<p>Good point Jeff, HOA could all of a sudden be a commercial demand
account. I think you have to wait for PSEG to tell you what they
allow. Every situation seems unique, so it is difficult to say
what is typical. They may be served by multiple service points.
PSEG has that information. I think it will save you a lot of
running around if you get into a discussion with the Customer
Service of Distribution Engineering sides of the company. If it
is served by one xfmr than the meter solution would be to meter
onthe secondary side. But again, Jeff brings up a good point.
PSEG should be able to combine all 200 accounts into a single
account for analysis. They can tell you if demand charges would
apply to the master account, and if by increased kWh billed in the
aggregate, if that would push you into a lower kWh tariff rate.
Chris<br>
</p>
<div class="moz-cite-prefix">On 7/5/2019 1:52 PM, Andrew Truitt
wrote:<br>
</div>
<blockquote type="cite"
cite="mid:CAKTVxmsm87ZLAB-wRLXrNfuijOiBWqs4hAQ+1TdV2sEuMqSh-w@mail.gmail.com">
<meta http-equiv="content-type" content="text/html; charset=UTF-8">
<div dir="ltr">
<div dir="ltr"><br>
</div>
<div>Thanks fellas. Todd, these meters are already on a single
account but NJ's remote net metering law only covers public
entities \U0001f620.</div>
<div><br>
</div>
<div>Chris, all meters are owned by the same entity (the HOA).
We have a call into the utility (PSE&G). We do not have
experience in this area so any advice you may have on how to
be successful in this endeavour based on your time on the
other side of the curtain would be appreciated. Would an
entity like this (a community with ~200 homes) typically be
served by a single transformer or multiple? If a single then
the simplest / most attainable solution would be to re-route
the 15 meter circuits to a pad-mounted panelboard / main meter
on the secondary side of the transformer, right?</div>
<div dir="ltr"><br clear="all">
<div>
<div dir="ltr" class="m_-8116403664689143884gmail_signature"
data-smartmail="gmail_signature">
<div dir="ltr">
<div>
<div dir="ltr">
<div><br>
</div>
<div>
<div dir="ltr"><span
style="font-size:10pt;font-family:ArialMT,serif,EmojiFont;color:rgb(64,64,64)">Regards, </span><br>
</div>
<div dir="ltr"><span
style="font-size:10pt;font-family:ArialMT,serif,EmojiFont;color:rgb(64,64,64)"><br>
</span></div>
<div dir="ltr"><br>
</div>
<table
style="border-spacing:0px;border-collapse:collapse;color:rgb(68,68,68);width:400px;font-size:9pt;font-family:Arial,sans-serif;line-height:normal"
cellspacing="0" cellpadding="0">
<tbody>
<tr>
<td style="padding:0px 0px
6px;font-size:12pt;color:rgb(23,147,206);width:259px"><font
face="Tahoma, sans-serif">Andrew Truitt</font><span
style="font-family:Arial,sans-serif">
<table
style="color:rgb(68,68,68);font-size:9pt;border-spacing:0px;border-collapse:collapse;width:400px;line-height:normal"
cellspacing="0" cellpadding="0">
<tbody>
<tr>
<td colspan="2"
style="font-family:Arial,sans-serif;padding:0px;font-size:10pt;color:rgb(44,44,44);width:400px"
width="400">
<div
style="color:rgb(136,136,136);font-family:arial,sans-serif;font-size:12.8px"><span
style="color:rgb(68,68,68)"><span
style="font-family:verdana,sans-serif"><a class="moz-txt-link-abbreviated" href="http://www.dr.ventures">www.dr.ventures</a></span></span></div>
<span
style="font-family:arial,sans-serif;font-size:12.8px;color:rgb(68,68,68)"><span
style="font-family:verdana,sans-serif">d: 202.486.7507</span></span><span
style="font-family:Tahoma,sans-serif"><br>
</span></td>
</tr>
<tr>
<td colspan="2"
style="font-family:Arial,sans-serif;padding:0px;font-size:10pt;color:rgb(44,44,44);width:400px"
width="400">
<div
style="color:rgb(0,0,0);font-family:Calibri,Helvetica,sans-serif,Helvetica,EmojiFont,"Apple
Color Emoji","Segoe
UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple Color
Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple Color
Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple Color
Emoji","Segoe UI
Emoji",NotoColorEmoji;font-size:16px;margin:0px"><br>
</div>
<div
style="color:rgb(0,0,0);font-family:Calibri,Helvetica,sans-serif,Helvetica,EmojiFont,"Apple
Color Emoji","Segoe
UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple Color
Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple Color
Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple Color
Emoji","Segoe UI
Emoji",NotoColorEmoji;font-size:16px;margin:0px">
<div style="margin:0px"><span
style="color:rgb(153,153,153);font-family:Arial,sans-serif,serif,EmojiFont;font-size:10pt">NABCEP Certified
PV Installation
Professional ID: 032407-66</span><br>
</div>
<div style="margin:0px">
<div style="margin:0px">
<div style="margin:0px"><font
size="1"
face="Arial,sans-serif,serif,EmojiFont"
color="#500050"><span
style="font-size:12.78px"><font size="2"
face="Arial,sans-serif,serif,EmojiFont"
color="#999999"><span
style="font-size:10pt">Colorado Journeyman Electrician License No.:
600132</span></font></span></font></div>
<div style="margin:0px"><font
size="1"
face="Arial,sans-serif,serif,EmojiFont"
color="#500050"><span
style="font-size:12.78px"><font size="2"
face="Arial,sans-serif,serif,EmojiFont"
color="#999999"><span
style="font-size:10pt"><br>
</span></font></span></font></div>
</div>
</div>
</div>
</td>
</tr>
</tbody>
</table>
</span></td>
<td style="padding:0px 0px
6px;width:141px;text-align:right"><img
alt="Logo"
src="https://s8.postimg.cc/vbfqwedet/DRV_-_1920.png"
class="m_-8116403664689143884gmail-CToWUd"
style="border:0px;vertical-align:middle"
moz-do-not-send="true" width="200"
height="83" border="0"></td>
</tr>
<tr>
<td colspan="2"
style="padding:0px;width:400px;border-top:1px
solid rgb(23,147,206)" width="400"> <br>
</td>
</tr>
<tr>
<td colspan="2"
style="padding:0px;font-size:10pt;width:400px"
width="400">
<div
style="color:rgb(0,0,0);font-family:Calibri,Helvetica,sans-serif,Helvetica,EmojiFont,"Apple
Color Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple
Color Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple
Color Emoji","Segoe UI
Emoji",NotoColorEmoji,"Segoe
UI Symbol","Android
Emoji",EmojiSymbols,Helvetica,EmojiFont,"Apple
Color Emoji","Segoe UI
Emoji",NotoColorEmoji;font-size:16px;margin:0px"><br>
</div>
</td>
</tr>
<tr>
<td colspan="2"
style="padding:0px;width:400px"
width="400"><br>
</td>
</tr>
<tr>
<td colspan="2"
style="font-family:Arial,sans-serif;padding:0px;font-size:8pt;width:400px;text-align:justify"
width="400"><span
style="font-family:Tahoma,sans-serif"><font
color="#999999">The content of this
email is confidential and intended for
the recipient specified in message
only. It is strictly forbidden to
share any part of this message with
any third party, without a written
consent of the sender. If you received
this message by mistake, please reply
to this message and follow with its
deletion, so that we can ensure such a
mistake does not occur in the future.</font></span></td>
</tr>
</tbody>
</table>
<div><br style="color:rgb(80,0,80)">
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
</div>
<br>
<div class="gmail_quote">
<div dir="ltr" class="gmail_attr">On Fri, Jul 5, 2019 at 5:57
AM Christopher Warfel <<a
href="mailto:cwarfel@entech-engineering.com"
target="_blank" moz-do-not-send="true">cwarfel@entech-engineering.com</a>>
wrote:<br>
</div>
<blockquote class="gmail_quote" style="margin:0px 0px 0px
0.8ex;border-left:1px solid
rgb(204,204,204);padding-left:1ex">
<div bgcolor="#FFFFFF">
<p>I used to work for a utility and it is utility
dependent. The key I think is whether all the
submetering customers are actually owned by the same
entity. For example, a commercial complex may have
several building on site, each submetered. The whole
complex could be master metered at the service delivery
point. If so, master metering will save in several
ways, most notably the monthly charge, but demand
charges and possibly a reduction in the energy charge
depending upon the tariff can also occur. The utility
should be able to run the analysis for you. I would
request from the utility the details on master metering
at the location. This will quickly get you into their
domain/processes. Unless you have experience in this
area, it can be difficult to calculate the
cost/benefit. Chris</p>
<p><br>
</p>
<div
class="m_-8116403664689143884gmail-m_-2417942070706252053moz-cite-prefix">On
7/4/2019 2:09 PM, Andrew Truitt wrote:<br>
</div>
<blockquote type="cite">
<div dir="ltr">
<div><br>
</div>
<div>Happy 4th Wrenches! Has anyone ever been through
the process of consolidating utility electric meters
for a client? We're talking to an HOA that has 15
meters throughout the community for common area
loads (clubhouse, pool pump, lighting, fountain...)
so they're paying a fixed monthly charge on each in
addition to energy and demand charges.
Consolidating to a single master meter (possibly
with sub-metering) would likely lower their costs on
its own, and (more importantly?) would improve the
value proposition for a PV+ESS installation. We're
not sure if the community is served by a single or
multiple transformers yet, but if it is just one
then the process should be straightforward from a
technical standpoint. The interwebs tell me that
some providers (seems like mostly co-ops) are open
to this, but I can't find anything for this
particular utility. </div>
<br clear="all">
<div>
<div dir="ltr"
class="m_-8116403664689143884gmail-m_-2417942070706252053gmail_signature">
<div dir="ltr">
<div>
<div dir="ltr">
<div><br>
</div>
<div>
<div dir="ltr"><span
style="font-size:10pt;font-family:ArialMT,serif,EmojiFont;color:rgb(64,64,64)">Regards, </span><br>
</div>
<div dir="ltr"><span
style="font-size:10pt;font-family:ArialMT,serif,EmojiFont;color:rgb(64,64,64)"><br>
</span></div>
<div dir="ltr"><br>
</div>
<table
style="border-spacing:0px;border-collapse:collapse;color:rgb(68,68,68);width:400px;font-size:9pt;font-family:Arial,sans-serif;line-height:normal"
cellspacing="0" cellpadding="0">
<tbody>
<tr>
<td style="padding:0px 0px
6px;font-size:12pt;color:rgb(23,147,206);width:259px"><font
face="Tahoma, sans-serif">Andrew
Truitt</font><span
style="font-family:Arial,sans-serif">
<table
style="color:rgb(68,68,68);font-size:9pt;border-spacing:0px;border-collapse:collapse;width:400px;line-height:normal"
cellspacing="0"
cellpadding="0">
<tbody>
<tr>
<td colspan="2"
style="font-family:Arial,sans-serif;padding:0px;font-size:10pt;color:rgb(44,44,44);width:400px"
width="400">
<div
style="color:rgb(136,136,136);font-family:arial,sans-serif;font-size:12.8px"><span
style="color:rgb(68,68,68)"><span style="font-family:verdana,sans-serif"><a
class="m_-8116403664689143884gmail-m_-2417942070706252053moz-txt-link-abbreviated"
href="http://www.dr.ventures" target="_blank" moz-do-not-send="true">www.dr.ventures</a></span></span></div>
<span
style="font-family:arial,sans-serif;font-size:12.8px;color:rgb(68,68,68)"><span
style="font-family:verdana,sans-serif">d: 202.486.7507</span></span><span
style="font-family:Tahoma,sans-serif"><br>
</span></td>
</tr>
<tr>
<td colspan="2"
style="font-family:Arial,sans-serif;padding:0px;font-size:10pt;color:rgb(44,44,44);width:400px"
width="400">
<div><br>
</div>
<div>
<div
style="margin:0px"><span
style="color:rgb(153,153,153);font-family:Arial,sans-serif,serif,EmojiFont;font-size:10pt">NABCEP Certified
PV Installation
Professional ID:
032407-66</span><br>
</div>
<div
style="margin:0px">
<div
style="margin:0px">
<div
style="margin:0px"><font
size="1"
face="Arial,sans-serif,serif,EmojiFont"
color="#500050"><span style="font-size:12.78px"><font size="2"
face="Arial,sans-serif,serif,EmojiFont"
color="#999999"><span style="font-size:10pt">Colorado Journeyman
Electrician
License No.:
600132</span></font></span></font></div>
<div
style="margin:0px"><font
size="1"
face="Arial,sans-serif,serif,EmojiFont"
color="#500050"><span style="font-size:12.78px"><font size="2"
face="Arial,sans-serif,serif,EmojiFont"
color="#999999"><span style="font-size:10pt"><br>
</span></font></span></font></div>
</div>
</div>
</div>
</td>
</tr>
</tbody>
</table>
</span></td>
<td style="padding:0px 0px
6px;width:141px;text-align:right"><img
alt="Logo"
src="https://s8.postimg.cc/vbfqwedet/DRV_-_1920.png"
class="m_-8116403664689143884gmail-m_-2417942070706252053gmail-CToWUd"
style="border:0px;vertical-align:middle"
moz-do-not-send="true"
width="200" height="83"
border="0"></td>
</tr>
<tr>
<td colspan="2"
style="padding:0px;width:400px;border-top:1px
solid rgb(23,147,206)" width="400"> <br>
</td>
</tr>
<tr>
<td colspan="2"
style="padding:0px;font-size:10pt;width:400px"
width="400">
<div><br>
</div>
</td>
</tr>
<tr>
<td colspan="2"
style="padding:0px;width:400px"
width="400"><br>
</td>
</tr>
<tr>
<td colspan="2"
style="font-family:Arial,sans-serif;padding:0px;font-size:8pt;width:400px;text-align:justify"
width="400"><span
style="font-family:Tahoma,sans-serif"><font
color="#999999">The content of
this email is confidential and
intended for the recipient
specified in message only. It
is strictly forbidden to share
any part of this message with
any third party, without a
written consent of the sender.
If you received this message
by mistake, please reply to
this message and follow with
its deletion, so that we can
ensure such a mistake does not
occur in the future.</font></span></td>
</tr>
</tbody>
</table>
<div><br style="color:rgb(80,0,80)">
</div>
</div>
</div>
</div>
</div>
</div>
</div>
</div>
<br>
<fieldset
class="m_-8116403664689143884gmail-m_-2417942070706252053mimeAttachmentHeader"></fieldset>
<pre class="m_-8116403664689143884gmail-m_-2417942070706252053moz-quote-pre">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="m_-8116403664689143884gmail-m_-2417942070706252053moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="m_-8116403664689143884gmail-m_-2417942070706252053moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" target="_blank" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="m_-8116403664689143884gmail-m_-2417942070706252053moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" target="_blank" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="m_-8116403664689143884gmail-m_-2417942070706252053moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" target="_blank" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="m_-8116403664689143884gmail-m_-2417942070706252053moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" target="_blank" moz-do-not-send="true">www.members.re-wrenches.org</a>
</pre>
</blockquote>
</div>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a
href="mailto:RE-wrenches@lists.re-wrenches.org"
target="_blank" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
rel="noreferrer" target="_blank" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
rel="noreferrer" target="_blank" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm"
rel="noreferrer" target="_blank" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org"
rel="noreferrer" target="_blank" moz-do-not-send="true">www.members.re-wrenches.org</a><br>
<br>
</blockquote>
</div>
</div>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
</body>
</html>