<div dir="ltr">Greetings, Wrenchies~<div><br></div><div>Matt Sherald&#39;s subject today resembles a client inquiry that is on my radar this week--perfect timing!</div><div><br></div><div>Dave Angelini &amp; All~ What if only the PV array negatives are in parallel but the PV positives are divided across more than one charge controller? </div><div>My client is on the Outback platform instead of Schneider, the battery negative is grounded &amp; by extension the PV negatives are also grounded. </div><div>Client has no DC GFI since it&#39;s an older installation &amp; he would add three Flexmax 80 controllers; we&#39;ll put appropriate DC breakers on each PV+</div><div>&amp; Battery+ controller wire. Client&#39;s Mate 1 is old school so the revved up Flexmax 100 (with no built in display) is not of much interest in this case.</div><div><br></div><div>The reason the client needs to share PV negative across the controllers is it&#39;s a retrofit situation with some wires in place &amp; no simple</div><div>way to add more.  No inspectors are involved &amp; I see no technical problem. Your thoughts?</div><div><br></div><div>The Wrench List is the Bomb!</div><div><br clear="all"><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br><br>Landline: 970-731-4675</div><div>Cell phone or for text messaging: 970-946-6584</div></div></div></div></div></div><div hspace="streak-pt-mark" style="max-height:1px"><img alt="" style="width:0px;max-height:0px;overflow:hidden" src="https://mailfoogae.appspot.com/t?sender=abWlja0BhYnJhaGFtc29sYXIuY29t&amp;type=zerocontent&amp;guid=e85b5771-cf6a-4e71-8576-9af402e183a0"><font color="#ffffff" size="1">\u1427</font></div>