<html>
  <head>
    <meta http-equiv="Content-Type" content="text/html; charset=UTF-8">
  </head>
  <body text="#000000" bgcolor="#FFFFFF">
    <p>I've had problems with several manufacturers' onboard relays, and
      12 v outputs.  For instance I now always use a 2nd relay
      controlled by the onboard relay, even for little things like
      Zephyr Power Vents.  If you look at the new relays compared to say
      the old Trace SW relays, they're just not near the same.</p>
    <p>That's concerning that over current would fry the whole Radian
      control board.   On Midnite Classics, if you exceeded the 200mA
      12v output, it just shut the output off.<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 12/14/18 6:58 AM,
      <a class="moz-txt-link-abbreviated" href="mailto:dan@foxfire-energy.com">dan@foxfire-energy.com</a> wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:20181214065843.720a661d8db719b1f2ad39509c9edaa3.90de070e16.wbe@email04.godaddy.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <span style="font-family:Verdana; color:#000000; font-size:10pt;">
        <div>OBTW. the FNDC is a dry contact.</div>
        <div><br>
        </div>
        <div>db<br>
        </div>
        <div><br>
        </div>
        <div><br>
          Dan Brown<br>
          Foxfire Energy Corp.<br>
          Renewable Energy Systems<br>
          (802)-483-2564<br>
          <a href="http://www.Foxfire-Energy.com" moz-do-not-send="true">www.Foxfire-Energy.com</a><br>
          NABCEP #092907-44</div>
        <div><br>
          <br>
        </div>
        <blockquote id="replyBlockquote" webmail="1" style="border-left:
          2px solid blue; margin-left: 8px; padding-left: 8px;
          font-size:10pt; color:black; font-family:verdana;">
          <div id="wmQuoteWrapper">
            -------- Original Message --------<br>
            Subject: [RE-wrenches] Interesting gen start problem<br>
            From: William Miller &lt;<a
              href="mailto:william@millersolar.com"
              moz-do-not-send="true">william@millersolar.com</a>&gt;<br>
            Date: Thu, December 13, 2018 3:11 pm<br>
            To: RE-wrenches &lt;<a
              href="mailto:re-wrenches@lists.re-wrenches.org"
              moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
            <br>
            <style>
 #wmQuoteWrapper /* Font Definitions */ @font-face  {font-family:Calibri; panose-1:2 15 5 2 2 2 4 3 2 4;}
 #wmQuoteWrapper @font-face  {font-family:Tahoma; panose-1:2 11 6 4 3 5 4 4 2 4;}
 #wmQuoteWrapper /* Style Definitions */ p.MsoNormal, #wmQuoteWrapper li.MsoNormal, #wmQuoteWrapper div.MsoNormal  {margin:0in; margin-bottom:.0001pt; font-size:11.0pt; font-family:"Calibri","sans-serif";}
 #wmQuoteWrapper a:link, #wmQuoteWrapper span.MsoHyperlink  {mso-style-priority:99; color:blue; text-decoration:underline;}
 #wmQuoteWrapper a:visited, #wmQuoteWrapper span.MsoHyperlinkFollowed  {mso-style-priority:99; color:purple; text-decoration:underline;}
 #wmQuoteWrapper p.MsoAcetate, #wmQuoteWrapper li.MsoAcetate, #wmQuoteWrapper div.MsoAcetate  {mso-style-priority:99; mso-style-link:"Balloon Text Char"; margin:0in; margin-bottom:.0001pt; font-size:8.0pt; font-family:"Tahoma","sans-serif";}
 #wmQuoteWrapper span.EmailStyle17  {mso-style-type:personal-compose; font-family:"Arial","sans-serif"; color:windowtext;}
 #wmQuoteWrapper span.BalloonTextChar  {mso-style-name:"Balloon Text Char"; mso-style-priority:99; mso-style-link:"Balloon Text"; font-family:"Tahoma","sans-serif";}
 #wmQuoteWrapper .MsoChpDefault  {mso-style-type:export-only; font-family:"Calibri","sans-serif";}
 #wmQuoteWrapper @page WordSection1  {size:8.5in 11.0in; margin:1.0in 1.0in 1.0in 1.0in;}
 #wmQuoteWrapper div.WordSection1  {page:WordSection1;}

</style>
            <div class="WordSection1">
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">Friends:</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">While
                  I\u2019d like to think I have seen everything, I came
                  across this scenario recently that surprised me:  </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">We
                  replace an existing FX system that had a generator
                  component.  Since the </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">FX
                  inverter can only provide 12 volts for generator
                  start, and we did not see a relay in the power room,
                  we assumed there was a 12 volt coil relay in the
                  generator room.  Turns out this was not the case.</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">Generators
                  use the cranking battery voltage (B+) to power control
                  circuits.  The B+ to start control relays is completed
                  by a contact closure.  In this case, there was no
                  relay.  Instead the original installer use the 12
                  volts from the FX inverters to provide substitute B+
                  to the generator control circuitry.  </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">The
                  end result is we burned up the Radian control board. 
                  Apparently the FX inverter had enough 12 volt
                  capability to make this work, but the Radians did not.</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">When
                  we began troubleshooting, our first clue something was
                  wrong was that there was no relay.  Our second clue
                  was that one of the12 volt start leads was grounded. 
                  We also burned up a relay in the generator.</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">I
                  hope this little cautionary tale helps one of you
                  avoid a burned up control board someday, somewhere. 
                  This problem was a big headache.</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">William</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">PS: 
                  Here is a <a target="_blank"
href="http://www.millersolar.com/MillerSolar/Portfolio/Inverters/battery_iinverters/TT-Radian/TT_Radian.html"
                    moz-do-not-send="true">web page</a> on this
                  particular installation.  On this project we
                  incorporated some of the GSLC wiring innovations
                  discussed in this forum.</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;">Wm</span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:12.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;"> </span></div>
              <div class="MsoNormal" style="font-size:12pt;"><span
style="font-size:10.0pt;font-family:&quot;Arial&quot;,&quot;sans-serif&quot;;color:black"><img
                    id="Picture_x0020_1"
                    src="cid:part5.CE598713.04AA9D04@solarray.com"
                    alt="Gradient Cap_mini"
                    wbeuser="dan@foxfire-energy.com" class="" width="80"
                    height="35" border="0"><br>
                  Lic 773985<br>
                  <a target="_blank" href="http://www.millersolar.com/"
                    moz-do-not-send="true">millersolar.com</a><br>
                  805-438-5600</span></div>
              <div class="MsoNormal" style="font-size:12pt;"> </div>
            </div>
            <hr>_______________________________________________<br>
            List sponsored by Redwood Alliance<br>
            <br>
            List Address: <a
              href="mailto:RE-wrenches@lists.re-wrenches.org"
              moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
            <br>
            Change listserver email address &amp; settings:<br>
            <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
              moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
            <br>
            List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
              moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
            <br>
            List rules &amp; etiquette:<br>
            <a href="http://www.re-wrenches.org/etiquette.htm"
              moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
            <br>
            Check out or update participant bios:<br>
            <a href="http://www.members.re-wrenches.org"
              moz-do-not-send="true">www.members.re-wrenches.org</a><br>
            <br>
          </div>
        </blockquote>
      </span>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>