    <p>I'm bumping it up to a pair of 50 watt modules, I don't want to
      go bigger because I need to fit them behind some shutters that
      will cover them in the summer.   To answer Bill's questions, the
      site is at 10,000 ft, about a 1:12 pitch, so its definitely going
      to pile up snow.  We had snow sitting this year there into May.</p>
    <p>Thanks,<br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 10/9/18 8:57 AM, Drake wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:20181009145803.8F353107089@pdx1-mailman03.dreamhost.com">
      <meta http-equiv="content-type" content="text/html;
        charset=windows-1252">
      We have an AC coupled  backup system at our house in S.E. Ohio. In
      the winter we have many cloudy days. We are using two 40 W Sunwise
      modules in series with a Morningstar PWM CC to maintain a 415 AH,
      24 V
      set of Full River AGM batteries. We don't need to use the AC
      charger for
      around 1/2 the year. In the winter, we charge regularly from the
      grid.<br>
      <br>
      Colorado has a <u>lot</u> more winter sun that SE Ohio. If I did
      ours
      over again, I'd double the maintainer array. But we have many
      periods, of
      several days in a row, where it is so dingy that our main array
      produces
      almost nothing, with no snow cover. I've never seen these
      prolonged, low
      light conditions in Colorado. If the price difference for a larger
      maintainer array isn't too much, I'd likely go bigger, especially
      since
      your battery bank is twice as big.  <br>
      <br>
      <a name="_MailAutoSig" moz-do-not-send="true"></a>Drake Chamberlin<br>
      <i>Athens Electric LLC<br>
        OH License 44810<br>
        CO License 3773<br>
        NABCEP Certified Solar PV <br>
        740-448-7328<br>
      </i><a href="http://athens-electric.com/" moz-do-not-send="true">http://athens-electric.com/</a>
      <br>
       <br>
      <br>
      <br>
      At 11:19 PM 10/8/2018, you wrote:<br>
      <blockquote type="cite" class="cite" cite="">Lots of questions
        this
        season..... I'm winterizing a cabin for a customer that will not
        be there
        for the next 8 months (summer use only). Inverter and loads will
        be off.
        The rooftop array will probably be covered with snow for
        extended periods
        of time, and he has a brand new 800 AH set of AGM batteries. 
        I've
        read that AGMs can handle sitting for longer periods of time,
        but my
        experience is that they are a bit finicky.  I'm planning on
        adding
        a small wall mounted array on a small Morningstar PWM controller
        that's
        sole purpose is to trickle charge the batteries and off set the
        self
        discharge in heavy snow.  What is the minimum size array
        needed?
        I've calculated self discharge rates from 2% to 5% /month, and
        I'm seeing
        a very small array would offset that.  Even at 5% monthly
        losses,
        and 4 hrs of sun/ day, I'm seeing a 10 watt array could meet
        that. 
        My current plan is a pair of 30 watt modules wired in series for
        the 24 v
        battery.  Is that too small? Or should I not even worry,
        because
        enough sun will creep through the snow to the main array?
        Thanks, -- Ray
        Walters Remote Solar 303 505-8760
        _______________________________________________ List sponsored
        by Redwood
        Alliance List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a> Change
        listserver email address &amp; settings:
        <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
          eudora="autourl" moz-do-not-send="true">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
        List-Archive:
        <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
          eudora="autourl" moz-do-not-send="true">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
        List rules &amp; etiquette:
        <a href="http://www.re-wrenches.org/etiquette.htm"
          eudora="autourl" moz-do-not-send="true">
          www.re-wrenches.org/etiquette.htm</a> Check out or update
        participant
        bios:
        <a href="http://www.members.re-wrenches.org/" eudora="autourl"
          moz-do-not-send="true">
          www.members.re-wrenches.org</a> &lt;/x-flowed&gt;</blockquote>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>