<div style="font-size: 10pt;"><div dir="auto">I had a similar issue with an On an off grid genny earlier this year. The customer had a local On an tech come out and they replaced the voltage regulator board and cleared up the issue.</div><div dir="auto">They also said these regulator boards for the older gennies were getting hard to find, so just another thing for a customer to consider.</div><div dir="auto"><br></div><div dir="auto">Glenn</div><div dir="auto"><br></div><div><div dir="auto" font-size:9pt;"="">Sent from my 'smart' phone so please excuse spelling and typos.</div></div></div><div style="font-size: 10pt;"><div id="LGEmailHeader" dir="auto"><div dir="auto"><br></div><div dir="auto">------ Original message------</div><div dir="auto"><b>From: </b>Kirk Herander<vtsolar@icloud.com></vtsolar@icloud.com></div><div dir="auto"><b>Date: </b>Thu, Nov 8, 2018 4:17 PM</div><div dir="auto"><b>To: </b><a href="mailto:re-wrenches@lists.re-wrenches.org">re-wrenches@lists.re-wrenches.org</a>;</div><div dir="auto"><b>Cc: </b></div><div dir="auto"><b>Subject:</b>[RE-wrenches] Kohler generator 1/2 voltage</div><div dir="auto"><br></div></div><pre>Hello,
I got called in to debug an old off grid system with a Kohler 8.5 RES generator. Across L1-L2 is 120vac. From both L1 & L2 to common gnd/neutral is 60v. I verified the windings are connected for 120/240 operation(in series with center tap for G/N). These voltages are the same on the genny side of its breaker when turned off (no inverter connection). I am having trouble envisioning a scenario of mis-wiring if indeed each one of the windings is producing 120 VAC. Seems odd to me that a bad regulator would cause this, but who knows. Alternator? Ideas? Thanks.
Kirk Herander, VT Solar, LLC
_______________________________________________
List sponsored by Redwood Alliance
List Address:<a href="mailto: RE-wrenches@lists.re-wrenches.org"> RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: http<a href="mailto:://www.mail-archive.com/re-wrenches@lists.re-wrenches.org">://www.mail-archive.com/re-wrenches@lists.re-wrenches.org</a>/<a href="http://maillist.ht">maillist.ht</a>ml
List rules & etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre></div>
</body></html>