    <p>I've seen all 3 options.   This question actually comes up in the
      wiring of sub panels, and out buildings as well.  I find
      improperly bonded wiring all the time that allows current to flow
      on the ground, because Neutral was bonded at both ends, with an
      EGC also run in parallel(option 2 done incorrectly).  This is a
      big No No, and can cause voltages on exposed metal.  Next, my
      understanding is that option 1 is no longer allowed on a single
      service, although that is how all grid connected houses are wired
      to the grid and each other with separate meters.  (sorry I'm out
      of the office, so I don't have a code reference)<br>
    </p>
    <p>As far as different opinions from different AHJs, I've had
      inspectors switch mid project, with the first inspector saying
      option 2 was ok, then the 2nd inspector required us to later run a
      GEC back to the GE after.   On option 3,  you would always want an
      EGC running with the conductors.  I have occasionally then not
      connected that EGC at one end, if we also had the separate GEC
      running back to the GE, to avoid a "lightning loop".  Having 2
      ground conductors running to the same point along different paths
      allows lightning to induce a current in the wiring through the
      loop that is created.  </p>
    <p>It really does get more complicated, when you also consider the
      grounding system's secondary purpose of providing lightning
      protection.   I have a great book from Polyphasor on grounding for
      lightning protection that is a whole nother world beyond NEC. 
      They had grounding systems with dozens of GEs (for communications
      towers) but everything was attached in a star pattern to avoid any
      lightning loops.  Its actually possible to meet both NEC and
      lightning protection requirements, but it takes more
      consideration, and hence the varied opinions.  Not having current
      running on the ground system however is a serious safety issue.<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 9/7/19 7:05 AM, Jason Szumlanski
      wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAE438R9mxVV2x-PEJM-=8xi_cKOZpP-1g7zKt2kto4CL4mtKkw@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="ltr">
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif">There doesn't
          seem to be a definitive and detailed consensus
          article/resource out there that addresses this topic. There
          are articles that dance around the subject, but little in
          terms of practical ways to accomplish grounding/binding with a
          supply side interconnection. AHJ's and engineers have all
          kinds of differing opinions. As an industry, it seems like we
          should have a definitive guide on the subject.</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif">Let's take a
          simple/common ungrounded inverter (or microinverter) system
          that is interconnected using supply side taps inside an
          existing load center with main disconnect. From the roof to
          the PV AC Combiner you have an appropriately sized EGC, and no
          GEC because a GEC is not required in this ungrounded system
          other than the existing premises GEC (and GE system). Let's
          assume the AHJ agrees that no GEC is required from the roof,
          which is a whole other subject that drive me nuts). Coming
          from the PV AC Combiner panel (if present) or Inverter you
          have two current carrying conductors L1 and L2 that are tapped
          on the service conductors. The neutral from the PV AC Combiner
          or inverter is landed on the existing neutral bus of the same
          main load center where the tap is made. </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif">Now what
          happens with the EGC that comes from the roof to the PV AC
          Combiner (or inverter)?</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif">What I have run
          into, and there may be other opinions, are the following
          assertions by AHJs:</div>
        <div class="gmail_default">
          <ul>
            <li><font face="arial, helvetica, sans-serif">Land the EGC
                on the PV AC Combiner and stop there. Bond neutral to
                ground. The neutral carries the fault current to the
                system bonding point in the main service panel.</font></li>
            <li><font face="arial, helvetica, sans-serif">Land the EGC
                in the PV AC Combiner and continue the EGC to the ground
                bar in the main service panel. Do not bond neutral to
                ground in the PC AC Combiner.</font></li>
            <li><font face="arial, helvetica, sans-serif">From the PV AC
                Combiner, install a GEC directly to the existing
                grounding electrode, and do not run an EGC to the main
                service panel.</font></li>
            <li><font face="arial, helvetica, sans-serif">Some
                combination of the above.</font></li>
          </ul>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif">Can anyone
          point to a clear and concise 3-line diagram that explains the
          acceptable options? Hopefully something that and AHJ will
          consider, like an IAEI article or NEC Handbook graphic.</div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif"><br>
        </div>
        <div class="gmail_default"
          style="font-family:arial,helvetica,sans-serif"><br>
        </div>
        <div>
          <div dir="ltr" class="gmail_signature"
            data-smartmail="gmail_signature">
            <div dir="ltr">
              <div>
                <div dir="ltr">
                  <div dir="ltr">
                    <div dir="ltr">
                      <div dir="ltr">
                        <div dir="ltr">
                          <div style="text-align:start"><font
                              face="arial, helvetica, sans-serif">J<span
                                class="gmail_default"
                                style="font-family:arial,helvetica,sans-serif">ason
                                Szumlanski</span></font></div>
                          <div style="text-align:start"><font
                              face="arial, helvetica, sans-serif"><span
                                class="gmail_default"
                                style="font-family:arial,helvetica,sans-serif">Florida
                                Solar Desing Group</span></font></div>
                        </div>
                      </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>