    <p>I started recommending people use the new ECM drive circ pumps. 
      They use half the power and are a direct replacement.  Have your
      plumber check out the Taco e series, or the Grundfos Alpha series
      of circ pumps.  <br>
    </p>
    <pre class="moz-signature" cols="72">Ray Walters
Remote Solar
303 505-8760</pre>
    <div class="moz-cite-prefix">On 9/7/18 8:45 PM, David Palumbo wrote:<br>
    </div>
    <blockquote type="cite"
      cite="mid:5b9337b4.1c69fb81.acae7.38bb@mx.google.com">
      <meta http-equiv="Content-Type" content="text/html; charset=utf-8">
      <meta name="Generator" content="Microsoft Word 15 (filtered
        medium)">
      <style><!--
/* Font Definitions */
@font-face
        {font-family:"Cambria Math";
        panose-1:2 4 5 3 5 4 6 3 2 4;}
@font-face
        {font-family:Calibri;
        panose-1:2 15 5 2 2 2 4 3 2 4;}
/* Style Definitions */
p.MsoNormal, li.MsoNormal, div.MsoNormal
        {margin:0in;
        margin-bottom:.0001pt;
        font-size:11.0pt;
        font-family:"Calibri",sans-serif;}
a:link, span.MsoHyperlink
        {mso-style-priority:99;
        color:blue;
        text-decoration:underline;}
a:visited, span.MsoHyperlinkFollowed
        {mso-style-priority:99;
        color:#954F72;
        text-decoration:underline;}
.MsoChpDefault
        {mso-style-type:export-only;}
@page WordSection1
        {size:8.5in 11.0in;
        margin:1.0in 1.0in 1.0in 1.0in;}
div.WordSection1
        {page:WordSection1;}
--></style>
      <div class="WordSection1">
        <p class="MsoNormal">El Sid 10W DC pumps are great but in my
          experience they did not have the flow and head \u201coomph\u201d for
          long runs for the zones on our second and third floors with
          our hydronic heating system (wood boiler). In our off grid
          house we installed El Sid\u2019s on all 4 zones in the late 1980\u2019s.
          We had recurring problems with the 2<sup>nd</sup> and 3<sup>rd</sup>
          floor zones (long runs) becoming air bound repeatedly after a
          couple of months of heavy use in the winter. Basement and 1<sup>st</sup>
          floor zones did not have this problem. I consulted with some
          plumbing and heating folks and ended up replacing the 2<sup>nd</sup>
          and 3<sup>rd</sup> floor zone El Sid\u2019s with 115VAC Grundfos
          circ pumps. Problem solved, no more air lock problems. I had a
          hard time understanding that while the El Sid\u2019s worked OK on
          the longer, higher head zones but did not have the power to
          avoid the air lock situation in our heating system. One of the
          plumbers explained it to me twenty something years ago BUT I
          don\u2019t recall his explanation now. Maybe some wrench with more
          hydronic chops than I can explain it.</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Dave Palumbo</p>
        <p class="MsoNormal">Independent Power</p>
        <p class="MsoNormal">Hyde Park, VT</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <p class="MsoNormal">Sent from <a
            href="https://go.microsoft.com/fwlink/?LinkId=550986"
            moz-do-not-send="true">Mail</a> for Windows 10</p>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div
          style="mso-element:para-border-div;border:none;border-top:solid
          #E1E1E1 1.0pt;padding:3.0pt 0in 0in 0in">
          <p class="MsoNormal" style="border:none;padding:0in"><b>From:
            </b><a href="mailto:bbassett2@gmail.com"
              moz-do-not-send="true">Bradley Bassett</a><br>
            <b>Sent: </b>Friday, September 7, 2018 10:09 PM<br>
            <b>To: </b><a
              href="mailto:re-wrenches@lists.re-wrenches.org"
              moz-do-not-send="true">RE-wrenches</a><br>
            <b>Subject: </b>Re: [RE-wrenches] Forced air Furnace</p>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div>
            <p class="MsoNormal">I have multiple ElSid pumps in my
              heating system which have been running for just about 15
              years without the slightest hitch. At 10W each they are
              hard to beat, but they do need DC so a power supply is
              needed. I ran them off 24VDC direct from the battery for
              the first 10 years and from a small MeanWell power supply
              for the last 5 years. My only complaint is that when there
              are 4 of them running it sounds like a miniature WWII
              bomber. No loud enough to hear outside of the utility room
              but something to keep in mind.</p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Brad Bassett</p>
          </div>
          <div>
            <p class="MsoNormal">AEE Solar</p>
          </div>
          <div>
            <p class="MsoNormal"><o:p> </o:p></p>
          </div>
          <div>
            <p class="MsoNormal">Brad</p>
          </div>
        </div>
        <p class="MsoNormal"><o:p> </o:p></p>
        <div>
          <div>
            <p class="MsoNormal">On Fri, Sep 7, 2018 at 7:33 AM Drake
              &lt;<a href="mailto:drake.chamberlin@redwoodalliance.org"
                moz-do-not-send="true">drake.chamberlin@redwoodalliance.org</a>&gt;
              wrote:</p>
          </div>
          <blockquote style="border:none;border-left:solid #CCCCCC
            1.0pt;padding:0in 0in 0in
            6.0pt;margin-left:4.8pt;margin-right:0in">
            <div>
              <p class="MsoNormal">Dana, <br>
                <br>
                Your comments, and other comments on this list have made
                me see the light. We are going to go with a boiler. <br>
                <br>
                What is the best source of equipment for this
                application these days? <br>
                <br>
                Many years ago, I helped install a system in Colorado
                using El Sid pumps, with guidance from you, if you
                recall this ancient history. <br>
                <br>
                Cheers,<br>
                <br>
                Drake <br>
                <br>
                <a name="m_-8249959848673430069__MailAutoSig"
                  moz-do-not-send="true"></a>Drake Chamberlin<br>
                <i>Athens Electric LLC<br>
                  OH License 44810<br>
                  CO License 3773<br>
                  NABCEP Certified Solar PV <br>
                  740-448-7328<br>
                </i><a href="http://athens-electric.com/"
                  target="_blank" moz-do-not-send="true">http://athens-electric.com/</a>
                <br>
                <br>
                <br>
                At 07:43 PM 8/23/2018, you wrote:<br>
                <br>
              </p>
              <blockquote style="margin-top:5.0pt;margin-bottom:5.0pt">
                <p class="MsoNormal">Content-Type:
                  multipart/alternative;<br>
                          
                  boundary="----=_NextPart_000_0068_01D43B08.DFB2A130"<br>
                  Content-Language: en-us<br>
                  <br>
                  Drake,<br>
                  All the conventional units I have amp clamped over the
                  years are pushing 900-900+ watts per hour. I do not
                  recommend them ever &amp; to date I have never found a
                  lower wattage blower. I would assume that a permanent
                  magnet motor would fit this suggestion, but I have not
                  found one.<br>
                  For off grid I recommend: Radiant floor heat first and
                  hot water base board second long before hot air. Air
                  is a better insulator than a heat transfer agent.<br>
                  The new ECM (electronically commutated motors) pump
                  motors are basically at DC permanent magnet motor
                  power draws [Taco &amp; Grundfoss] these days.<br>
                   <br>
                  Best of luck with this one.<br>
                   <br>
----------------------------------------------------------------------------<br>
                  Dana Orzel                              Great Solar
                  Works, Inc. <br>
                  <b>C - 208.721.7003                       <a
                      href="mailto:dana@solarwork.com" target="_blank"
                      moz-do-not-send="true">dana@solarwork.com</a><br>
                  </b>Idaho Contractor - # 028765         Idaho PV #
                  028374<br>
                  NABCEP # 051112-136                       <a
                    href="http://www.solarwork.biz" target="_blank"
                    moz-do-not-send="true">www.solarwork.biz</a><br>
                  <u>"Responsible Technologies for Responsible People
                    since 1988"  <br>
                  </u><b>P</b> Please consider the environment before
                  printing this email.<br>
                   <br>
                   <br>
                  <b>From:</b> RE-wrenches &lt;<a
                    href="mailto:re-wrenches-bounces@lists.re-wrenches.org"
                    target="_blank" moz-do-not-send="true">re-wrenches-bounces@lists.re-wrenches.org</a>&gt;
                  <b>On Behalf Of </b>Drake<br>
                  <b>Sent:</b> Thursday, August 23, 2018 2:37 PM<br>
                  <b>To:</b> RE-wrenches &lt;<a
                    href="mailto:re-wrenches@lists.re-wrenches.org"
                    target="_blank" moz-do-not-send="true">re-wrenches@lists.re-wrenches.org</a>&gt;<br>
                  <b>Subject:</b> [RE-wrenches] Forced air Furnace<br>
                   </p>
                <p class="MsoNormal"
style="mso-margin-top-alt:0in;margin-right:0in;margin-bottom:12.0pt;margin-left:.5in">Hello
                  Wrenches,</p>
                <p class="MsoNormal"
style="mso-margin-top-alt:0in;margin-right:0in;margin-bottom:12.0pt;margin-left:.5in">What
                  is the best choice for a propane, forced air furnace
                  for an off grid house? We would prefer one that
                  doesn't have a phantom load, although the transformer
                  for the thermostat may not be avoidable. Low blower
                  current would be preferable. The furnace AC will be
                  powered by a Magnum 4448 PAE.</p>
                <p class="MsoNormal"
style="mso-margin-top-alt:0in;margin-right:0in;margin-bottom:12.0pt;margin-left:.5in">Thank
                  you,</p>
                <p class="MsoNormal"
style="mso-margin-top-alt:0in;margin-right:0in;margin-bottom:12.0pt;margin-left:.5in">Drake
                </p>
                <p class="MsoNormal" style="margin-left:.5in">Drake
                  Chamberlin</p>
                <p class="MsoNormal" style="margin-left:.5in">Athens
                  Electric LLC</p>
                <p class="MsoNormal" style="margin-left:.5in">OH License
                  44810</p>
                <p class="MsoNormal" style="margin-left:.5in">CO License
                  3773</p>
                <p class="MsoNormal" style="margin-left:.5in">NABCEP
                  Certified Solar PV </p>
                <p class="MsoNormal" style="margin-left:.5in">740-448-7328</p>
                <p class="MsoNormal"
style="mso-margin-top-alt:0in;margin-right:0in;margin-bottom:12.0pt;margin-left:.5in"><a
                    href="http://athens-electric.com/" target="_blank"
                    moz-do-not-send="true">http://athens-electric.com/</a>
                </p>
                <p class="MsoNormal"> <br>
                  _______________________________________________<br>
                  List sponsored by Redwood Alliance<br>
                  <br>
                  List Address: <a
                    href="mailto:RE-wrenches@lists.re-wrenches.org"
                    target="_blank" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
                  <br>
                  Change listserver email address &amp; settings:<br>
                  <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
                    target="_blank" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>
                  <br>
                  <br>
                  List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
                    target="_blank" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>
                  <br>
                  <br>
                  List rules &amp; etiquette:<br>
                  <a href="http://www.re-wrenches.org/etiquette.htm"
                    target="_blank" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
                  <br>
                  Check out or update participant bios:<br>
                  <a href="http://www.members.re-wrenches.org/"
                    target="_blank" moz-do-not-send="true">www.members.re-wrenches.org</a></p>
              </blockquote>
            </div>
          </blockquote>
        </div>
        <p class="MsoNormal"
style="mso-margin-top-alt:0in;margin-right:0in;margin-bottom:12.0pt;margin-left:4.8pt">_______________________________________________<br>
          List sponsored by Redwood Alliance<br>
          <br>
          List Address: <a
            href="mailto:RE-wrenches@lists.re-wrenches.org"
            target="_blank" moz-do-not-send="true">RE-wrenches@lists.re-wrenches.org</a><br>
          <br>
          Change listserver email address &amp; settings:<br>
          <a
href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org"
            target="_blank" moz-do-not-send="true">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
          <br>
          List-Archive: <a
href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html"
            target="_blank" moz-do-not-send="true">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
          <br>
          List rules &amp; etiquette:<br>
          <a href="http://www.re-wrenches.org/etiquette.htm"
            target="_blank" moz-do-not-send="true">www.re-wrenches.org/etiquette.htm</a><br>
          <br>
          Check out or update participant bios:<br>
          <a href="http://www.members.re-wrenches.org" target="_blank"
            moz-do-not-send="true">www.members.re-wrenches.org</a></p>
        <p class="MsoNormal"><o:p> </o:p></p>
      </div>
      <br>
      <fieldset class="mimeAttachmentHeader"></fieldset>
      <br>
      <pre wrap="">_______________________________________________
List sponsored by Redwood Alliance

List Address: <a class="moz-txt-link-abbreviated" href="mailto:RE-wrenches@lists.re-wrenches.org">RE-wrenches@lists.re-wrenches.org</a>

Change listserver email address &amp; settings:
<a class="moz-txt-link-freetext" href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a>

List-Archive: <a class="moz-txt-link-freetext" href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a>

List rules &amp; etiquette:
<a class="moz-txt-link-abbreviated" href="http://www.re-wrenches.org/etiquette.htm">www.re-wrenches.org/etiquette.htm</a>

Check out or update participant bios:
<a class="moz-txt-link-abbreviated" href="http://www.members.re-wrenches.org">www.members.re-wrenches.org</a>

</pre>
    </blockquote>
    <br>
  </body>
</html>