<div dir="ltr"><div>Allan S. sent follow up queries after my response to Drake&#39;s dilemma. Allan&#39;s queries are pasted below.</div><div><br></div><div>Mick here: Sorry I didn&#39;t state my suggestion more clearly but, yes, in this situation the only way to know if the battery is worth trying to salvage is to pump it up nicely with a bunch of energy (meeting the battery mfr&#39;s &quot;full charge parameters&quot; or as close as possible)...shut off the generator &amp; shut off the solar array...set the Tri-Metric (or other shunt based monitor) to measure &quot;amp hours from full&quot; &amp; make sure the counter is starting at 0.00 amp hours from full...then impose loads on the battery bank &amp; let it all run until the inverter shuts off due to low battery voltage. (The loads don&#39;t have to impose a steady &quot;20 hour discharge rate&quot; &amp; we&#39;re not trying for laboratory accuracy. To give the battery a fair chance at proving its mettle, be sure the discharge rate is equitably chosen for the battery type &amp; temperature, etc. To be &quot;equitable&quot;, the servicing technician should run the test in a way that doesn&#39;t ask the battery to perform miraculously...just to perform within its design parameters.) </div><div><br></div><div>Allan correctly states that 1.75 volts per cell is the &quot;industry standard&quot; discharge cut off point for lead acid batteries (@ 25 degrees C) so if the system is 48v nominal, that&#39;s 24 cells X 1.75 = 42.0 volts as the setpoint for the inverter&#39;s LBCO &quot;low battery cutoff function&quot;. The amp-hour monitor will display the number of amp-hours that the battery was able to deliver before the inverter crashed on voltage &amp; that value can be compared to the original rated capacity. So...although I must have muddled my explanation, Allan, the Tri-Metric type monitors can indeed measure &amp; display the battery&#39;s amp-hour capacity. One must eliminate solar recharge during the test &amp; any other variables such as generator run time...then there&#39;s only a battery, an inverter, some loads, and the amp-hour counting gizmo. </div><div><br></div><div>&gt;&gt;An unhealthy battery will reach the failure point in a fairly short amount of time &amp; for a fairly small amount of labor.&lt;&lt; A semi-healthy battery is a greater challenge because it takes longer to wring them out &amp; the service tech may opt to educate the client on how to complete the &quot;pump &amp; dump&quot; measurement after the tech leaves the site. If the client can be persuaded to install a shunt &amp; an amp-hour meter, they&#39;ll also have better instrumentation in place to help them &amp; their service technician down the road. Some clients will want to try an EQ charge or other measures &amp; the ah counter will be able to display any improvements that result from those efforts...or the lack of improvements. </div><div><br></div><div>As my Dutch solar buddy would say, &quot;Meten is Weten&quot;: &quot;Measuring is Knowing.&quot; A battery based energy system owner who only has a DC voltmeter is like a car owner whose only instrument is a tire pressure gauge. Definitely some clients balk at the expense &amp; new learning required to retrofit a proper ah monitor, but better instrumentation may prove a good value to them in the long run.</div><div><br></div><div>The Wrench List is the Bomb! Mick Abraham </div><div><br></div>---------- Forwarded message ----------<br>From: Sindelar Solar &lt;<a href="mailto:Allan@sindelarsolar.com" target="_blank">Allan@sindelarsolar.com</a>&gt;<br>To: <a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank">re-wrenches@lists.re-wrenches.org</a><br>Cc: <br>Bcc: <br>Date: Wed, 21 Nov 2018 11:40:55 -0700<br>Subject: Re: [RE-wrenches] Batt Cap AGM<br><div bgcolor="#FFFFFF"><p>Mick, <br></p><p>While I fully agree on the importance of a monitor such as the TriMetric, I&#39;m confused by some of what you&#39;ve written below. A TriMet (or any similar monitor for LA) can measure amp-hours removed and replaced, but it can&#39;t measure &amp; display the battery bank&#39;s amp-hour capacity. Only taking the time to drain the bank at a measured rate will do that, and I have yet to have a customer want to pay me to do a battery capacity test down to 1.75 vpc at the 20-hour rate - or any rate for that matter. The TriMet is set up such that the installer tells the TriMet the battery capacity. In a case such as this, what number would you program into the TM as the amp-hour capacity? How would you determine this value?</p><p>Thanks, Allan<br></p><div class="gmail-m_1755573528693512476moz-signature">-- <br><div class="gmail-m_1755573528693512476WordSection1"><p class="MsoNormal" style="line-height:normal"><b>Allan Sindelar</b><br><a href="mailto:allan@sindelarsolar.com" target="_blank">allan@sindelarsolar.com</a><br>NABCEP Certified PV Installation Professional<br>New Mexico EE98J Journeyman Electrician<br>Founder (Retired), Positive Energy, Inc<span class="gmail-m_1755573528693512476GramE">.</span><br><b>505 780-2738 cell</b></p></div></div></div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br><br>Landline: 970-731-4675</div><div>Cell phone or for text messaging: 970-946-6584</div></div></div></div></div><div hspace="streak-pt-mark" style="max-height:1px"><img alt="" style="width:0px;max-height:0px;overflow:hidden" src="https://mailfoogae.appspot.com/t?sender=abWlja0BhYnJhaGFtc29sYXIuY29t&amp;type=zerocontent&amp;guid=5df9f78a-78ee-4840-ba15-e12d9faa6853"><font color="#ffffff" size="1">\u1427</font></div>