<div dir="ltr">I&#39;m seeking some guidance on how to treat transformers when included in a PV system.<div><br></div><div>Specific system details:<div>- (3x) SolarEdge 33.3 inverters combined in a 200A panel</div></div><div>- 480/208 transformer to be installed between 200A panel and main distribution panel (service is 208 wye)</div><div><br></div><div>My questions:</div><div><br></div><div>- Is there any consensus on what circuit is considered the &quot;primary&quot; and which is the &quot;secondary&quot; in this type of scenario?</div><div>   - NEC 690.9(D) speaks of &quot;considering first one side of the transformer, then the other side of the transformer, as the primary&quot;. Is this relevant? i.e. Is it possible for both sides of the transformer to be labeled as a primary?</div><div><br></div><div>- I understand that 450.4(A) requires overcurrent protection on the &quot;input conductors&quot; (aka &quot;primary conductors&quot;?), correct? Must we provide overcurrent protection on the &quot;other&quot; side in the above scenario?</div><div>   - We were originally planning to land each inverter output on a 50A breaker inside a 200A main lug panel - must we also include a main breaker?</div><div><br></div><div>- How do we size the grounding conductors on either side of the transformer?</div><div>   - Is the grounding conductor between MDP and transformer considered an EGC (250.122)?</div><div>   - Is the inverter-side of the transformer considered a separately derived system, in which case the grounding conductor would be considered a GEC (250.102(C)(1))?</div><div><br></div><div>Thanks for any advice!</div><div><br></div><div>--</div><div>Corey Shalanski</div><div>Joule Energy</div><div>New Orleans, LA</div></div>