    For an inverter with two MPPT inputs, you will need to treat the
    negatives and positive lines separate unless<br>
    the manufacturer says something else.  That means one  SPD per array
    unfortunately.  Negative and positive connect<br>
    to separate leads of the SPD and then ground in the middle.  As both
    positive and negative PV lines rise together<br>
    relative to ground, the SPD is supposed to clamp that rise to below
    the equipment's hi-pot voltage that they test<br>
    to at the factory.  (i.e. common mode voltage rise) All wires except
    for ground (chassis) of the equipment are tied <br>
    together and the hi-pot machine (sort of like a Megger ?) applies
    the high voltage between all those wires on one <br>
    side and ground on the other to make sure the insulation doesn't
    break down inside the equipment.  <br>
    This hi-pot test goes for AC  utility input/output connections and
    DC from the PV input side.  <br>
    <br>
    The SPD  has to clamp plus and minus and AC inputs to a lower
    voltage than this hipot rating but higher voltage<br>
    than lines will see differentially in voltage.  Remember that in a
    3-wire SPD, there is two sets of MOVs in series and<br>
    the center is tied to ground.  If one MOV starts conducting at say,
    500 volts DC then you can apply up to 1000<br>
    volts  between the hot leads.  Each plus and negative line can rise
    up to 500 volts from the lightning before they<br>
    start to clamp.  The  bigger the lightning strikes effect, the more
    current will be applied to the MOVs though and<br>
    the clamp voltage will rise somewhat.  That's why the SPD arrestor
    voltage should be well below the hi-pot voltage,<br>
    whatever that is...  Hi-pot voltages are quite a bit higher than the
    operating voltage.  For example, All Classic CC's<br>
    are tested to 2270 volts DC from hot lines to ground.  It's
    something like double the operating voltage plus 1000V<br>
    and multiply by 1.414 for DC rating.....  I'm going off memory so
    don't quote me on that but something like that.<br>
    <br>
    I think that Ray has the right idea about short connections like
    from the local generator.  Battery also.<br>
    Just apply SPDs to anything that goes outside like an antenna.<br>
    <br>
    boB<br>
    <br>
    <br>
    <div class="moz-cite-prefix">On 10/9/2018 8:26 AM, cwarfel wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:d9456b9d-7f42-89d7-1ffb-53810345cd2f@entech-engineering.com">
      <meta http-equiv="Content-Type" content="text/html;
        charset=windows-1252">
      <p><font face="Verdana">I think something on the order <font
            face="Verdana">of 90+% lig<font face="Verdana">htnin<font
                face="Verdana">g strikes come from the utili<font
                  face="Verdana">ty feed, not the dc side. That has to
                  be ignored if in a high str<font face="Verdana">ike
                    area or<font face="Verdana"> grid is<font
                        face="Verdana">olated. </font></font></font></font></font></font></font></font><br>
      </p>
      <br>
      <div class="moz-cite-prefix">On 10/8/2018 10:37 PM, Ray wrote:<br>
      </div>
      <blockquote type="cite"
        cite="mid:50c7a8a6-0a86-90cf-0075-c5d755da1069@solarray.com">
        <meta http-equiv="Content-Type" content="text/html;
          charset=windows-1252">
        <p>I believe you can use the SPD 300 AC on 2 strings, if PV neg
          is grounded.  You would connect the green to ground (or PV
          neg) and then connect the red to one string pos, and connect
          the black to the other string pos.  This would be limited to
          300 v also.  I haven't tried that exact configuration, but I
          have used the 300 AC to protect both the AC in and AC out on
          120 vac inverters.  I also believe you can use a 600 DC
          version, and wire as I mentioned, but the LEDs won't light. If
          you are using ungrounded inverters, then I think you would
          need an SPD for each string in order to protect both the pos
          and neg of each string, like you've been doing.</p>
        <p>Maybe someone from Midnite can clarify this.</p>
        <p>As far as it being worth it, I haven't had lightning related
          damage since I started using the Midnite SPDs, and I used to
          have system damage every year.  If you are not in lightning
          country, or the install is in a low spot with less likelihood
          of taking a hit, you might be able to skimp.  But for some of
          these off grid ridge top installs, I consider it a must. Some
          times I don't install one on the gen circuit, if its really
          close.<br>
        </p>
        <p>  <br>
        </p>
        <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
        <div class="moz-cite-prefix">On 10/8/18 4:03 PM, Drake wrote:<br>
        </div>
        <blockquote type="cite"
          cite="mid:20181008220322.B75F41071B1@pdx1-mailman03.dreamhost.com">
          <meta http-equiv="content-type" content="text/html;
            charset=windows-1252">
          Hello Wrenches,<br>
          <br>
          Do you use surge arrestors with multi MPPT input string
          inverters? Do you put a separate arrestor on each MPPT input?
          I find it sort of pricey using a Midnite Solar arrestor on
          each string, but have been doing that. Is there a less
          expensive approach that is effective? <br>
          <br>
          I believe the Midnite units are the best. Are they worth the
          expense?<br>
          <br>
          Thank you,<br>
          <br>
          Drake<br>
           <br>
           <br>
          <a name="_MailAutoSig" moz-do-not-send="true"></a>Drake
          Chamberlin<br>
          <i>Athens Electric LLC<br>
            OH License 44810<br>
            CO License 3773<br>
            NABCEP Certified Solar PV <br>
            740-448-7328<br>
          </i><a href="http://athens-electric.com/"
            moz-do-not-send="true">http://athens-electric.com/</a> <br>
          <br>
          <br>
          <fieldset class="mimeAttachmentHeader"></fieldset>
          <br>
          <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
        </blockquote>
        <br>
        <br>
        <fieldset class="mimeAttachmentHeader"></fieldset>
        <br>
        <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org" moz-do-not-send="true">www.members.re-wrenches.org</a>

</pre>
      </blockquote>
      <br>
      <div class="moz-signature">-- <br>
        <meta http-equiv="content-type" content="text/html;
          charset=windows-1252">
        <div class="moz-signature"><br>
          <div class="moz-signature">
            <meta http-equiv="content-type" content="text/html;
              charset=windows-1252">
            <div class="moz-signature">
              <div class="moz-signature">
                <div class="moz-signature">
                  <div class="moz-signature">
                    <div class="moz-signature">
                      <meta http-equiv="content-type"
                        content="text/html; charset=windows-1252">
                      <font size="-1">         Christopher Warfel, PE<br>
                               ENTECH Engineering, Inc.<br>
                        PO Box 871, Block Island, RI 02807<br>
                                       (401)466-8978</font><br>
                      <div class="moz-signature"> <br>
                        <meta http-equiv="content-type"
                          content="text/html; charset=windows-1252">
                        <title></title>
                        <a href="http://entech-engineering.com"
                          moz-do-not-send="true"><img
                            moz-do-not-send="false"
                            src="cid:part13.E5646B8D.62A1B44F@midnitesolar.com"
                            alt="EEI logo" class="" height="89"
                            width="201" border="0"></a> </div>
                    </div>
                  </div>
                </div>
              </div>
            </div>
          </div>
        </div>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>