<div dir="auto">Hi all i have great respect for Magnum, it seems to have greater surge capacity, and i have 120 volt draws greater thsn 2500 watts on one leg. I never had a to much load one one leg problem. With Magnum, so please give more information</div><br><div class="gmail_quote"><div dir="ltr">On Thu, May 31, 2018, 7:09 AM Drake <<a href="mailto:drake.chamberlin@redwoodalliance.org">drake.chamberlin@redwoodalliance.org</a>> wrote:<br></div><blockquote class="gmail_quote" style="margin:0 0 0 .8ex;border-left:1px #ccc solid;padding-left:1ex">That is interesting about Magnum: Tech support <br>
told me that the 4024PAE was two separate 2000 W <br>
inverters. We had problems with a microwave shutting the system down.<br>
<br>
Do you find you have good reliability with Magnum products?<br>
<br>
Drake<br>
<br>
<br>
At 03:53 PM 5/30/2018, you wrote:<br>
>HI Dave and everyone, Its interesting because <br>
>there is a great deal of difference between <br>
>OEMâ\u20ac\u2122s. Outback says 4kw at 120v for 8kw <br>
>radian. ( tech support) Magnum says 27 amps at <br>
>120v, 16.7 amps at 240 for MS4024PAE ( from the <br>
>manual) Schneider says 4200 watts at 120v on <br>
>XW-6848 ( from the manual) Also I know that the <br>
>Magnum allows you to charge with just 120v and I <br>
>think the XW is the same, OB you have to have <br>
>240v. Cheers jay > On May 30, 2018, at 7:52 AM, <br>
>Dave Angelini Offgrid Solar <br>
><<a href="mailto:offgridsolar@sti.net" target="_blank" rel="noreferrer">offgridsolar@sti.net</a>> wrote: > > The 8kw radian <br>
>still has to have balance! You can't expect it <br>
>to supply > 8kw @ 120vac. It can supply 8kw @ <br>
>240 vac. > > >> Does each of the 4 kW 240 volt <br>
>inverters have a maximum on the 120-volt >> <br>
>power it can supply? for example, can it supply <br>
>70% of the 4 kW on 120 >> -volts? >> This <br>
>example would leave 5.6 kW of 120-volt? >> >> On <br>
>Tue, May 29, 2018 at 11:09 PM, jerrysgarage01 >> <br>
><<a href="mailto:jerrysgarage01@gmail.com" target="_blank" rel="noreferrer">jerrysgarage01@gmail.com</a>> >> wrote: >> >>> The <br>
>Radian has 2, 4k, 240 volt inverters, so its <br>
>different but the way >>> the >>> computer works <br>
>it makes the same from the load side of <br>
>things >>> Jerry >>> >>> >>> >>> Sent from my <br>
>Verizon, Samsung Galaxy smartphone >>> >>> >>> <br>
>-------- Original message -------- >>> From: <br>
>frenergy <<a href="mailto:frenergy@psln.com" target="_blank" rel="noreferrer">frenergy@psln.com</a>> >>> Date: 5/29/18 <br>
>5:51 PM (GMT-10:00) >>> To: <br>
><a href="mailto:re-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">re-wrenches@lists.re-wrenches.org</a> >>> Subject: <br>
>[RE-wrenches] Xfmr's job? >>> >>> Hey <br>
>folks, >>> >>> Outback FP2 with Xfrmr <br>
>shifts power to "other" leg if that >>> leg <br>
>needs more than the one FX can provide, <br>
>right? Say, you need 5.5 KW >>> on leg 1, the <br>
>Xfrmr pulls some power from the leg 2 (inverter) <br>
>to >>> support that 5.5KW load on leg 1. >>> >>> <br>
>My question (assuming above is accurate) is does <br>
>the 8048 Radian do the >>> same? >>> >>> <br>
>Thanks, >>> >>> Bill >>> >>> Feather River Solar <br>
>Electric >>> Bill Battagin, Owner >>> 4291 <br>
>Nelson St. >>> Taylorsville, CA 95983 >>> <br>
>530.284.7849 >>> CA Lic 874049 >>> <br>
><a href="http://www.frenergy.net" rel="noreferrer noreferrer" target="_blank">www.frenergy.net</a> >>> >>> >>> --- <br>
>_______________________________________________ <br>
>List sponsored by Redwood Alliance List Address: <br>
><a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a> Change <br>
>listserver email address & settings: <br>
><a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a> <br>
>List-Archive: <br>
><a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a> <br>
>List rules & etiquette: <br>
><a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a> Check out or <br>
>update participant bios: <a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
_______________________________________________<br>
List sponsored by Redwood Alliance<br>
<br>
List Address: <a href="mailto:RE-wrenches@lists.re-wrenches.org" target="_blank" rel="noreferrer">RE-wrenches@lists.re-wrenches.org</a><br>
<br>
Change listserver email address & settings:<br>
<a href="http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org" rel="noreferrer noreferrer" target="_blank">http://lists.re-wrenches.org/options.cgi/re-wrenches-re-wrenches.org</a><br>
<br>
List-Archive: <a href="http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html" rel="noreferrer noreferrer" target="_blank">http://www.mail-archive.com/re-wrenches@lists.re-wrenches.org/maillist.html</a><br>
<br>
List rules & etiquette:<br>
<a href="http://www.re-wrenches.org/etiquette.htm" rel="noreferrer noreferrer" target="_blank">www.re-wrenches.org/etiquette.htm</a><br>
<br>
Check out or update participant bios:<br>
<a href="http://www.members.re-wrenches.org" rel="noreferrer noreferrer" target="_blank">www.members.re-wrenches.org</a><br>
<br>
</blockquote></div>