<p>Unfortunately I'm seeing premature failures of the 2 v models
even more. You have paralleled cells in each battery, and it can
be difficult to even identify the failures. I found the infared
camera to be invaluable, as you can see the shorted cell clearly
in a thermal image.<br>
</p>
<pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
<div class="moz-cite-prefix">On 9/12/18 9:53 AM, Drake wrote:<br>
</div>
<blockquote type="cite"
cite="mid:20180912155326.870EA105C7A@pdx1-mailman03.dreamhost.com">
<meta http-equiv="content-type" content="text/html;
charset=windows-1252">
I agree with the comments that followed on this thread, and would
also
like to add that Trojan L-16 batteries have a high rate of
premature
failure. Possibly the 2 V cells are better, but the 6 V cells seem
very
prone to dying early. Trojan batteries were robust in past
decades, but
seem exceedingly fragile now. <br>
<br>
At 08:44 PM 9/11/2018, you wrote:<br>
<blockquote type="cite" class="cite" cite="">Hello wrenches,<br>
<br>
I inspected a system that another company had installed. It
had
single string of 12 x Trojan L16RE-2V batteries about 2 years
old.
They had experienced a battery melt-down. It looks as though
the
meltdown had occurred internally, not from a bad connection.<br>
<br>
The system was dual stack Outback VFXR-3524A inverters (to be
precise one
was a sealed unit). The set-points were as follows:<br>
Absorb Voltage was 29.8V<br>
Absorb Time was 6.0 hours<br>
Float Voltage was 27.0V<br>
Rebulk Voltage was 27.0V<br>
End Amps was 0A<br>
<br>
These settings extended similarly to 2 x FM80 charge
controllers.<br>
<br>
I was able to jumper the melted battery and get her power in 15
minutes. Her installer had left her without power for 2
weeks. My clients will kill me if that happened!<br>
<br>
Anyway, I believe these set-points are way out of whack and too
aggressive. The voltage is OK (Trojan recommends ~29.6V for
this)
but the Absorb time seems way too long, Rebulk is too high and
end amps
isn't helping. However, Im not finding a definitive article
from
Trojan that describes typical Absorb times or even how to adjust
towards
a good Absorb Time, based on specific gravity measurements or
amperage
absorption.  <br>
<br>
My diagnosis is that these batteries have been cooked over the
past 2
years. In the electrolyte, there is noticeable
"floaties". The client said that the original installer
had accused her of not using distilled water, but I don't
believe that
would cause her symptoms. I believe the floaties are plate
material.<br>
<br>
I'd be interested in wrenches opinions familiar with these
batteries if
these are appropriate settings for a low energy user. I will
attempt to get through to Trojan as well.<br>
<br>
Thanks in advance<br>
<br>
<br>
<br>
-- <br>
<br>
<font color="#305A78"><br>
</font><br>
Mac Lewis<br>
<br>
<font face="Verdana"><b>"Yo solo sé que no sé nada."Â
-Sócrates<br>
</b></font>_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
eudora="autourl" moz-do-not-send="true">
http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
<br>
<br>
List-Archive:
<a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
eudora="autourl" moz-do-not-send="true">
http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
<br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm"
eudora="autourl" moz-do-not-send="true">
www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org/" eudora="autourl"
moz-do-not-send="true">
www.members.re-wrenches.org</a></blockquote>
<br>
<fieldset class="mimeAttachmentHeader"></fieldset>
<br>
<pre wrap="">_______________________________________________
List sponsored by Redwood Alliance
List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>
Change listserver email address & settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
List rules & etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>
Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>
</pre>
</blockquote>
<br>
</body>
</html>