<div dir="auto">I have run into this many times and have never found a definitive answer.  The disconnect spec typically says that it must be protected with an ocpd at or less than the disco rating, but we are dealing with a current limited device (inverter) in this case so it would seem legal to me.</div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Wed, Aug 21, 2019, 5:22 PM Greg &lt;<a href="mailto:greg@remotepowerinc.com">greg@remotepowerinc.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
  

    
  
  <div text="#000099" bgcolor="#FFFFFF">
    Fellow Wrenches,  I&#39;m having a discussion with a utility engineer
    regarding the following situation:<br>
    <br>
    Installing a 6kW inverter that has a full rated output of 25 amps. 
    80% of 30 is 24.  That means to me I need to go up to a 40 amp
    breaker.  I&#39;m running #8 (continuous load 25 x 1.25 etc.)  <br>
    The engineer believes I should use a 60 amp disco since it&#39;s on a 40
    amp breaker.  My thinking is I can use a 30 amp disco since it can
    not produce more than 25 amps ever.  <br>
    <br>
    Do any of you have a reference that shows what I&#39;m doing is okay?
    Not okay?  <br>
    <br>
    Thanks again, <br>
    Greg Egan<br>
    Remote Power Inc.  <br>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>