    The SPD-600 is evidently the one to use on the SMA TL inverters.<br>
    <br>
    In older grounded PV systems, if the negative or positive is
    grounded directly to ground, then you could get by without<br>
    an SPD connected to that grounded conductor because it is, well,
    already grounded and that line will rise in voltage along with<br>
    the ground voltage from the strike.  However, if this grounded PV
    conductor  is connected through one of the r ground fault
    interrupters <br>
    that has a 1/2 amp or slightly higher ground bonding connection,
    (not permanently bonded),  like the Classic or MPPT-60 and<br>
    some other controllers with internal GFIs then I would think that a
    separate SPD line be used for positive and negative PV lines on that
    array.<br>
    We don't want that ground bond to open on that line and risk
    internal arcing in the equipment.<br>
    <br>
    As for arc faults, SPDs are a passive type protector and should not
    make any noise that might be interpreted by the sensor as arcing.<br>
    Lightning itself may very well be interpreted as an arc.  I think
    that the Bird-House system which has a switcher supply up-stairs<br>
    in the Bird-Next might have been an arc fault culprit for some TL
    inverters.  Sometimes it is hard for a AF detector to tell the<br>
    difference.  Hopefully they are better now.<br>
    <br>
    "I have clients who have covered the SPD's in tape to keep the light
    from attracting small flying insects to the electronics area. "<br>
    <br>
    I hear you there, Dave !  We are working on being able to coordinate
    the lightning strike with the insects so that the SPD also<br>
    works as a bug zapper !    :)   <span class="moz-smiley-s1"><span>:-)</span></span> 
    <br>
    Just kidding...<br>
    <br>
    boB<br>
    <br>
    <br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/9/2018 3:10 PM, Dave Angelini
      Offgrid Solar wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:e5c18726138503324bff50e197aac59e@127.0.0.1">
      <meta http-equiv="content-type" content="text/html; charset=utf-8">
      <p>We have been using Midnite SPD's since they came out. The one
        suggestion I have is the light is too intense. I have clients
        who have covered the SPD's in tape to keep the light from
        attracting small flying insects to the electronics area. Some
        places just have too many bugs :( The blue seems to bring them.
        I saw an inverter fan filter that was an 1/8 of an inch thick
        with gnats.</p>
      <p>Fly paper will help but the battery circuit and AC panel SPD's
        need some help here.</p>
      <pre><strong><span>Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank" moz-do-not-send="true">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net" moz-do-not-send="true">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
      <p> </p>
    </blockquote>
    <br>
    <br>
    <br>
    " boB,
    <p>            To add to Drake's  wonderings, I've had a few SMA
      TL-40 inverters trip with an AFCI fault.  Significant hassle to
      get onsite and deal with it. Some with metal roofs some without,
      may have been lightening in the area.</p>
    Bill "<br>
    <br>
    <br>
    <br>
    <br>
    <blockquote type="cite"
      cite="mid:e5c18726138503324bff50e197aac59e@127.0.0.1">
      <p>On Tue, 09 Oct 2018 17:02:32 -0400, Drake
        <a class="moz-txt-link-rfc2396E" href="mailto:drake.chamberlin@redwoodalliance.org">&lt;drake.chamberlin@redwoodalliance.org&gt;</a> wrote:</p>
      <blockquote type="cite" style="padding-left:5px;
        border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->Hi
        boB,<br>
        <br>
        I will keep putting an SPD on each string and on the AC line.
        Sometimes my systems end up with a lot of blue lights hanging
        from a wiring gutter!<br>
        <br>
        Have you ever heard of any problems using the Midnite SPDs with
        Sunny Boy TL series inverters? So far, I don't think I've had a
        problem, although one TL-22, on a large metal roof, had arc
        fault protector trips. <br>
        <br>
        Thanks,<br>
        <br>
        Drake<br>
        <br>
        <a name="_MailAutoSig" moz-do-not-send="true"></a>Drake
        Chamberlin<br>
        <em>Athens Electric LLC<br>
          OH License 44810<br>
          CO License 3773<br>
          NABCEP Certified Solar PV <br>
          740-448-7328<br>
        </em><a href="http://athens-electric.com/"
          moz-do-not-send="true">http://athens-electric.com/</a> <br>
         <br>
        <br>
        <br>
        At 01:39 PM 10/9/2018, you wrote:<br>
        <blockquote class="cite">Content-Type: multipart/alternative;<br>
           boundary="------------98C0DCEF93B9ECF248E0580B"<br>
          Content-Language: en-US<br>
          <br>
          <br>
          For an inverter with two MPPT inputs, you will need to treat
          the negatives and positive lines separate unless<br>
          the manufacturer says something else.  That means one  SPD per
          array unfortunately.  Negative and positive connect<br>
          to separate leads of the SPD and then ground in the middle. 
          As both positive and negative PV lines rise together<br>
          relative to ground, the SPD is supposed to clamp that rise to
          below the equipment's hi-pot voltage that they test<br>
          to at the factory.  (i.e. common mode voltage rise) All wires
          except for ground (chassis) of the equipment are tied <br>
          together and the hi-pot machine (sort of like a Megger ?)
          applies the high voltage between all those wires on one <br>
          side and ground on the other to make sure the insulation
          doesn't break down inside the equipment.  <br>
          This hi-pot test goes for AC  utility input/output connections
          and DC from the PV input side.  <br>
          <br>
          The SPD  has to clamp plus and minus and AC inputs to a lower
          voltage than this hipot rating but higher voltage<br>
          than lines will see differentially in voltage.  Remember that
          in a 3-wire SPD, there is two sets of MOVs in series and<br>
          the center is tied to ground.  If one MOV starts conducting at
          say, 500 volts DC then you can apply up to 1000<br>
          volts  between the hot leads.  Each plus and negative line can
          rise up to 500 volts from the lightning before they<br>
          start to clamp.  The  bigger the lightning strikes effect, the
          more current will be applied to the MOVs though and<br>
          the clamp voltage will rise somewhat.  That's why the SPD
          arrestor voltage should be well below the hi-pot voltage,<br>
          whatever that is...  Hi-pot voltages are quite a bit higher
          than the operating voltage.  For example, All Classic CC's<br>
          are tested to 2270 volts DC from hot lines to ground.  It's
          something like double the operating voltage plus 1000V<br>
          and multiply by 1.414 for DC rating.....  I'm going off memory
          so don't quote me on that but something like that.<br>
          <br>
          I think that Ray has the right idea about short connections
          like from the local generator.  Battery also.<br>
          Just apply SPDs to anything that goes outside like an antenna.<br>
          <br>
          boB<br>
          <br>
          <br>
          On 10/9/2018 8:26 AM, cwarfel wrote:<br>
          <blockquote class="cite"><br>
            <span style="font-family: Verdana;">I think something on the
              order of 90+% lightning strikes come from the utility
              feed, not the dc side. That has to be ignored if in a high
              strike area or grid isolated. </span><br>
            <br>
            On 10/8/2018 10:37 PM, Ray wrote:<br>
            <blockquote class="cite"><br>
              I believe you can use the SPD 300 AC on 2 strings, if PV
              neg is grounded.  You would connect the green to ground
              (or PV neg) and then connect the red to one string pos,
              and connect the black to the other string pos.  This would
              be limited to 300 v also.  I haven't tried that exact
              configuration, but I have used the 300 AC to protect both
              the AC in and AC out on 120 vac inverters.  I also believe
              you can use a 600 DC version, and wire as I mentioned, but
              the LEDs won't light. If you are using ungrounded
              inverters, then I think you would need an SPD for each
              string in order to protect both the pos and neg of each
              string, like you've been doing.<br>
              <br>
              Maybe someone from Midnite can clarify this.<br>
              <br>
              As far as it being worth it, I haven't had lightning
              related damage since I started using the Midnite SPDs, and
              I used to have system damage every year.  If you are not
              in lightning country, or the install is in a low spot with
              less likelihood of taking a hit, you might be able to
              skimp.  But for some of these off grid ridge top installs,
              I consider it a must. Some times I don't install one on
              the gen circuit, if its really close.<br>
              <br>
                <br>
              <br>
              <pre>Ray Walters
Remote Solar
303 505-8760</pre>
              <span style="font-family: 'Courier New', Courier;"></span>On
              10/8/18 4:03 PM, Drake wrote:<br>
              <blockquote class="cite">Hello Wrenches,<br>
                <br>
                Do you use surge arrestors with multi MPPT input string
                inverters? Do you put a separate arrestor on each MPPT
                input? I find it sort of pricey using a Midnite Solar
                arrestor on each string, but have been doing that. Is
                there a less expensive approach that is effective? <br>
                <br>
                I believe the Midnite units are the best. Are they worth
                the expense?<br>
                <br>
                Thank you,<br>
                <br>
                Drake<br>
                 <br>
                 <br>
                <a name="_MailAutoSig" moz-do-not-send="true"></a>Drake
                Chamberlin<br>
                <em>Athens Electric LLC<br>
                  OH License 44810<br>
                  CO License 3773<br>
                  NABCEP Certified Solar PV <br>
                  740-448-7328<br>
                </em><a href="http://athens-electric.com/"
                  moz-do-not-send="true">http://athens-electric.com/</a>
                <br>
                <br>
                <br>
                <br>
                <br>
                <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" moz-do-not-send="true">
www.members.re-wrenches.org</a>

</pre>
                <span style="font-family: 'Courier New', Courier;"></span></blockquote>
              <br>
              <br>
              <br>
              <br>
              <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" moz-do-not-send="true">
www.members.re-wrenches.org</a>

</pre>
              <span style="font-family: 'Courier New', Courier;"></span></blockquote>
            <br>
            -- <br>
            <br>
            <span style="font-size: small;">         Christopher Warfel,
              PE<br>
                     ENTECH Engineering, Inc.<br>
              PO Box 871, Block Island, RI 02807<br>
                             (401)466-8978</span><br>
             <br>
            <a href="http://entech-engineering.com"
              moz-do-not-send="true"> <img
                src="cid:part17.7616CD24.E6513526@midnitesolar.com"
                alt="EEI logo" class="" height="89" width="201"> </a> <br>
            <br>
            <br>
            <br>
            <pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org" moz-do-not-send="true">
www.members.re-wrenches.org</a>

</pre>
            <span style="font-family: 'Courier New', Courier;"></span></blockquote>
          <br>
          <br>
          <br>
          _______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            moz-do-not-send="true">
            http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
          <br>
          <br>
          List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
            moz-do-not-send="true">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
          <br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm"
            moz-do-not-send="true"> www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org/"
            moz-do-not-send="true"> www.members.re-wrenches.org</a></blockquote>
      </blockquote>
      <div>-- <br>
        <pre> </pre>
        <pre> </pre>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>