<div dir="ltr">Given the DC voltage sag I have to wonder how a bank of lithium batteries would react as if I understand correctly they maintain the same voltage through out their entire range of SOC.<div><br></div><div>Christopher</div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Fri, Jul 26, 2019 at 1:19 PM Ray &lt;<a href="mailto:ray@solarray.com">ray@solarray.com</a>&gt; wrote:<br></div><blockquote class="gmail_quote" style="margin:0px 0px 0px 0.8ex;border-left:1px solid rgb(204,204,204);padding-left:1ex">
  
    
  
  <div bgcolor="#FFFFFF">
    <p>I&#39;ve run a 3 Hp pump on a pair of VFX 3648s, but then the 2nd
      issue was DC voltage sag from the batteries.  We had a string of
      Rolls 5000s that could not keep the voltage high enough below 70%
      SOC.  Be sure to have plenty of battery behind this system.  Also
      you might look into the soft start controllers,  I&#39;ve used some
      from Franklin that were a cheaper option than a bigger inverter.<br>
    </p>
    <pre class="gmail-m_-5310762092621794174moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="gmail-m_-5310762092621794174moz-cite-prefix">On 7/26/19 7:32 AM, Jeff Clearwater
      wrote:<br>
    </div>
    <blockquote type="cite">
      
      <span><span style="font-weight:bold">Thanks Ray and Jerry</span><span style="font-weight:bold">,</span><span style="font-weight:bold"><br>
        </span><span style="font-weight:bold"><br>
        </span><span style="font-weight:bold">Great to hear from you
          both with your years of combined experi</span><span style="font-weight:bold">ence :)</span><br>
        <br>
        <span style="font-weight:bold">So yes looking at the 5 sec has
          me switching back to a trusty Radian - <span style="text-decoration:underline">even then from what you
            are say</span></span><span style="text-decoration:underline"><span style="font-weight:bold">ing it may not
            work.</span></span><br>
        <br>
        And you are right Ray -  Outback is careful to rate the
        &quot;overload capability&quot; in KVA rather than KW due most likely to
        voltage sag of course.<br>
        <br>
        <span style="font-weight:bold">So this 53 LRA 2 HP motor - if
          I can only trust the 5 second (50 A) might not start -
          especially with other loads on the system?</span><br>
        <br>
        <span style="font-weight:bold">RAD</span><span style="font-weight:bold">IA</span><span style="font-weight:bold">N SURGE RATINGS:</span><br>
        <br>
        <span style="font-weight:bold">Maximum Output Current</span> <br>
        1 ms peak 100 Amps AC at 240 VAC, 200 Amps AC at 120 VAC<br>
        100 ms RMS 70.7 Amps AC at 240 VAC<br>
        <br>
        <span style="font-weight:bold">Overload Capability</span><br>
        100 ms surge 16.97 kVa<br>
        5 seconds 12 kVa<br>
        30 minute 9 kVa<br>
        <br>
        <span style="font-weight:bold">Other&#39;s </span><span style="font-weight:bold">experience with 2 HP sewage pump or
          well pump motors on a Radian?</span><span style="font-weight:bold"><br>
        </span><span style="font-weight:bold"><br>
        </span><span style="font-weight:bold">Thanks!</span><span style="font-weight:bold"><br>
        </span><span style="font-weight:bold"><br>
        </span><span style="font-weight:bold">Jeff</span><br>
        <br>
        <br>
        Ray wrote on 7/25/19 5:48 PM:</span><br>
      <br>
      <blockquote type="cite">
        
        <p>I only look at the 5 sec and 30 sec surge ratings to get an
          idea what an inverter can really do in the real world.  All
          those millisecond ratings/ in rush current specs won&#39;t get a
          pump or motor started, and will basically just get you into
          trouble.  The reason they have those ratings in amps and not
          watts, is that the voltage craters during that 100mS surge.<br>
        </p>
        <p>I can&#39;t tell you how many times we tried to start a pump,
          compressor, or large table saw, and the inverter just shut
          off, even though the &quot;in rush current&quot; was within the
          theoretical inverter capacity.  Actual Wrench list
          testimonials are much more valuable than those arcane specs.<br>
        </p>
        <pre class="gmail-m_-5310762092621794174moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
        <div class="gmail-m_-5310762092621794174moz-cite-prefix">On 7/25/19 5:15 PM, Jeff Clearwater
          wrote:<br>
        </div>
        <blockquote type="cite">
          
          <span><span style="font-weight:bold">Hey There Wrenches,</span><br>
            <br>
            So be advised that after a little research the SW dual stack
            will NOT double the surge ratings of a single SW.<br>
            <br>
            But that brings me to my second question:<br>
            <span style="font-weight:bold"><br>
            </span><span style="font-weight:bold">What inverter surge
              rating should one refer to when looking at maximum Inrush
              or LRA - 1ms?  100ms?  1 se</span><span style="font-weight:bold">c?</span><br>
            <br>
            <span style="font-weight:bold">Your</span><span style="font-weight:bold"> engineering wisdom welcomed!</span><br>
            <br>
            Thanks,<br>
            <br>
            Jeff<br>
            <br>
            <br>
            <br>
            Jeff Clearwater wrote on 7/23/19 8:27 PM:</span><br>
          <br>
          <blockquote type="cite">
            
            <span>Thanks for the tip!  I&#39;ll check the firmware.<br>
              <br>
              Dave Angelini Offgrid Solar wrote on 7/22/19 9:11 AM:</span><br>
            <br>
            <blockquote type="cite">
              
              <p>Hi Jeff,</p>
              <p> </p>
              <p>I am not going to guess if this will work, it should. 
                I use XW&#39;s because they start anything I have come
                across.</p>
              <p>If you do this, make sure but SW&#39;s have the latest and
                same firmware. There were problems with stacked SW&#39;s
                early on in their development.</p>
              <pre><strong><span>Dave Angelini Offgrid Solar
&quot;we go where powerlines don&#39;t&quot;
<a href="http://members.sti.net/offgridsolar/" target="_blank">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net" target="_blank">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
              <p>On Mon, 22 Jul 2019 07:26:07 -0700, Jeff Clearwater <a class="gmail-m_-5310762092621794174moz-txt-link-rfc2396E" href="mailto:jeffc@villagepowerdesign.com" target="_blank">&lt;jeffc@villagepowerdesign.com&gt;</a>
                wrote:</p>
              <blockquote type="cite" style="padding-left:5px;border-left:2px solid rgb(16,16,255);margin-left:5px;width:100%">
                Hey Esteemed Wrenches,<br>
                <br>
                So I recently built a power trailer with a single 4 KW
                (4048) Schneider SW for a client with a moderate cabin
                lifestyle.<br>
                <br>
                But he lives on a high hill and even though his 2 HP
                Macerator is only rated at 15 amps continuous that baby
                starts up with a whopping kick - probably close to or at
                it&#39;s 53 Amps Locked Rotor rating.<br>
                <br>
                <span style="font-weight:bold">The SW has the
                  following surge capability:</span><br>
                <br>
                <span><span style="font-weight:bold">SW 4048 Rated</span><span style="font-weight:bold"> @ 240 Volts:</span><br>
                  Continuous <span class="gmail-m_-5310762092621794174__postbox-detected-content gmail-m_-5310762092621794174__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">- <span class="gmail-m_-5310762092621794174__postbox-detected-content gmail-m_-5310762092621794174__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px"><span class="gmail-m_-5310762092621794174__postbox-detected-content gmail-m_-5310762092621794174__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">15</span>.2</span></span>
                  Amps 3700 Watts<br>
                  <span class="gmail-m_-5310762092621794174__postbox-detected-content gmail-m_-5310762092621794174__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px;color:rgb(0,0,0)">30
                    Minutes - 18.3</span> Amps 4400 Watts<br>
                  <span class="gmail-m_-5310762092621794174__postbox-detected-content gmail-m_-5310762092621794174__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">5 Secs</span> -
                  29.2 Amps 7000 Watts<br>
                  <span class="gmail-m_-5310762092621794174__postbox-detected-content gmail-m_-5310762092621794174__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">Max (100ms?) - 41</span>
                  Amps - 9840 Watts<br>
                  <br>
                  Can I be confidant that 2 stacked SWs will start this
                  baby?<br>
                  <br>
                  <span style="font-weight:bold">Any experience with
                    similar macerators - or simply educated guesses</span><span style="font-weight:bold">?</span><span style="font-weight:bold"><br>
                  </span><br>
                  Thanks!<br>
                  <br>
                  Jeff<br>
                  <br>
                </span></blockquote>
              <div>-- <br>
                <pre> </pre>
                <pre><strong><span style="font-size:small">Dave Angelini Offgrid Solar
&quot;we go where powerlines don&#39;t&quot;
<a href="http://members.sti.net/offgridsolar/" target="_blank">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net" target="_blank">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
              </div>
            </blockquote>
            <br>
            <br>
            <fieldset class="gmail-m_-5310762092621794174mimeAttachmentHeader"></fieldset>
            <br>
            <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
          </blockquote>
          <br>
          <br>
          <fieldset class="gmail-m_-5310762092621794174mimeAttachmentHeader"></fieldset>
          <pre class="gmail-m_-5310762092621794174moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
        </blockquote>
        <br>
        <fieldset class="gmail-m_-5310762092621794174mimeAttachmentHeader"></fieldset>
        <br>
        <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <br>
      <br>
      <fieldset class="gmail-m_-5310762092621794174mimeAttachmentHeader"></fieldset>
      <pre class="gmail-m_-5310762092621794174moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="gmail-m_-5310762092621794174moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="gmail-m_-5310762092621794174moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </div>

_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address &amp; settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules &amp; etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div><br clear="all"><div><br></div>-- <br><div dir="ltr" class="gmail_signature"><div dir="ltr"><div><div dir="ltr"><div dir="ltr"><div dir="ltr"><p style="text-align:center"><span style="font-size:10pt;color:rgb(31,73,125)"><font face="Arial, sans-serif">Chris Schaefer\u2019s<br></font></span><a href="http:www.solarandwindfx.com" style="font-size:12.8px" target="_blank"><img src="http://www.solarandwindfx.com/wp-content/uploads/2015/01/Solar-Wind-FX-Logo.png" width="200" height="40" style="color: rgb(31, 73, 125); font-family: Arial, sans-serif; font-size: 10pt;"></a><br><i><span style="font-family:Arial,sans-serif;color:rgb(31,73,125)"><span style="font-size:9pt">Tel/Fax
585-229-2083 or Cell 585-748-1870 </span><span style="font-size:12px"><br></span></span></i><i style="font-size:12.8px"><span style="font-size:10pt"><font color="#1f497d"><font face="Arial, sans-serif">5115
South Hill Road ~ Canandaigua New York 14424<br></font></font></span></i><i style="font-size:12.8px"><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><a href="http://www.solarandwindfx.com" target="_blank"><span style="color:blue">www.solarandwindfx.com</span></a> ~ E-mail: <span style="color:blue"><a href="mailto:chris@solarandwindfx.com" target="_blank">chris@solarandwindfx.com</a></span></span></i></p><p style="text-align:center"><i><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"><img src="http://solarandwindfx.com/wp-content/uploads/2015/01/certs.jpg" width="200" height="56"><br></span></i></p>

<p style="text-align:center"><span style="font-size:10pt;font-family:Arial,sans-serif;color:black">Thomas Jefferson,
the author of our great Constitution, once said, &quot;democracy&quot; will
cease to exist when you take away from those who are willing to work and give
to those who would not.&quot;</span><span style="font-size:10pt;font-family:Arial,sans-serif;color:rgb(31,73,125)"></span></p></div></div></div></div></div></div>