<div dir="auto">Hi about 20 years ago we used to build a soft start, it was a reduced voltage starter, composed of AC capacitors and a relay. Upon start from pressure switch the power would flow through capacitors? And shortly there after the relay would close after motor started to turn. It seems to me we also did it with large resistor ? My memory is not the best but others may have done same. I do not remember the type of motor. Also there us a hard start kit for a PSC motor. Modern soft starts are speed drives on 3 phase motors. <div dir="auto"><br></div><div dir="auto">If i remember correctly or at all, i will send more information. </div></div><br><div class="gmail_quote"><div dir="ltr" class="gmail_attr">On Fri, Jul 26, 2019, 9:03 AM Jeff Clearwater <<a href="mailto:jeffc@villagepowerdesign.com">jeffc@villagepowerdesign.com</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">
<div bgcolor="#FFFFFF" text="#000000"><span>Hey Wrenches,<br>
<br>
Anyone have success using soft-start modules on well and sewage pumps to
lower the surge for off-grid inverters?<br>
<br>
The baby we are trying to tame is a 2 HP 15 amp, 53 LRA Omnivore Grinder
Pump - LSG200 series - single phase 230 Vac.<br>
<br>
Thanks!<br>
<br>
Jeff<br>
<br>
</span><br>
<span><span>~~~~~~~~~~~<br>
</span>
</span>
<div class="m_7713523709702593197moz-signature">
<span>Jeff Clearwater</span><span><span><br>
</span>Village Power Design<br>
</span><span><span><span><a href="https://www.linkedin.com/in/jeff-clearwater-0622a312/" target="_blank" rel="noreferrer">linkedin</a>
</span></span></span><br>
<span><span><a href="http://www.villagepowerdesign.com" target="_blank" rel="noreferrer">www.villagepowerdesign.com</a></span><br>
cell - <span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)" class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-phone">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span></div>
<span><br>
Jeff Clearwater wrote on 7/26/19 6:32 AM:</span><br>
<br>
<blockquote type="cite">
<span><span style="font-weight:bold">Thanks Ray and Jerry</span><span style="font-weight:bold">,</span><span style="font-weight:bold"><br>
</span><span style="font-weight:bold"><br>
</span><span style="font-weight:bold">Great to hear from you both
with your years of combined experi</span><span style="font-weight:bold">ence :)</span><br>
<br>
<span style="font-weight:bold">So yes looking at the 5 sec has me
switching back to a trusty Radian - <span style="text-decoration:underline">even then from what you are say</span></span><span style="text-decoration:underline"><span style="font-weight:bold">ing
it may not work.</span></span><br>
<br>
And you are right Ray - Outback is careful to rate the "overload
capability" in KVA rather than KW due most likely to voltage sag of
course.<br>
<br>
<span style="font-weight:bold">So this 53 LRA 2 HP motor - if I can
only trust the 5 second (50 A) might not start - especially with other
loads on the system?</span><br>
<br>
<span style="font-weight:bold">RAD</span><span style="font-weight:bold">IA</span><span style="font-weight:bold">N SURGE RATINGS:</span><br>
<br>
<span style="font-weight:bold">Maximum Output Current</span> <br>
1 ms peak 100 Amps AC at 240 VAC, 200 Amps AC at 120 VAC<br>
100 ms RMS 70.7 Amps AC at 240 VAC<br>
<br>
<span style="font-weight:bold">Overload Capability</span><br>
100 ms surge 16.97 kVa<br>
5 seconds 12 kVa<br>
30 minute 9 kVa<br>
<br>
<span style="font-weight:bold">Other's </span><span style="font-weight:bold">experience with 2 HP sewage pump or well pump
motors on a Radian?</span><span style="font-weight:bold"><br>
</span><span style="font-weight:bold"><br>
</span><span style="font-weight:bold">Thanks!</span><span style="font-weight:bold"><br>
</span><span style="font-weight:bold"><br>
</span><span style="font-weight:bold">Jeff</span><br>
<br>
<br>
Ray wrote on 7/25/19 5:48 PM:</span><br>
<br>
<blockquote type="cite">
<p>I only look at the 5 sec and 30 sec surge ratings to get an idea
what an inverter can really do in the real world. All those
millisecond ratings/ in rush current specs won't get a pump or
motor started, and will basically just get you into trouble. The
reason they have those ratings in amps and not watts, is that the
voltage craters during that 100mS surge.<br>
</p>
<p>I can't tell you how many times we tried to start a pump,
compressor, or large table saw, and the inverter just shut off,
even though the "in rush current" was within the theoretical
inverter capacity. Actual Wrench list testimonials are much more
valuable than those arcane specs.<br>
</p>
<pre class="m_7713523709702593197moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
<div class="m_7713523709702593197moz-cite-prefix">On 7/25/19 5:15 PM, Jeff Clearwater
wrote:<br>
</div>
<blockquote type="cite">
<span><span style="font-weight:bold">Hey There Wrenches,</span><br>
<br>
So be advised that after a little research the SW dual stack
will NOT double the surge ratings of a single SW.<br>
<br>
But that brings me to my second question:<br>
<span style="font-weight:bold"><br>
</span><span style="font-weight:bold">What inverter surge
rating should one refer to when looking at maximum Inrush or
LRA - 1ms? 100ms? 1 se</span><span style="font-weight:bold">c?</span><br>
<br>
<span style="font-weight:bold">Your</span><span style="font-weight:bold"> engineering wisdom welcomed!</span><br>
<br>
Thanks,<br>
<br>
Jeff<br>
<br>
<br>
<br>
Jeff Clearwater wrote on 7/23/19 8:27 PM:</span><br>
<br>
<blockquote type="cite">
<span>Thanks for the tip! I'll check the firmware.<br>
<br>
Dave Angelini Offgrid Solar wrote on 7/22/19 9:11 AM:</span><br>
<br>
<blockquote type="cite">
<p>Hi Jeff,</p>
<p> </p>
<p>I am not going to guess if this will work, it should. I
use XW's because they start anything I have come across.</p>
<p>If you do this, make sure but SW's have the latest and same
firmware. There were problems with stacked SW's early on in
their development.</p>
<pre><strong><span>Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank" rel="noreferrer">http://members.sti.net/offgridsolar/</a>
e-mail <a href="mailto:offgridsolar@sti.net" target="_blank" rel="noreferrer">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
<p>On Mon, 22 Jul 2019 07:26:07 -0700, Jeff Clearwater <a class="m_7713523709702593197moz-txt-link-rfc2396E" href="mailto:jeffc@villagepowerdesign.com" target="_blank" rel="noreferrer"><jeffc@villagepowerdesign.com></a>
wrote:</p>
<blockquote type="cite" style="padding-left:5px;border-left:#1010ff 2px solid;margin-left:5px;width:100%">
Hey Esteemed Wrenches,<br>
<br>
So I recently built a power trailer with a single 4 KW
(4048) Schneider SW for a client with a moderate cabin
lifestyle.<br>
<br>
But he lives on a high hill and even though his 2 HP
Macerator is only rated at 15 amps continuous that baby
starts up with a whopping kick - probably close to or at
it's 53 Amps Locked Rotor rating.<br>
<br>
<span style="font-weight:bold">The SW has the following
surge capability:</span><br>
<br>
<span><span style="font-weight:bold">SW 4048 Rated</span><span style="font-weight:bold"> @ 240 Volts:</span><br>
Continuous <span class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">- <span class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px"><span class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">15</span>.2</span></span>
Amps 3700 Watts<br>
<span class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px;color:#000000">30
Minutes - 18.3</span> Amps 4400 Watts<br>
<span class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">5 Secs</span> - 29.2
Amps 7000 Watts<br>
<span class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-date" style="display:inline;font-size:inherit;padding:0px">Max (100ms?) - 41</span>
Amps - 9840 Watts<br>
<br>
Can I be confidant that 2 stacked SWs will start this
baby?<br>
<br>
<span style="font-weight:bold">Any experience with
similar macerators - or simply educated guesses</span><span style="font-weight:bold">?</span><span style="font-weight:bold"><br>
</span><br>
Thanks!<br>
<br>
Jeff<br>
<br>
</span></blockquote>
<div>-- <br>
<pre> </pre>
<pre><strong><span style="font-size:small">Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank" rel="noreferrer">http://members.sti.net/offgridsolar/</a>
e-mail <a href="mailto:offgridsolar@sti.net" target="_blank" rel="noreferrer">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
</div></blockquote>
<br>
<br>
<fieldset class="m_7713523709702593197mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="m_7713523709702593197moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="m_7713523709702593197moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="m_7713523709702593197moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">www.members.re-wrenches.org</a>
</pre></blockquote>
<br>
<br>
<fieldset class="m_7713523709702593197mimeAttachmentHeader"></fieldset>
<pre class="m_7713523709702593197moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="m_7713523709702593197moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="m_7713523709702593197moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="m_7713523709702593197moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">www.members.re-wrenches.org</a>
</pre></blockquote>
<br>
<fieldset class="m_7713523709702593197mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="m_7713523709702593197moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="m_7713523709702593197moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="m_7713523709702593197moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">www.members.re-wrenches.org</a>
</pre></blockquote>
<br>
<br>
<fieldset class="m_7713523709702593197mimeAttachmentHeader"></fieldset>
<br>
<pre>_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="m_7713523709702593197moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="m_7713523709702593197moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" rel="noreferrer">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="m_7713523709702593197moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" rel="noreferrer">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank" rel="noreferrer">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="m_7713523709702593197moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank" rel="noreferrer">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
<br>
<div class="m_7713523709702593197moz-signature">-- <br><span>~~~~~~~~~~~<br>
</span>
<div class="m_7713523709702593197moz-signature">
<span>Jeff Clearwater</span><span><span><br>
</span>Village Power Design<br>
</span><span><span><span><a href="https://www.linkedin.com/in/jeff-clearwater-0622a312/" target="_blank" rel="noreferrer">linkedin</a>
</span></span></span><br>
<span><span><a href="http://www.villagepowerdesign.com" target="_blank" rel="noreferrer">www.villagepowerdesign.com</a></span><br>
cell - <span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)" class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-phone">413-559-9763<br>
~~~~~~~~~~~~~~~~~~~~~~~</span></span></div>
<span><span style="display:inline;font-size:inherit;padding:0px;color:rgb(80,80,80)" class="m_7713523709702593197__postbox-detected-content m_7713523709702593197__postbox-detected-phone"></span></span></div>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>