<div dir="ltr">Designing with a CPS 50/60TL for the first time and I&#39;m sure the contractor (my client) is going to want to leave off the neutral connection because Chint says it&#39;s optional. Not crazy about it but I have no good anecdotal evidence to point to it being a bad idea. Faults can still clear as long as there&#39;s an MBJ at the panel or xfmr (which there will be) so I&#39;m not worried about safety. Just curious if anyone&#39;s had trouble with monitoring on these when there&#39;s no neutral installed. My preference is just to keep it there but downsize it to the EGC size to save on copper. Thanks in advance!<div><br></div><div>// Evan</div></div>