation. During the transfer switch installation, the contractor also switched line 1 and line 2, but that shouldn&#39;t really matter, except for Enphase consumption monitoring, which was messed up by the swapping of the lines.</li></ul><div>So I&#39;m looking for ideas. I&#39;m wondering if the OCPD would be a likely place for lightning damage to manifest itself. I can&#39;t visually detect any other damage anywhere else. I can&#39;t imagine that the transfer switch installation would have anything to do with it, but the timing is interesting. Other than replacing the subpanel and OCPD and firing it back up (no pun intended), I&#39;m not sure how to approach further investigation.</div><div><br></div><div>Jason Szumlanski</div><div>Florida Solar Design Group</div></div><div class="gmail_default" style="font-family:arial,helvetica,sans-serif"><br></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><div dir="ltr"><b><div style="text-align:center"><br></div></b></div></div></div></div></div></div></div></div></div><img width="0" height="0" class="mailtrack-img" alt="" style="display:flex" src="https://mailtrack.io/trace/mail/d61b72d4441dc65e0ee620272d7a5c2d9d261222.png?u=1613865"></div>