<div dir="ltr">Greetings, Wrenchies~<div><br></div><div>Below I&#39;ve pasted a visual from the Trace T240 transformer product guide, circa 2000:</div><div><br></div><div><div><img src="cid:ii_jn0ctsmc0" alt="image.png" width="518" height="399"><br></div><div><br></div><div>My client&#39;s 240vAC 60 hertz source circuit has the two hots but no neutral. They&#39;d like to run some 120v tools &amp; appliances, hence the autoformer. I see in the diagram that a neutral from the input side is not required, but:</div><div><br></div><div>* In that event, can I ground the newly derived neutral without causing havoc? The main home where the 240v wires originate is about 150 feet away &amp; the AC neutral is single point grounded there. </div><div><br></div><div>Other cautions or caveats? Thanks in advance. The Wrench List is The Bomb~</div><div>  </div><div><div dir="ltr" class="gmail_signature" data-smartmail="gmail_signature"><div dir="ltr"><div>Mick Abraham, Proprietor<br><a href="http://www.abrahamsolar.com" target="_blank">www.abrahamsolar.com</a><br><br>Landline: 970-731-4675</div><div>Cell phone or for text messaging: 970-946-6584</div></div></div></div></div></div><div hspace="streak-pt-mark" style="max-height:1px"><img alt="" style="width:0px;max-height:0px;overflow:hidden" src="https://mailfoogae.appspot.com/t?sender=abWlja0BhYnJhaGFtc29sYXIuY29t&amp;type=zerocontent&amp;guid=8364eae7-d84f-45d4-8b1b-a795cf421fea"><font color="#ffffff" size="1">\u1427</font></div>