Wrenches,<br>
  <br>
I've got 5 SB 7.7s going in and I'm contemplating various ways to 
configure the 5 SPS circuits.<br>
  <br>
Questions:<br>
  <br>
1.  I'm not clear if additional overcurrent protection is needed 
anywhere in the circuit?  - the SMA manual doesn't mention it and I'm 
wondering if it's built in?  I assume the switch is not carrying the 
current so doesn't need OCP but how about the outlet?<br>
  <br>
2.  SMA recommends 30mA of for the GFCI device - Most GFCI outlets are 
5mA (Class A) or 20mA (Class B).  What have folks been using to avoid 
nuisance tripping?  Does this lead us back to a 30mA GFCI breaker?<br>
  <br>
3.  Anyone experience appliance damage from brownouts - can one run 
multiple fridges on one 16 Amp circuit?  Experience?<br>
  <br>
Thanks!<br>
  <br>
Jeff<br>
  <br>
  <div class="moz-signature"><span>~~~~~~~~~~~<br>





</span>
<div class="moz-signature">

  <span>Jeff Clearwater</span><span><span><br>
  </span>Village Power Design<br>
  </span><span><span><span><a 
href="https://www.linkedin.com/in/jeff-clearwater-0622a312/">linkedin</a>
 </span></span></span><br>


  <span><span><a href="http://www.villagepowerdesign.com">www.villagepowerdesign.com</a></span><br>



















cell - <span style="display: inline; font-size: inherit; padding: 0px; 
color: rgb(80, 80, 80);" class="__postbox-detected-content 
__postbox-detected-phone" 
__postbox-detected-content="__postbox-detected-phone">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span></div>

<span><span style="display: inline; font-size: inherit; padding: 0px; 
color: rgb(80, 80, 80);" class="__postbox-detected-content 
__postbox-detected-phone" 
__postbox-detected-content="__postbox-detected-phone"></span></span></div>
</body>
</html>