    <p>Regardless of the Amazing Batcap 30 yr claims debunked by Dan,  a
      system wired in the manner described (5 batteries in parallel,
      then series connecting the sets of 5 for 48 v) is just not going
      to charge and discharge evenly.  Its violated the no more than 4
      parallel strings rule, so I'm surprised it lasted even 5 years. 
      My guess is that some of the batteries are toast and some may have
      a bit of life in them, since they were so grossly imbalanced, so a
      neighbor might be able to use a few of the best ones for a couple
      more years. Ultimately the rule in off grid solar is "Batteries
      are the Weakest Link".  The customer is not going to have a decent
      experience until they replace that mess with a properly sized and
      wired battery bank from a reputable manufacturer.</p>
    <p>I won't take on new clients if we can't get the system up to
      snuff.  I don't need those oh so predictable calls that the power
      is off again.  <br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 11/21/18 1:06 AM, Dan Fink wrote:<br>
    </div>
    <blockquote type="cite"
cite="mid:CAF+3LncHW=2N8GdtHcNam2GUnVOE0Rab72uJvgrwR90qWrLdag@mail.gmail.com">
      <meta http-equiv="content-type" content="text/html; charset=UTF-8">
      <div dir="auto">
        <div>Hello All; I would question the client about the origin of
          this battery bank. New, used, how long in storage and in
          service, etc. If he bought these new, that's a very expensive
          battery bank!</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">Usually when I've run into banks of massively
          parallel, low amp-hour sealed lead acid batteries, the origin
          was "a great surplus deal on a whole bunch of batteries from
          wheelchairs/UPS units/manufacturer overrun etc."</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">My BS meter on the manufacturer Batcap was
          triggered by a few things....</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">-The company is focused on selling audiophiles
          xxxscratch thatxxx punks with car stereos so loud they set off
          car alarms 6 spots down. They need lots of amps right now to
          thump that bass.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">- The company name Batcap targets the capacitor
          boost market for this application, but actually a dedicated
          battery is a great idea, as it would recharge quickly from the
          (often up-sized) car alternator. But some folks seem to think
          the name implies there's a capacitor involved. There isn't.
          Sneaky language in the company name.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">-  Sealed, low internal resistance, 100-125
          amp-hours. Sounds like a stock AGM to me, compared to a VRSLA.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">- Spec sheet contains grammatical errors that
          indicate the writer does not speak English as a first
          language.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">- "Solar" seems to have been added to the
          website and battery label stickers as an afterthought....and
          30 years cycle life in a solar application? Has Batcap been
          around for 30 years? Sounds like somebody importing Asian AGMs
          and sticking them with new stickers.</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto">DAN FINK</div>
        <div dir="auto">Buckville Energy Consulting, Box Prairie CO
          970-672-4342</div>
        <div dir="auto"><br>
        </div>
        <div dir="auto"><br>
          <br>
          <div class="gmail_quote" dir="auto">
            <div dir="ltr">On Tue, Nov 20, 2018, 23:28 Mick Abraham &lt;<a
                href="mailto:mick@abrahamsolar.com" target="_blank"
                rel="noreferrer" moz-do-not-send="true">mick@abrahamsolar.com</a>
              wrote:<br>
            </div>
            <blockquote class="gmail_quote" style="margin:0 0 0
              .8ex;border-left:1px #ccc solid;padding-left:1ex">
              <div dir="ltr">
                <div>
                  <div dir="ltr"
                    class="m_-3986755880765008142m_2168128817494015gmail_signature"
                    data-smartmail="gmail_signature">
                    <div dir="ltr">Hello, Drake &amp; All~<br>
                    </div>
                  </div>
                </div>
                <div class="gmail_quote">
                  <div dir="ltr">
                    <div><br>
                    </div>
                    <div>Drake described his service dilemma about
                      batteries bought elsewhere &amp; whether to
                      correct the original hinky pack wiring (copied
                      below). My reply below may seem cynical &amp; I
                      may seem too eager to declare the existing battery
                      as: "Failed". Call me jaded.</div>
                    <div><br>
                    </div>
                    <div>Mick's $0.02 is: If there's no amp-hour monitor
                      in the system, I suggest you first try to persuade
                      the homeowner to buy a metering shunt &amp; a
                      modest amp-hour meter such as the
                      Tri-Metric--which could be used to measure &amp;
                      display the battery bank's amp-hour capacity. If
                      the client won't approve that expenditure (&amp;
                      hourly labor for explanations), the service tech
                      is hamstrung. Nobody can measure the health of a
                      battery bank by just looking at it or talking
                      about it...and clients sometimes receive the
                      inevitable "battery bad news" if they are shown
                      the diminished capacity on a digital display after
                      an equitably managed "pump &amp; dump".</div>
                    <div><br>
                    </div>
                    <div>Your thought, Drake, of holding back on any
                      re-wiring of the battery pack...seems
                      prudent...until the first set of amp-hour
                      measurements are recorded as a baseline. From
                      there...a common pattern is a series of attempted
                      remediation efforts--all for pay, of course--until
                      the homeowner acknowledges that it's time to start
                      afresh. </div>
                    <div><br>
                    </div>
                    <div>Oops, I left out an important step: getting a
                      read on whether the client has the money for new
                      batteries or not. I'm personally terrible at
                      getting that reconnaissance done early enough. If
                      the client isn't materially blessed to be able to
                      get new batteries, they might be better off
                      spending limited funds on fuel for the engine
                      generator instead of on battery testing &amp;
                      tutorials.</div>
                    <div><br>
                    </div>
                    <div>The Wrench List is the Bomb~<br clear="all">
                      <div>
                        <div dir="ltr"
class="m_-3986755880765008142m_2168128817494015m_-6805958290932026730gmail_signature"
                          data-smartmail="gmail_signature">
                          <div dir="ltr">
                            <div><br>
                            </div>
                            <div>Mick Abraham, Proprietor<br>
                              <a href="http://www.abrahamsolar.com"
                                rel="noreferrer noreferrer"
                                target="_blank" moz-do-not-send="true">www.abrahamsolar.com</a><br>
                              <br>
                              Landline: 970-731-4675</div>
                            <div>Cell phone or for text messaging:
                              970-946-6584</div>
                          </div>
                        </div>
                      </div>
                      <div class="gmail_quote">
                        <blockquote class="gmail_quote" style="margin:0
                          0 0 .8ex;border-left:1px #ccc
                          solid;padding-left:1ex"><br>
                          ---------- Forwarded message ----------<br>
                          From: Drake &lt;<a
                            href="mailto:drake.chamberlin@redwoodalliance.org"
                            rel="noreferrer noreferrer" target="_blank"
                            moz-do-not-send="true">drake.chamberlin@redwoodalliance.org</a>&gt;<br>
                          To: RE-wrenches &lt;<a
                            href="mailto:re-wrenches@lists.re-wrenches.org"
                            rel="noreferrer noreferrer" target="_blank"
                            moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                          Cc: <br>
                          Bcc: <br>
                          Date: Tue, 20 Nov 2018 11:41:17 -0500<br>
                          Subject: [RE-wrenches] Batt Cap AGM<br>
                          <div>
                            Hello Wrenches,<br>
                            <br>
                            An owner of an existing system has a bank of
                            twenty, 100 AH, 12 V Deep
                            cycle batteries of the
                            <a
                              href="http://www.xstaticbatcap.com/what-is-a-batcap-.html"
                              rel="noreferrer noreferrer"
                              target="_blank" moz-do-not-send="true">Batcap</a>
                            <a
                              href="http://www.xstaticbatcap.com/what-is-a-batcap-.html"
                              rel="noreferrer noreferrer"
                              target="_blank" moz-do-not-send="true">
                            </a>brand.<br>
                            <br>
                            The bank is made up of four sets of 5
                            batteries in parallel to produce
                            <b>500 AH battery sets at 12 V.</b> These
                            four parallel sets are then
                            wired  in series to give a 48 V nominal
                            bank. <br>
                            <br>
                            The battery voltages vary from around 13 to
                            15 volts. The bank is about 5
                            years old. The CEO of Batcap told the system
                            owner that these batteries
                            have lasted up to 30 years in solar
                            applications, so he has high
                            expectations for these batteries being
                            around for a while. <br>
                            <br>
                            My first impulse is to rewire the bank in a
                            normal series - parallel
                            configuration. But there are too many
                            strings to do this without a bus
                            bar. Besides, the batteries are likely
                            damaged, and rewiring them might
                            cause the bank to exhibit unsuspected
                            problems. How much money is worth
                            putting into this bank? $0?<br>
                            <br>
                            The owner seems like a reliable guy who
                            likely hired the wrong installer.
                            He could use some help. What would you do in
                            this situation? Rewire the
                            bank, leave it well enough alone or run for
                            the hills.<br>
                            <br>
                            Thanks,<br>
                            <br>
                            Drake <br>
                            <br>
                            <a
name="m_-3986755880765008142_m_2168128817494015_m_-6805958290932026730_m_668141993065556566__MailAutoSig"
                              rel="noreferrer noreferrer"
                              moz-do-not-send="true"></a>Drake
                            Chamberlin<br>
                            <i>Athens Electric LLC<br>
                              OH License 44810<br>
                              CO License 3773<br>
                              NABCEP Certified Solar PV <br>
                              740-448-7328<br>
                            </i><a href="http://athens-electric.com/"
                              rel="noreferrer noreferrer"
                              target="_blank" moz-do-not-send="true">http://athens-electric.com/</a>
                            <br>
                          </div>
                          <br>
                        </blockquote>
                      </div>
                    </div>
                  </div>
                  <div hspace="streak-pt-mark" style="max-height:1px"><img
                      alt=""
                      style="width:0px;max-height:0px;overflow:hidden"
src="https://mailfoogae.appspot.com/t?sender=abWlja0BhYnJhaGFtc29sYXIuY29t&amp;type=zerocontent&amp;guid=179fab7b-0187-4bde-bd69-7ddf5f09be55"
                      moz-do-not-send="true"><font size="1"
                      color="#ffffff">\u1427</font></div>
                </div>
              </div>
              <div hspace="streak-pt-mark" style="max-height:1px"><img
                  alt=""
                  style="width:0px;max-height:0px;overflow:hidden"
src="https://mailfoogae.appspot.com/t?sender=abWlja0BhYnJhaGFtc29sYXIuY29t&amp;type=zerocontent&amp;guid=20210fc2-3ee7-43bc-98b7-aef93c98ddc9"
                  moz-do-not-send="true"><font size="1" color="#ffffff">\u1427</font></div>
              _______________________________________________<br>
              List sponsored by Redwood Alliance<br>
              <br>
              List Address: <a
                href="mailto:RE-wrenches@lists.re-wrenches.org"
                rel="noreferrer noreferrer" target="_blank"
                moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
              <br>
              Change listserver email address &amp; settings:<br>
              <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                rel="noreferrer noreferrer noreferrer" target="_blank"
                moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
              <br>
              List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                rel="noreferrer noreferrer noreferrer" target="_blank"
                moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
              <br>
              List rules &amp; etiquette:<br>
              <a href="http://www.re-wrenches.org/etiquette.htm"
                rel="noreferrer noreferrer noreferrer" target="_blank"
                moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
              <br>
              Check out or update participant bios:<br>
              <a href="http://www.members.re-wrenches.org"
                rel="noreferrer noreferrer noreferrer" target="_blank"
                moz-do-not-send="true">www.members.re-wrenches.org</a><br>
              <br>
            </blockquote>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <pre class="moz-quote-pre" wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
  </body>
</html>