<p>We have been using Midnite SPD's since they came out. The one suggestion I have is the light is too intense. I have clients who have covered the SPD's in tape to keep the light from attracting small flying insects to the electronics area. Some places just have too many bugs :( The blue seems to bring them. I saw an inverter fan filter that was an 1/8 of an inch thick with gnats.</p>
<p>Fly paper will help but the battery circuit and AC panel SPD's need some help here.</p>
<pre><strong><span>Dave Angelini Offgrid Solar
"we go where powerlines don't"
<a href="http://members.sti.net/offgridsolar/" target="_blank">http://members.sti.net/offgridsolar/</a>
e-mail  <a href="mailto:offgridsolar@sti.net">offgridsolar@sti.net</a>
text 209 813 0060</span></strong></pre>
<p>&nbsp;</p>
<p>On Tue, 09 Oct 2018 17:02:32 -0400, Drake &lt;drake.chamberlin@redwoodalliance.org&gt; wrote:</p>
<blockquote type="cite" style="padding-left:5px; border-left:#1010ff 2px solid; margin-left:5px; width:100%"><!-- html ignored --><!-- head ignored --><!-- meta ignored -->Hi boB,<br /><br /> I will keep putting an SPD on each string and on the AC line. Sometimes my systems end up with a lot of blue lights hanging from a wiring gutter!<br /><br /> Have you ever heard of any problems using the Midnite SPDs with Sunny Boy TL series inverters? So far, I don't think I've had a problem, although one TL-22, on a large metal roof, had arc fault protector trips. <br /><br /> Thanks,<br /><br /> Drake<br /><br /> <a name="_MailAutoSig"></a>Drake Chamberlin<br /> <em>Athens Electric LLC<br /> OH License 44810<br /> CO License 3773<br /> NABCEP Certified Solar PV <br /> 740-448-7328<br /> </em><a href="http://athens-electric.com/">http://athens-electric.com/</a> <br /> &nbsp;<br /><br /> <br /> At 01:39 PM 10/9/2018, you wrote:<br />
<blockquote class="cite">Content-Type: multipart/alternative;<br /> &nbsp;boundary="------------98C0DCEF93B9ECF248E0580B"<br /> Content-Language: en-US<br /><br /> <br /> For an inverter with two MPPT inputs, you will need to treat the negatives and positive lines separate unless<br /> the manufacturer says something else.&nbsp; That means one&nbsp; SPD per array unfortunately.&nbsp; Negative and positive connect<br /> to separate leads of the SPD and then ground in the middle.&nbsp; As both positive and negative PV lines rise together<br /> relative to ground, the SPD is supposed to clamp that rise to below the equipment's hi-pot voltage that they test<br /> to at the factory.&nbsp; (i.e. common mode voltage rise) All wires except for ground (chassis) of the equipment are tied <br /> together and the hi-pot machine (sort of like a Megger ?) applies the high voltage between all those wires on one <br /> side and ground on the other to make sure the insulation doesn't break down inside the equipment.&nbsp; <br /> This hi-pot test goes for AC&nbsp; utility input/output connections and DC from the PV input side.&nbsp; <br /><br /> The SPD&nbsp; has to clamp plus and minus and AC inputs to a lower voltage than this hipot rating but higher voltage<br /> than lines will see differentially in voltage.&nbsp; Remember that in a 3-wire SPD, there is two sets of MOVs in series and<br /> the center is tied to ground.&nbsp; If one MOV starts conducting at say, 500 volts DC then you can apply up to 1000<br /> volts&nbsp; between the hot leads.&nbsp; Each plus and negative line can rise up to 500 volts from the lightning before they<br /> start to clamp.&nbsp; The&nbsp; bigger the lightning strikes effect, the more current will be applied to the MOVs though and<br /> the clamp voltage will rise somewhat.&nbsp; That's why the SPD arrestor voltage should be well below the hi-pot voltage,<br /> whatever that is...&nbsp; Hi-pot voltages are quite a bit higher than the operating voltage.&nbsp; For example, All Classic CC's<br /> are tested to 2270 volts DC from hot lines to ground.&nbsp; It's something like double the operating voltage plus 1000V<br /> and multiply by 1.414 for DC rating.....&nbsp; I'm going off memory so don't quote me on that but something like that.<br /><br /> I think that Ray has the right idea about short connections like from the local generator.&nbsp; Battery also.<br /> Just apply SPDs to anything that goes outside like an antenna.<br /><br /> boB<br /><br /> <br /> On 10/9/2018 8:26 AM, cwarfel wrote:<br />
<blockquote class="cite"><br /> <span style="font-family: Verdana;">I think something on the order of 90+% lightning strikes come from the utility feed, not the dc side. That has to be ignored if in a high strike area or grid isolated. </span><br /><br /> On 10/8/2018 10:37 PM, Ray wrote:<br />
<blockquote class="cite"><br /> I believe you can use the SPD 300 AC on 2 strings, if PV neg is grounded.&nbsp; You would connect the green to ground (or PV neg) and then connect the red to one string pos, and connect the black to the other string pos.&nbsp; This would be limited to 300 v also.&nbsp; I haven't tried that exact configuration, but I have used the 300 AC to protect both the AC in and AC out on 120 vac inverters.&nbsp; I also believe you can use a 600 DC version, and wire as I mentioned, but the LEDs won't light. If you are using ungrounded inverters, then I think you would need an SPD for each string in order to protect both the pos and neg of each string, like you've been doing.<br /><br /> Maybe someone from Midnite can clarify this.<br /><br /> As far as it being worth it, I haven't had lightning related damage since I started using the Midnite SPDs, and I used to have system damage every year.&nbsp; If you are not in lightning country, or the install is in a low spot with less likelihood of taking a hit, you might be able to skimp.&nbsp; But for some of these off grid ridge top installs, I consider it a must. Some times I don't install one on the gen circuit, if its really close.<br /><br /> &nbsp; <br /><br />
<pre>Ray Walters
Remote Solar
303 505-8760</pre>
<span style="font-family: 'Courier New', Courier;"></span>On 10/8/18 4:03 PM, Drake wrote:<br />
<blockquote class="cite">Hello Wrenches,<br /><br /> Do you use surge arrestors with multi MPPT input string inverters? Do you put a separate arrestor on each MPPT input? I find it sort of pricey using a Midnite Solar arrestor on each string, but have been doing that. Is there a less expensive approach that is effective? <br /><br /> I believe the Midnite units are the best. Are they worth the expense?<br /><br /> Thank you,<br /><br /> Drake<br /> &nbsp;<br /> &nbsp;<br /> <a name="_MailAutoSig"></a>Drake Chamberlin<br /> <em>Athens Electric LLC<br /> OH License 44810<br /> CO License 3773<br /> NABCEP Certified Solar PV <br /> 740-448-7328<br /> </em><a href="http://athens-electric.com/">http://athens-electric.com/</a> <br /><br /> <br /><br /> <br />
<pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a>

</pre>
<span style="font-family: 'Courier New', Courier;"></span></blockquote>
<br /><br /> <br /><br />
<pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a>

</pre>
<span style="font-family: 'Courier New', Courier;"></span></blockquote>
<br /> -- <br /><br /> <span style="font-size: small;">&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; Christopher Warfel, PE<br /> &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; ENTECH Engineering, Inc.<br /> PO Box 871, Block Island, RI 02807<br /> &nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp;&nbsp; (401)466-8978</span><br /> &nbsp;<br /> <a href="http://entech-engineering.com"> <img src="cid:fa605fa29a063e3de384e32289a84138@sti.net" alt="EEI logo" width="201" height="89" /> </a>&nbsp;<br /><br /> <br /><br />
<pre>_______________________________________________
List sponsored by Redwood Alliance

List Address:
<a href="mailto:RE-wrenches@lists.re-wrenches.org">
RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive:
<a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a href="http://www.re-wrenches.org/etiquette.htm">
www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a href="http://www.members.re-wrenches.org">
www.members.re-wrenches.org</a>

</pre>
<span style="font-family: 'Courier New', Courier;"></span></blockquote>
<br /><br /> <br /> _______________________________________________<br /> List sponsored by Redwood Alliance<br /><br /> List Address: RE-wrenches@lists.re-wrenches.org<br /><br /> Change listserver email address &amp; settings:<br /> <a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"> http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a> <br /><br /> List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"> http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a> <br /><br /> List rules &amp; etiquette:<br /> <a href="http://www.re-wrenches.org/etiquette.htm"> www.re-wrenches.org/etiquette.htm</a><br /><br /> Check out or update participant bios:<br /> <a href="http://www.members.re-wrenches.org/"> www.members.re-wrenches.org</a></blockquote>
</blockquote>
<div>-- <br />
<pre>&nbsp;</pre>
<pre>&nbsp;</pre>
</div>